Thanks again, Bob. Solid it will be, then.
I could pull from the baths with 4" or 6". If 6", I could go round / rectangular and use the inside wall stud cavity to get downstairs. Maybe? 4" round seems limiting during a shower.
UPDATE:
I used an online ASHRAE 62.2 2013 calculation tool, and guestimating the door pressure test infiltration, I get a mechanical ventilation rate of between 100 and 110 CFM required.
looking at the photo of the schematic above, and the Fantech HRV SHR1505R data below, I think this will work. Assuming 0.2 to 0.4 resistance in the lines.
This would work if I could zone the different bathrooms so they are all not exhausting air when only 1 is showering.
Really, thanks Bob