Long time reader, first time poster. I know many probably cringe at yet another exterior rigid foam insulation post but hopefully someone can advise on my situation as I have read forum posts here and around the internet until my head hurts.
I am replacing siding on my early 70's house. Vinyl siding was installed directly over the original stucco and horizontal wood lap siding at some point. It was nailed through both the stucco and wood and was a rather poor installation job so I have decided that the best course of action is to tear everything down to the plywood sheathing and start over. The benefit to this being that it offers a great chance to add insulation for better energy efficiency and comfort. I have already purchased the siding and will be doing Alaskan Yellow Cedar in board and batten.
The walls are 2x4 construction and from inside out are:
1/2" Drywall
A thin vapour barrier (maybe 3mil?)
2x4 studs with pink fiberglass batts
3/8" plywood sheathing
felt/tar paper
As a bit of a bonus, before I moved in, the windows were replaced with nice energy efficient triple pane windows. Due to the fact that vinyl siding had been installed over the existing siding, the window installers installed the windows to be flush with the current siding which means once all of the existing siding is removed, I should have ~3 inches to play with before having to extend window sills. Great for adding extra insulation!
In reading about adding rigid insulation in retrofit situations I quickly discovered that trapped moisture and condensation are a very real problem to address when adding insulation with an interior vapour barrier. Being an older house, the vapour barrier is somewhat leaky but I am doing my best to seal up air leaks where possible. Without pulling down all the drywall, it's a fact of life for this house that there will be some air leakage which makes me feel that being mindful of exterior insulation, ventilation, and a wall system is of the upmost importance.
From what I have read, the Rockwool rigid insulation would be the best option from a breath-ability standpoint but the cost is prohibitive.
In my mind, XPS is ruled out for a number of reasons but mainly due to its poor moisture permeability and environmental considerations.
So I have more or less settled on EPS. The moisture permeability seems to be reasonable in the less dense versions, price is good, and the option of the graphite EPS is a good option to consider also.
From what I have read, with 2x4 walls, and being in a climate zone 7, I would need a minimum of R10 exterior insulation to keep the sheathing warm enough to avoid condensation. Correct me if this is wrong.
My questions are:
1. Given that this is not a perfect wall system and just a retrofit, would there be much of a difference from a condensation management standpoint between 2" Graphite EPS providing a claimed R10 (I believe I have found un-faced Graphite EPS, other option is perforated faced which offers a lower perm rating) and 2" Type 1 EPS which offers an R8 rating and the highest perms (5.25) possible? Or am I still in danger of moisture issues with either of these options?
2. Should house wrap be installed against the plywood sheathing or over the insulation before furring strips and siding?
3. My plan is to install horizontal 1x4 furring strips over the insulation to attach the vertical board and batten to thus creating a rain screen of sorts which should also help with drying.
4. Will type 1 EPS be rigid enough to install furring strips over without it compressing? Or do I need to look at something more resistant to compression? I am most interested in Type 1 due to its higher vapour perms. (5.25 for type 1 compared to 3.5 for type 2)
5. Finally, a bit of a technical question: Does cedar siding installed over furring strips add to the R-value of the wall or does the air gap behind the cedar negate any r-value or reduce it compared to it being installed in direct contact with the EPS insulation?
I'd appreciate any feedback, thoughts, recommendations, etc. that anyone can offer!