Vapor barrier on poured basement walls?
Last Post 03 Feb 2017 10:01 AM by PARAHOMES. 8 Replies.
rgonyerUser is Offline
29 Jan 2017 02:28 PM
We're getting ready in the next day or two to put down our XPS and vapor barrier on our basement floor. Should we hang vapor barrier on the poured walls first so we can fold those underneath the vapor barrier on the floor assuing no moisure will ever go anywhere but under the floor? Or is it OK just to use foam on those basement walls after the floor is poured?
Bob IUser is Offline
29 Jan 2017 05:05 PM
If you are using polyiso on the walls, that is a vapor barrier and air barrier, so poly would have no purpose. But it is a good idea to run the slab poly up the wall enough to be held by the polyiso, so the Air Barrier is continuous.
29 Jan 2017 06:34 PM
Thanks Bob. Is polyiso what you'd recommend over XPS?
30 Jan 2017 07:37 AM
yes; much, much lower GWF (global warming factor), but also higher R value per $.
ChrisJUser is Offline
30 Jan 2017 02:51 PM
For the walls but not under the slab
30 Jan 2017 03:05 PM
yup; EPS under the slab
30 Jan 2017 03:41 PM
XPS performance will eventually fall to that of EPS. The extra volume of excavation for thicker foam at the same labeled R is cheap.
Polyiso is hygroscopic and can load up with moisture under a cold slab, but it's fine on the interior sides of walls down to slab level. If it's going to rest on the slab the vapor barrier needs to extend up the foundation wall, behind the wall-foam. It's better to use EPS along the slab edge between the foundation wall & slab, with the bottom edge of the polyiso resting on EPS rather than concrete.
01 Feb 2017 07:05 AM
Posted By Dana1 on 30 Jan 2017 03:41 PM
Great this is exactly what I'm doing. I wound up going with XPS for under slab because the excavation was already done and I only had 2" to work with. That part is done. I have been using scrap chunks of XPS to glue against the foundation wall, (If I have to buy more for this purpose I'll get EPS). Vapor barrier will be lapped over that then up the wall, and polyiso against the walls all the way up.
PARAHOMESUser is Offline
Where are you getting your building science from? GBA school of dumb bells? You should be asking more questions rather than giving bad costly advice. As a result homes designed here and GBA will end up with costly mistakes.
Right Side Graphs
Water vapor diffusion depends on a resistance factor (u-value), vapor diffusions thickness sd-value, permeability.
1.All of the foam products have low moisture contents until they see RH 60% + then they are still low, applicable to walls, or terrestrial vapor pressures/temp @ capillary material air pockets, peak load @ 100% depending on porosity.
2.PISO has better perm-in retention than XPS but not much.
3.POLISO has lower u-value than EPS/XPS is it’s free saturation state due to its lower surface diffusion/liquid transport, as it takes on water/temp and XPS has lower stable perm-in than EPS/PISO.
Left Side Graphs
Liquid Transport Coefficent (DW) – This is liquid convection treated as diffusion since it relates absorbed water over an sf area over time. It depends on material and boundary conditions.
DWs - The liquid transport coefficient for suction Dws….describes the capillary uptake of water when the imbibing surface is fully wetted. In the context of building physics this corresponds to rain on a facade or an imbibition experiment. The suction transport is dominated by the larger capillaries, since their lower capillary tension is more than compensated by their markedly lower flow resistance.
DWW - The liquid transport coefficient for redistribution - describes the spreading of the imbibed water when the wetting is finished, no new water is taken up any more and the water present in the material begins to redistribute. In a building component, this corresponds to the moisture migration in the absence of rain. The redistribution is dominated by the smaller capillaries since their higher capillary tension draws the water out of the larger capillaries.
Since the redistribution is a slower process (taking place in the small capillaries with their high flow resistance), the corresponding liquid transport coefficient is generally markedly less than the coefficient for suction.
The foams exhibit no capillary conduction @ Max Moisture Content above free saturation. Mineral wool board exhibits better properties.
So if you have a high soil Plastic Index (PI) XPS due to it’s low perm-inch is a better choice, otherwise, there is not alot of difference between EPS/POLISO to justify cost, not only perm-inch but Dw.
DANA1: "XPS performance will eventually fall to that of EPS. The extra volume of excavation for thicker foam at the same labeled R is cheap."
Not - EPS has better perm-in thermal conductivity than XPS. XPS will never "fall" to it's performance in any boundary conditions due to the surface layers @ MMC.
DANA1 : "Polyiso is hygroscopic and can load up with moisture under a cold slab, but it's fine on the interior sides of walls down to slab level. If it's going to rest on the slab the vapor barrier needs to extend up the foundation wall, behind the wall-foam. It's better to use EPS along the slab edge between the foundation wall & slab, with the bottom edge of the polyiso resting on EPS rather than concrete. "
and this too is WAY OFF Dana 1,
"POLISO is hygrophobic"     It does not have more normalized water content nor Dw than the others.
Plastic Index (PI) test at differeent depths properly designs insulation & vapor management & footing/wall depths, and they are cheap. A soils shear test especially for low PI s/b conducted but can get expensive but so can failed foundations.
Foam compression, deflection, creep are on the order of 7-10 lower than high perm-inch MWB. If the slab is not suspended properly, along with low shear & high PI soil the foam/barrier will crack in tension. Once that happens high pressures/flow rates at the cracks cause lots of issues.