Posted By rmawhinney on 30 Jun 2014 01:43 PM
Thank you for all the information Dana! How much ISO would I need on the walls and roof if I were to leave out the bat insulation? I love the idea of container buildings but I have all the spruce material I need. If I didn't already have that then I would consider it for sure.
If all of the insulation is outside the structural sheathing the sheathing will be at the same temperature and humidity as any other wood in the house, so it doesn't much matter if it's 3/4" of iso or a foot. But for staying comfy in Maine you'd probably be happier if it were a foot.
To meet
code-min performance with only exterior insulation in Maine (climate zones 6 & 7) you need at least 4" of polyiso. You could meet code min LABELED R at only 3.25" (R20), but the mid-winter performance of polyiso would be lower than labeled. If you only have room for 3", you'll be better off with staggered layers, with 1.5" of polyiso next to the sheathing, and 1.5" EPS exterior to that. While the labeled values would be R9/R6.3 for the iso/EPS respectively, during mid-winter the outer layer of EPS would be about R7, but the inner layer of polyiso would be about R11. If you put 2 layers of 1.5" iso the outer layer would be only good for about R3-R5. This is due to the funky detrating curves for polyiso, which peaks at about 50F mid-layer temp, but falls off a cliff for layers with a mid-layer temp below 30F.
EPS keeps gaining performance with lower temp for quite awhile, and doesn't have that steep cut-off at very low temps found with polyiso, which is why the a 50/50 thickness stackup of EPS/iso performs better in a Maine climate than an all-iso solution, despite the labeled values.