Posted By Alexis on 29 Aug 2013 01:27 PM
no, it's not a walkout.
There will be 2" of cc spray foam underneath the slab and 3.5" on the interior of basement wall. Framing the wall on the footer would allow the spray foam crew to come only one and spray everything... that's why I'm thinking of doing it that way...
Spray foam
under the slabs has a very spotty track record in my neighborhood, and I simply wouldn't do it. Its cheaper and more reliable to use EPS (the stuff of cheap coolers and coffee cups.) EPS runs about 9-10 cents per R-foot compared to closed cell foam at 17-19 cents/R-foot, and it arrives at the job site completely cured, no funky PITA shrinkage or mis-curing issues that can happen with closed cell polyurethane sprayed onto dirt (preferably clean 1/2-3/4" screenings). It's the right stuff.
Spraying closed cell foam between 2x4 studs is a waste of good foam, since the thermal bridging of the studs ruins the average performance. The difference in "whole-wall-R" with the thermal bridging factored between R15 rock wool and 3.5" of R7/inch foam is R15.2 vs. R11.7, a difference of less than R4. And that's at a fairly low framing fraction of 15% (24" o.c. stud spacing, few or no windows & doors, single top plate). That difference could be made up with as little as 1" of EPS (or a 1" shot of closed cell on the concrete, separating it from the stud edge. And in practical terms you're really not going to get 3.5" of foam between studs since it's not easily trim-able- figure on 3".
And putting stud edges in contact with the sub-grade concrete is just asking for moisture & mold issues getting started even before the house is finished. It needs both a capillary and thermal break to be robust. Rigid or spray closed cell foams can provide both, but it must be placed between the framing & concrete.
Massive quantities of closed cell polyurethane also have the issue that the HFC245fa blowing agent is a powerful greenhouse gas, about 1000x as potent as CO2 on a lifecycle basis. An inch or two in select locations for managing vapor permeance and air sealing can be sorta-green, but there's no way that's true in under-slab or foundation wall applications at 2-3.5". In those locations at those thicknesses it will have a greater lifecycle greenhouse effect in excess of the source energy use it's offsetting. XPS (pink/blue/green board) has similar issues, but EPS and polyiso are blown with pentane, with only ~7x CO2 greenhouse potency.
If you were shooting for ~R20 on the foundation wall (3.5" of R6/inch foam is R21), a standard R20-R22 insulated concrete form would get you there, probably for less upcharge than the $3.50 per square foot you would have paid for the closed cell polyurethane. But if the foundation has already been poured, that ship has sailed. At a 15% framing fraction the studwall with R15 rock wool comes in at nearly R12, and putting 2" of EPS between the concrete & studwall brings it to R20. Alternatively, 3.25" of polyisocyanurate held in place with 1x furring through-screwed to to the foundation with TapCons 24" o.c. gets you there (also at ~10 cents/R-foot)