Radiant barrier on ICF?
Last Post 14 May 2009 07:47 AM by lambabbey. 11 Replies.
arkie6User is Offline
18 Apr 2009 02:40 PM
I am having brick installed on the exterior of my ICF home with full walk-out basement.  The south faceing wall will be ~20' high and ~62' long.  Down here in the south, that brick gets really hot when the sun shines on it in the summer.  This heat then radiats out from the brick late into the night.
Standard practice here is to put a 1" air gap between the brick and the wall.  I was thinking about installing a radiant barrier on the outside of the ICF foam before the brick is installed to reflect some of this summer heat.   The cost for this aluminum and polyolefin based radiant barrier that I've been looking at is ~$0.15/ft2.  Are there any downsides to installing this radiant barrier other than the cost and time to install it?
Another idea I had was to just install 1/2" polyiso foil faced sheathing over the exterior foam.  This would add a radiant barrier as well as an additional R 3 to the existing 5" of EPS.  Local cost for this 1/2" foam board is ~$0.33/ft2.
Comments or suggestions?
18 Apr 2009 10:20 PM
Kinda defeats the science behind ICF adding this additional product. The thermal mass will work just fine in preventing all that excess heat from entering the structure. You idea may have some merit, but not something I would bother with.
19 Apr 2009 09:57 AM
I am with Chris, don't bother. you have lots of insulation and concrete to keep the heat out.
jusaxemeUser is Offline
19 Apr 2009 05:44 PM
Study the science behind the issue and make an informed decision.
There is no such thing as "cold"  Just heat and lack of heat.
Heat travels by conduction,COnvection, or Radiat flow
EPS has good resistance to conductive heat transfer.  I have never heard of anyone claiming it is superior as a radiant heat transfer barrier.
reflective insulation
Consumer Information on Reflective Insulation
reflective-insulation picture
contents
1. What is Reflective Insulation?
2. History
3. How Reflective Insulation Works
4. Benefits of Using Reflective Insulation
5. Certifications
6. Installation
7. Other common uses for reflective insulation
8. Select References
Reflective insulation has become a standard component of total insulation system design in both new construction and retrofits. Using reflective insulation for either home insulation or metal building insulation will increase the comfort level inside, protect against condensation and save on energy costs.
While other types of insulation are made to resist or impede the flow of warm air, reflective insulation reflects back radiant (infra-red) energy from the sun so it does not penetrate the building. It can also reflect back radiant heat inside the house so it does not escape. The concept is simple: each unit of radiant heat energy that is reflected away from your home in summer and each unit reflected back inside during winter means less operation of your air conditioning and heating systems, less wear and tear on your equipment, and less money you pay in utility costs.
Reflective insulation is commonly made of either aluminum foil attached to some sort of backing material or two layers of foil with foam or plastic bubbles in between creating an airspace to reduce convective heat transfer also. The aluminum foil component in reflective insulation will reduce radiant heat transfer by as much as 97%.
Examples of Reflective Insulation
Prodex TOTAL Insulation - Foil-Foam-Foil Foil-Bubble-White Polyethylene Foil-Bubble-Foil
History
Reflective insulation is a commercial spinoff of the NASA Apollo Space Program. NASA used a reflective foil covering to create a radiant barrier for both the spacecraft and space suits to reflect the intense heat of the sun away from the astronauts by day and to reflect internal heat back inside the capsule or space suit at night for warmth. NASA estimates that "Using conventional insulation, a space suit would have required a 7-foot-thick protective layer." Reflective insulation brings this radiant barrier technology to consumers for all types of building applications.
Radiation is the transfer of heat (infra-red radiant energy) from a hot surface to a cold surface through air or a vacuum. Radiation is the dominant method of heat transfer in a building accounting for 65-85 percent of all heat transfer through walls, ceilings, attic and floors. Reflective insulation is an effective barrier against radiant heat transfer because it reflects back almost all of the infrared radiation striking its surface and emits very little of the heat conducted through it. Reflective insulation products also incorporate trapped air spaces as part of the system to retard the convective flow of heated air the way fiberglass insulation does. The total thermal performance of the reflective system varies with the size and number of enclosed reflective spaces within the building cavity.
The thermal resistance of insulation is measured in R-value, or resistance to the movement of heated air by convection. The higher the R-value the more effective the insulation will be in resisting convective heat transfer. R-value does not measure an insulation's ability to resist radiant heat. Mass insulation like fiberglass or foam board primarily slows convective heat transfer.
In contrast, reflective aluminum foil facing an airspace like an attic, wall cavity, or crawlspace creates a radiant heat barrier. Aluminum foil reflects back 97% of radiant energy that strikes it. The generally accepted definition of a radiant barrier system specifies that the reflective material face an open air space. Radiant barriers that have no central layer of foam or bubbles to trap air are not insulation per se, and by definition, have no R-value. The idea is that a radiant barrier facing an enclosed air space (like an attic or a wall cavity) becomes a "reflective insulation" with a measurable R- value. Despite the advances in space technology in insulation systems based on understanding and modifying the effects of radiation, no universally accepted laboratory method has yet been devised to measure and report the resistance to heat flow of a multi-layer foil to properly compare reflective insulation to the R-values of mass insulation.
Reflective Insulation Installed in the Ceiling of an Attic as a Radiant Barrier
Reflective insulation is most effective in reducing the downward flow of heat through the roof in summer and through the floor in winter. Reflective insulation systems are typically located between roof rafters, floor joists, and wall studs.
Click here for a comprehensive article on attic insulation.
Reflective insulation is effective in floor systems above unheated basements and ventilated crawl spaces. Heat is lost through floors primarily by radiation (up to 93%). When reflective insulation is installed in the ground floors and crawl spaces of cold buildings, it prevents the indoor heat rays from penetrating down, reflecting the heat back into the building, thereby warming the floor. Since aluminum is non-permeable, it is unaffected by ground vapors. A properly installed reflective insulation system in the floor will act as a vapor barrier, significantly retarding penetration of ground moisture into the house above.
Click here for a comprehensive article on the Physics of Foil.
  • Light weight, very strong and easy to install
  • Moisture-proof - will not allow moisture to pass through in either direction
  • Eliminates condensation within the ceiling and walls when properly installed as a vapor barrier
  • Unaffected by humidity with lower moisture transfer and absorption rates than mass insulation - no mildew, mold or fungus growth
  • No significant mass to absorb and retain heat
  • Very low emittance values "E-values" (typically 0.03 compared to 0.90 for most insulation) which significantly reduces heat transfer by radiation
  • No change thermal performance over time due to compaction, disintegration or moisture absorption - common concerns with mass insulation
  • Easier to install than fiberglass - can be stapled, nailed, glued or sewn
  • Safer for workers to install than fiberglass - there are no fibers to breath or cause skin irritation, or eye irritation
  • Nontoxic and non-carcinogenic - does not irritate the skin, eyes, or throat and contains no substances which will out-gas
  • Carries a Class A / Class 1 Fire Rating
  • Radon retarder - will limit radon penetration through the floor
  • Not a nesting material for rodents, birds or insects
  • Attractive in areas where the insulation shows such as in a metal building
  • Reduces the "black globe effect" in animal confinement buildings
  • Energy Savings - Research conducted by the Florida Solar Energy Center (FSEC) has shown that the installation of a radiant barrier can have significant economic benefits. Attics account for approximately 22 percent of the heat gain in a typical Florida house. Installing an attic radiant barrier will reduce heat gain through the roof by about 40 percent. This equates to a savings of 8 to 12 percent on the annual electricity costs for air conditioning in a typical Florida home. The summer peak energy use savings was as much as 27%. This study also showed that the average peak reduction from the radiant barrier system was three times a great as that produced by added insulation (a change from R-19 to R-13).
20 Apr 2009 02:43 PM
Jusaxeme,
I enjoyed reading your post about radiant barriers.  I do have one question.  What effect does dust have when it settles on the radiant barrier's shiny side?  I did not see that addressed in your post.
20 Apr 2009 03:17 PM
Alton,
Thank you for your question.
Dust would diminish the emisstivity and thus diminish the effectiveness.
There are two ways to address this (although I wonder how large of a problem this would be in the setting that is a subject of the original poster's question--ie, behind the brick)
#1, an Atomic polymer nanoclay coating will create a paramagnetic surface that is thus photocatalytic and self-cleaning.
#2, The best radiant barriers recognise that there must be a gap or the radiant properties become conductive.  Sandwiching the reflective material between clear bubble pack helps
21 Apr 2009 01:16 PM
Posted By Chris Johnson on 04/18/2009 10:20 PM
I really don't see the idea of a radiant barrier defeating the science behind ICF, but rather supplementing it.  It doesn't take anything away from the thermal mass or insulation properties of the ICF wall in cooling dominated climates.  In climates where most energy is expended in cooling the home, and in particular where you have a masonry exterior with high thermal mass, I can see this helping to reduce peak and overall cooling loads by reflecting a large part of that radiant heat load away from the home.
In the summer here in Arkansas we don't get the same thermal mass benefits as the high desert areas since night time temperatures here in July and August rarely dip below what I would consider a comfortable temperature.
The only downside I can see is the time to install it and the cost of the material.  The better radiant barriers that I have found on the net run about $130 for 1000 sq ft.  These are generally 48" wide rolls of material and would go up relatively quickly.  If properly installed, this could also provide a good exterior wall moisture/vapor barrier, particularly around window and door openings.
Tom in MaineUser is Offline
30 Apr 2009 05:37 PM
How is heat going to radiate through 5" of foam?
Don't waste your money!
ICFARXXUser is Offline
06 May 2009 04:16 PM
Arkie6
 I just built a green home in the state of Alabama and my homeowner had this very question. We went through all the reasons why he would not have to install a RB on the exterior walls but in the end it just comes down to what you think. It does nothing but help. It may cost more and if you are fine with that then I say go for it as did my homeowner.
lambabbeyUser is Offline
14 May 2009 07:00 AM
I'm going to be building a small ICF home (1,300 sq ft) here in coastal Maine that will be airtight and super-insulated.   It won't qualify as a Passivhaus, but should come close in heatload numbers.    I'm going to be going with a double layer of ThermaSteel panels for the roof (15" total) and have also considered adding a floating layer of Prodex (foil-foam-foil) reflective insulation on the inside of the house beneath the ThermaSteel to potentially give me an extra R-15 in the roof--basically, gilding the lily.   Do any of you folks familiar with this product feel that I would gain any measurable benefit in R-value from this additional layer of insulation beneath what will already be an R-67 roof?
Let me know your thoughts, would you?   Thanks.
John
John A Gasbarre<br>Lamb Abbey Orchards<br>Union, ME 04862<br>[email protected]<br>
14 May 2009 07:32 AM
John,
Do you plan to have as much as an inch air space between the foil and ThermaSteel panels or does this product with two shiny sides require it?
Alton:
I'll have it sandwiched between a grid of 2x4s, giving it 1-1/2" of airspace on each side.    Here are other configurations that Prodex recommends.
Hope this helps. . .
John