Hi
I am helping my son build a total icf home in western New York and are to the point of insulating the ceilings. Our plan is to spray 4" of closed cell foam on the flat ceiling drywall and covering the 2x4 bottom cord of the roof truss.
We were also considering installing 2" rigid foam board prior to the drywall to help with thermal bridging from the truss.
Would this work or could there be issues with condensation etc.
thanks for any input
Spraying 4" of closed cell foam in this application is the opposite of "green", due to the EXTREMELY high global warming potential of the blowing agent used (almost always HFC245fa), at about 1000x CO2. If the purpose is to air seal, you can get better air sealing with 3-4" of high expansion half-pound density open cell foam, which are almost always blown with water. To avoid self-ignition or adhesion issues the closed cell would have to be installed with two lifts of 2" with a cooling period in between, and will cost a bit over $4/sq.ft, compared to about $1.20/sq.ft. for 3.5" of open cell foam sprayed in one lift.
Dick Russell has it dead-right that burying the truss chords in blown cellulose is a better and cheaper thermal break than 2" of rigid foam. But if you take the rigid foam route, use either EPS (the beaded stuff of disposable coffee cups, R8.4 @ 2"), or polyisocyanurate (R12-13 @ 2"), both of which are blown with pentane (which has a GWP of about 7x CO2), and NOT XPS (pink, blue, green board), which is blown with a mixture of HFCs, the major portion of which is HFC134a (about 1400x CO2).
But since you'll need something like a 8-12" fastener spacing long-screwing/nailing the gypsum through that foam you will get significant thermal bridging due to the high thermal conductivity of steel, which is about 300x that of the foam it is penetrating through. That can be mitigated if instead of long-nailing the gypsum through the foam you screw 1x furring 24" o.c. perpendicular to the truss chords between the foam and gypsum, and use short ring-shank nails to hang the gypsum on the furring. That cuts the thermal bridging through the foam by half or more.
With a vented attic design you don't need a vapor barrier at the ceiling- orders of magnitued more moisture gets into the attic via air leaks than by vapor diffusion through standard latex paint, and simply by air-sealing the ceiling plane (verified & remediated tight via blower door testing) you have taken care of the most likely moisture problems.
From a raw $/R point of view, cellulose is generally the cheapest way to go high-R. In an open blow situation you're talking 3-4 cents per square foot per R, so hitting R50 is on the order of a couple bucks per foot. Closed cell foam is about 5x as expensive per R, open cell foam about 3x as expensive per R. By far the greenest approach would be to use tapes caulk & can-foam/FrothPak for the air sealing, and cellulose for the actual insulation. If the trusses are 24" o.c. you may want to put up half-inch OSB on the under side of the trusses to manage the weight of high-R cellulose without sag, air sealing the seams with duct-mastic, and go hog wild on the cellulose. Even R75 plus an OSB support deck would be cheaper than just the 4" of closed cell foam, and the same or less labor installing the gypsum + rigid foam.