So I've paid for one HVAC manual J, done two online (coolcalc and loadcalc)
They basically all say the same. Numbers came in around 9000-9500k BTU Cooling, 15k heating.
Design temp is 15F winter, 87F summer. Mountains of North Carolina so yes, winter is colder than summer is hot.
Looking at Fujistu 9RLS3 (the 9,000 BTU one) or 12RLS3 (the 12,000 BTU)
Looking at Fujitsu Engineering tables for Cooling Capacity on the 9k it says on the line of 87F outside, 75F inside:
9300 BTU Total Capacity, 8000BTU Sensible Heat Capacity
For the 12k the line says:
12400 BTU Total Capacity, 10140 Sensible Heat Capacity
If anyone cares I'm looking at the RLS3H manual here, though I plan on getting the RLS3 (non-H) as below -5F is a rare occurrence (yes I have backup plan) - https://portal.fujitsugeneral.com/files/catalog/files/DTR_AS115E_01--ASU9-15RLS3_H1.pdf
So I don't know. Sure I could look at the line for 70F instead of 75F but look, it gets to 86F like from one week out of summer. I can deal with oh dang it's 77F in here and not 72F for a week four hours a day.
But I don't know if I'm looking at Total, or Sensible. I don't want to oversize so I can be in a 65F room when it's 90F out for one day every 12 years. But I don't want to be undersized.
If I look at TC the 9K seems about right. If I look as SHC then do I need the 12K?
And I have no idea what sensible HEATING capacity means in cooling table. Is that related to cooling, or does that mean if I need to run heat when it's 75F outside that's what I get for heat? That makes no sense as that value is lower than heat output when it's 5F outside. So that can't be it.
Question all boils down to so I need the 9k for summer, or the 12k for summer.
Either have plenty of the 15K BTU's I need for winter at 15F outside, and enough to heat on the oh-shoot-it's-2F outside put a spaceheater in the bedroom for 3 nights of the year.