Climatemaster tbw60 HP fault
Last Post 16 Oct 2021 11:01 PM by Jess. 1 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
JessUser is Offline
New Member
New Member
Send Private Message
Posts:5

--
16 Oct 2021 12:01 AM
New install B&D flow center Source flow 15gpm load flow 11 gpm and holds that on shutdown. Back flush load coil. Have factory supplied screens between pumps and heatpump. Runs about 5 min then faults out. Didn't back flush source side but looks good. Hooked a garden hose to flush loop field into a 55 gal poly drum water was clean in all 3 drum fills. Bottom of pump center was clean.
JessUser is Offline
New Member
New Member
Send Private Message
Posts:5

--
16 Oct 2021 11:01 PM
Solved, upon setup there is a dip sw setting for boiler/boiler less. I chose boilerless, I have no backup heat. Wrong choice and it was short cycling. Not sure what that switch is about. I'm going to have a Climatemaster tec check my work and dip sw settings go through commissioning paper work for warranty purposes. Also not sure why it had a high pressure fault, air maybe.