Rebar bend radius
Last Post 03 Jul 2007 11:07 PM by PatrickT. 4 Replies.
PatrickTUser is Offline
24 Jun 2007 03:43 PM
Having 8" core ICFs, what bend radius would you reccomend for #4 and #5 Rebar. (Horizontals for walls)
Patrick T.
icfcontractorUser is Offline
24 Jun 2007 07:42 PM
Patrick,,
I prefer 3". I think it is code for grade 60. I will have to do a little research.
ICF Contractor
24 Jun 2007 09:34 PM
Thanks ICFcontractor.
Sounds about right. I'm making a simple Rebar bender and I thought I'd get it right first before the welding!
Patrick T.
bnc_skcUser is Offline
24 Jun 2007 10:04 PM
Per ACI 318, the minimum diameter of bend for #3 - #8 bars is 6d (6 times the diameter of the bar). It is measured on the inside of the bend. Note that it is the minimun diameter, not radius.
For a #4 bar the minimum diameter is 3 inches (1.5" radius). For a #5 bar the minimum diameter is 3.75" (1.875" radius).
The above applies to bars other than stirrups and ties. Stirrups and ties #5 and smaller shall have a minimum diameter of bend of 4d.
Hope this helps.
By the way, ACI 318 requires cold bends unless permitted by the engineer.
bnc
Well got the Rebar bender made. Works pretty good too. I made it from old tractor parts. I started with a mandrel with a groove. The rest was a big hing section from a front end loader off an old Ford
Attachment: Straight.JPG
Attachment: Bent.JPG
Attachment: close.JPG
People Online People Online: Visitors Visitors: 278 Members Members: 0 Total Total: 278