Posted By Matcartier on 24 May 2018 02:29 PM
So with calls in to 12 different plumbers / HVAC guys (actual speaking calls... not just the ones that I left messages to that never called back...) and all of them telling me that my numbers don't actually show the size boiler that I need... I downloaded the Slant Fin heat load calc and did some more months of winter heating fuel use using Dana's method... All months came between 39000 and 44000, Slant fin gave me 43000. Slant fin also showed me that I have between 1.8 and 2.5 times more baseboard (just the finned sections) than what it recommends per room. For reasons that my numbers are wrong.... I'm having them tell me that they use home size using just the square footage and nothing else... I've gotten a couple that size it to the amount of baseboard, some that "let their supply house" do the heat load calc... using magic apparently... and some that "have done tons of these houses" and know that "its around 80000 btus..." I believe my numbers are correct and even if they aren't exact I'm pretty sure they're wrong toward being oversized but Im getting price quotes using the UFT-100. I'd prefer the 80 but aside from what seems to be a small difference in equipment cost will I be losing much by giving in to the UFT-100? (which I would absolutely play around with the high flame setback...) Is it worth standing my ground while all this equipment in my basement is still in working order? 82% (optimal) working order?
Slantfin's baseboard recommendations are set to minimize the total amount of baseboard needed to heat the place using high water temperatures.
For a condensing boiler to be operated at condensing efficiency takes about twice that much baseboard, so you actually NEED 1.8-2.5x as much baseboard than the high-temp system recommendations to be able take much advantage of the condensing efficiency. At an average water temp (AWT) of 170F (180F out, 160F return) baseboard delivers about 500 BTU/hr per foot, and that's probably the rough load/foot ratio in the Slantfin recommendations. At and AWT of 130F (135F out, 125F return- the beginning of condensing, ~90% combustion efficiency) baseboard puts out about 250 BTU/hr per foot. To hit 95% efficiency it has to be an even smaller ratio.
So, sizing the boiler to the radiation by the high-temp output of the baseboard is really for non-modulating boilers, and even then it's a MAXIMUM boiler size, not an optimum or even appropriate size. It only means that installing more boiler than the radiation can emit even at high temperature doesn't heat your house any faster or better than a boiler sized exactly to the radiation, so there is no point to installing a bigger boiler than that- it's a maximum.
But when you have 2x as much radiation than the house needs to be heated comfortably there is no point to installing the maximum amount of boiler that the radiation could possibly use, even if it's a cast-iron boiler.
With modulating condensing boilers you need to look at the MINIMUM fire output, and be sure that you have enough radiation to emit that much at condensing water temperatures. Oherwise you won't be able to get condensing efficiency without abusing the boiler with excessive cycling. For baseboard to hit a true mid-90s AFUE out of the boiler the min-fire output should be no more than about 200 BTY/hr per foot of baseboard. At that ratio it balance at an AWT of about 120F or a bit less with no-cycling. Ideally every zone should be able to emit at least 75% of the minimum fire output at an AWT of 120F. Below that it edges into short-cycling territory.
The min-fire output of the UFT-100W is about 9500 BTU/hr in condensing mode. That means ideally every zone would have at least 9500/200= 48 feet of baseboard. With that much baseboard it can deliver ~125F water out of the boiler at combustion efficiencies in the mid-90s and will not cycle on/off AT ALL during calls for heat, even if it's the only zone calling for heat. If it has only 36' it will cycle some, but it won't short cycle. Any shorter than that becomes a potential problem.
The min-fire output of the UFT-080W is 7600 BTU/hr. So it could balance perfectly with zones as short as 7600/200= 38', and would still tolerate zones as short as 28'.
So zone by zone, break it all down. If you have any zones shorter than 48' it will put a lot less wear & tear on the UFT-80W than it would on the UFT-100W.
For reference, here is the chart showing the output per foot of a popular Slantfin baseboard at different AWTs & flow rates:
https://www.slantfin.com/images/stories/Technical-Literature/ratings_fineline30_r.pdf