Exterior Rigid
Last Post 02 Dec 2013 07:15 PM by Surfsup. 43 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Page 3 of 3 << < 123
Author Messages
SurfsupUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:349

--
29 Nov 2013 06:55 PM
Just as a recap the roof is going to be this:

SS metal roof
#30 felt or synthetic
Sheathing
TJI 14" joist cavity 24" o/c
2" rigid polyiso board ripped to 1' 11-3/4" wide wedged between each TJI leaving 1-3/8" vent (R-12)
1" closed cell SPF for air seal (+R-7 for R-19)
HD batt or spider to fill the rest of the cavity which is 9-1/2" left open
gypsum

R38 is required so 38-19 = R19 batt but with the 9.5" I can use a R30 HD batt which is only 8.25" thick for a total of R49. leaving the lower nailing span gap alone. I guess I can use 1" rigid board and 2" ccSPF...

Can you do 1" rigid, 1" ccSPF and 8" ocSPF on top of that? (instead of the batt)
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
30 Nov 2013 04:33 PM
You're adding complication and steps that add cost. Skip the c.c. foam, put in ~R20 iso (3-3.5"), sealed at the edges with FrothPak or can foam, and either blown fiber or o.c. foam for the rest of the cavity fill. There is no such thing as a decent fit with batts in TJIs. If you're going with o.c. foam, skip the FrothPak- o.c. foam done right will provide as-good or better air sealing. You'll be at about R50 center cavity with that stackup.
SurfsupUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:349

--
02 Dec 2013 07:02 PM
OK I will do 3" rigid with the rest ocSPF. Thanks for hanging with me!
SurfsupUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:349

--
02 Dec 2013 07:15 PM
OK So a summary, ZONE 5:

ROOF:

SS metal roof 3:12 pitch light gray color
#30 felt or synthetic
Sheathing
TJI 14" joist cavity 24" o/c
3" rigid polyiso board ripped to 1' 11-3/4" wide wedged between each TJI leaving 1-3/8" vent (R-18)
6" open cell SPF (Demilec Agribalance)
gypsum

WALL:

siding - Hardi Lap or LP Smartside
3/4" polyiso rigid board
wood sheathing
2x6 walls
2x6 cavity filled with open cell SPF Demilec Agribalance
CertainTeed Membrain or Intelloplus or equiv
gypsum