At 3lbs+/ft^3 the only way cellulose will settle is with repeated actual-wetting/drying cycles (not mere humidity changes within normal ranges.) I suppose in a couple of centuries it MAY sag and need topping off under "normal" non-wetting circumstances... but not in a coupla decades (or even five.)
Two-hole method deliverers densities in 2.0-2.5lbs/ft^3 range, low enough to sag a bit over a decade or three, but FAR less sag than an open-blow attic floor situation (~1.5lb/ft^3 settled-density). R-value of cellulose doesn't begin to diminish with density until you're in the 2lbs/cubic foot range, and then drops only very slowly with density:
http://www.builditsolar.com/References/DensityvsRValue.htm.
Unlike mineral & glass fiber insulations, cellulose fibers are hollow, and do NOT rely solely on inter-fiber air trapping for their R-value. At densities of 3lbs/ft^3 or higher it limits convection currents within the material, and adds considerable thermal mass to the system. The total-performance "sweet spot" for cellulose is between 3-4lbs/cubic foot. Below that density infiltration & convection creeps up, and above that density R value slowly drops without much performance gain from further marginal drops in infiltration/convection issues. Most manufacturers spec 3.2 or 3.5lbs for achieving the rated dense-packed performance, but once you're over 3lbs cubic foot the differences are academic- you might be able to measure it in a lab, but not likely in the real world. (Some argue that 2.5lbs/ft^3 is good enough from a measured-performance POV, but it it may be more likely to run into settling issues than at slightly higher densities.)
The wet-spray stuff is guaranteed not to settle even at lower densities, since it has a water activated adhesive, but it's inflltration & convection factors aren't nearly as good as dense-packed. "Blow-in-bag" technique (using the fibrous netting) can be used for dense-packing, but it makes applying the finish wall tougher since it bows it out from framing. Blow-in-bag using wet-spray (at any density) can at least be trimmed flush to the studs after the adhesive cures, but not dry-blown, which retains it's shape primarily from spring tension against the retaining surfaces- if you trim it it won't fall out, but it'll lose density slightly.
Dry blown is preferred in very thick walls, since it can take weeks (or months!) for wet-spray to fully dry if applied deeper than standard stud depths. I'm not sure what the point of blow-in bag mesh would be in a Larsen Truss type design except for using the mesh as separators between the truss-bays so as to guarantee full & uniform density from one bay to the next. In a PassiveHouse engineered-beams-for-studs design the OSB webbing performs that containment function.
Batt & blown fiberglass can get you the same R-values, but they have their own issue (the requirement for fire-stop blocking in the stud bays, for instance). Batts are nearly impossible to install perfectly when dealing with plumbing & electrical schtuff, won't stuff properly into the small & nonstandard width sections of framing, and unless it's the high-density "cathedral ceiling" type, loses R value significantly with increased delta-T (not a problem in TN or CA, but a real issue in MN where it can be -10F outside for way more than a few hours out of the season.) Blown fiberglass need similar or somewhat higher densities as dense-packed cellulose to not sag, but that can be done if desired. |