Posted By KI7OM on 10 Jul 2012 08:51 PM
Having the basement return air located in the ceiling in your climate is simply poor design. The warm air supply registers are also likely in the ceiling. Elementary physics will tell you that the warm air is less dense and will layer near the ceiling and simply move to the return register or up the stairs. One of the first things you could do if the tear-down-rebuild it yet some time in the future is to move your basement return air from the ceiling to a baseboard/low wall location. Think of the return register like a big vacuum cleaner sucking up the cold air layered near the floor. In addition make sure that there is enough undercut space for the doors on any rooms allowing the return air to circulate to the low wall return air opening. A door on the stairway might also help.
Does your NG Heatolator have any sort of outside combustion air ducted to it or do you have anysort of makeup air venting into the house? It is quite possible that if your house is relatively tight that when running bathroom or kitchen vent fans you are drawing combustion gases back into the home while it is firing. If you can feel cold air inside the firebox with no fire and you are running exhaust fans elsewhere in the house that is very likely the case.
Seriously,
do the math on the elementary physics rather than mere arm-waving arm-chair physics!
You'll find that the stratification forces over a 9' tall room are really quite modest- orders of magnitude behind the air mixing motion induced by air handlers. In the bursty on/off mode this system is running the mixing of the air would be pretty good. Only over relatively long periods of undisturbed air would the buoyancy factors induce stratified temperatures in the room.
If there's a temperature gradient in the room it's likely to be from a significant heat-loss out the slab &/or outdoor air infiltration at a low point, or a very-cold door/wall is inducing a convection current. (More likely a combination of the three.)
Moving the
return register to floor level won't fix the cold-feet/warm-head problem one bit. Moving the
SUPPLY register to floor level. and directing it across the floor would help some though. But in a tight well insulated house you shouldn't have to move either to be comfortable. (Tightness and insulation levels are suspect here though.)
Good call on testing for backdrafting on the fireplace, which seems likely given the reported gas-odor issues. There could be other issues related to that unit that could account for the symptom, but backdrafting is a serious health hazard, something that needs to be rectified.