Best methods to waterproof ICF foundation
Last Post 15 Mar 2012 09:34 AM by ICFHybrid. 47 Replies.
Page 2 of 3 << < 123 > >>
BrucePolycreteUser is Offline
08 Mar 2012 10:16 AM
The question was what's the correct way to waterproof, and I tried to give you a complete answer. All you need to keep the water from penetrating the ICF is peel and stick or spray on. That's all we're "required" to tell you. If you want to know how to keep water draining off the wall surface, protect the membrane from hydrostatic pressure and protect it from debris, you have to take the second step. I believe the pictures on the website show plywood used to protect the membrane from damage by debris in backfill. In the interest in giving a complete answer, I stand by my original post. You, however, are free to build to code.
RonCrosstoneUser is Offline
08 Mar 2012 10:39 AM
The purpose of any water proofing membrane is to prevent water intrusion, one of the best methods is to prevent the water from ever reaching the foundation in the first place, I use a minimum of 12" of gravel (washed 1"-1.5" stone) for backfill up the side of the wall and up to 12" under the slab including some under the footing with 4" SDR 35 drainage pipe, this process coupled with a peel and stick or some other type of sealant is almost a sure guarantee that you will never have a leak even if your membrane fails.
Full ICF HomesUser is Offline
08 Mar 2012 11:36 AM
Posted By BrucePolycrete on 08 Mar 2012 10:16 AM
As I read the original thread, and as indicated in the subject line, it says BEST, not CORRECT.
As I read the words of your last sentence, it sounds like a minimum requirement waiver, which sounds a lot like the minimum requirements of the building code ... which you argue against.  Perhaps it is only me who thinks this is a double standard but I like to see people with both feet firmly planted on one side of the fence, not both.
Might it be in the best interests of your product to add your suggestions for the dimple membrane as the "better" way to install your system?
08 Mar 2012 11:45 AM
I'm sure we'll be looking at that and any other inconsistencies that crop up next time we edit the installation manual. Here's another: When placing vertical rebar, don't drop it from 18 feet as it can bend a cross tie...
galoreUser is Offline
08 Mar 2012 02:11 PM
I opted against peel&stick or liquid applied membrane but used dimple membrane and gravel backfill instead. Soil is expansive clay (Dallas, TX).
Basement walls are bone dry. Footings sit on limestone bedrock which collects water that slowly percolates through the clay so it requires drain tiles and sump (which pumps out once a week rain or no rain).
I don't get the point of peel&stick or liquid applied waterproofing. There can only be hydrostatic pressure if the drain tiles fail and if that happens I have much more serious problems than water intrusion through the EPS & concrete...
08 Mar 2012 02:47 PM
Posted By BrucePolycrete on 08 Mar 2012 11:45 AM
I don't like the search engine on this site so I'll have to rely on my memory for one more variable to this redundant waterproofing idea.  With other systems in a house, dew points and condensations can arise out of seemingly "better" ideas.
Sometime in the last 6 months someone brought up the idea that there is a notable technical difference between P & S and dimpled in that the latter leaves an air space.  This space allows any moisture that might get into the foam to dry out or any condensation that may develop to drain down the weeping tile whereas the P&S would not.  If both were used it would negate the concept of dimple alone.  Dimple has been suggested, but not demanded, by the tech people support for the system I use.  Sounds like solid logic to me but I rely on the "experts" to verify the building science. (Anyone with an unbiased technical opinion out there ...  ?)
I treat education as an ongoing and life long process so I am ever vigilant to improve my education.  My dad told that is why they put curtains on a hearse at funerals ...  (to make us stop looking, but I'm fairly sure he was referring to this topic  ).
peteinnyUser is Offline
08 Mar 2012 04:25 PM
Thanks for all of the posts. Very informative and lots of opinions. I think the most important thing to remember is to do it correctly so there are no water issues in the basement.
arkie6User is Offline
08 Mar 2012 10:22 PM
Not sure if it is the best method, but this is the one I used: Tamko TW-60 sheet waterproofing membrane with Tamko TWM-1 mastic to seal all edges. I then covered that with Polyguard LowFlow protection and drainage mat.
http://www.tamko.com/Waterproofing/...ngMembrane
http://www.polyguardproducts.com/pr...opment.htm
09 Mar 2012 09:53 PM
Thanks arkie6, Has anyone used any spray methods on ICF?
09 Mar 2012 10:36 PM
I've used (had someone apply) Spray-it-Blue, never an issue but costly, ICF Blue Stuff from the box stores was a little finicky until you get used to it, AquaSeal makes a Grey Coat which sprays decent as well
FBBPUser is Offline
10 Mar 2012 11:04 PM
Posted By RonCrosstone on 08 Mar 2012 10:39 AM
Ron - I would agree that this is the often prescribed method of dealing with water. I try to discourage it when ever possible for the very reason you state, "to prevent the water from ever reaching the foundation in the first place".
When you think about it a bit you will understand that if there is a flood or even just a misplaced downspout extension or open hose bib, there is now a direct path through the drainage rock to the footings. Furthermore adding stone under the footing guarantees that in case of flooding you will have underslab hydraulic pressure and probably a lifted slab.
I aim for three things when building a basement.
Keep the surface water on the surface.
Keep ground water originating outside the foundation, OUTSIDE the foundation
Keep the underslab dry by install underslab drains to a sump inside to control any water bypassing the foundation or originating underslab.
To do this, I try to avoid tying the outside drains to the inside. I never tie downspouts to the weeping tile and try to avoid draining the window wells to the weepers. The outside drains either goes to daylight or to a pumpable manway, sometimes both. The outside drain is located with its bottom at the bottom of the footing and cover with drainage rock after the moisture proofing is installed. Usually 12 to 18" of rock spread up to 2 feet from the footing. The rock is covered with fabric to prevent the infiltration of fines in to the drainage material. In difficult soils, I will sometimes run more rock up the wall as you mentioned but I always try to cap it with 12"or so of soils with limited infiltration rates to prevent surface waters from reaching the drainage material. Then the topsoil can be places but it is usually better to wait with the topsoil till the following year so that the settlement can be filled with clays or similar materials to prevent a trough of permeable soils next to the house.
For the moisture proofing any of the mentioned products will work if there is no ponding of water. If the is total saturation, I doubt that any of them will prevent water from entering the basement either at the wall to floor joint or any crack, void in the wall. These product are really intended to prevent the soil moistures from wicking into the concrete and not really to with stand saturated or flooded conditions. I like the dipple materials or sometime even a product like AmerDrain http://www.americanwick.com/UserFiles/File/PRODUCTS/Total_Drain._Amerdrain.pdf which has filtration fabric mounted on it. It is than placed smooth side to the foam and the fabric creates a small void outside of the plastic that allows any soil moisture to run down to the weepers. The plastic materials suit me better mainly because most of the approved spray or roll on product don't do well in freezing conditions.
By separating the two systems, in flood conditions, even with a power failure, it is possible to pump the outside manway with a gas powered pump to relieve hydraulic pressure on the walls IF the surface water does not have straight access to the weepers. When s.h.t.f. there is no guarantees but if you can prevent the water from getting under the slab, you have half a chance.
Bob
ICFHybridUser is Offline
10 Mar 2012 11:25 PM
Arkie, did you use a primer with the membrane over ICF, and if so, which one; the quick dry or the water based?
11 Mar 2012 12:07 AM
Bob, You are correct, I forgot to add one thing to my statement. I take the drainage pipes out to daylight in every case. I have used this system many times over the past 30-35 years and have had to repair many homes and commercial buildings that were built incorrectly and had extensive water intrusion. In each case I used the system described above with complete success, only I also took each system out to daylight. The best use of the system was when we had extensive water flowing though the site in a commercial application. We used this system as described above to catch the water as it moved over and through the ground and then directed the water down through the stone and away from the structure. But had we not brought the drain pipe out to daylight, it most likely would have floated the slab or even pushed the basement walls in. I suppose that it might not be possible to use this system in every case, but when done properly, water will never enter the house even if the waterproofing membrane fails. Regarding the use of filter fabric, I have a tendency to shy away from filter fabric based on the following story; In the early 80s we built a 100,000 sf building for a large computer company in Massachusetts. Since it was a large structure it needed "in roof" drains, these drains were then directed out to the parking lot where they emptied into leaching catch basins. Per the engineer these basins were wrapped in filter fabric and then surrounded by 4"-6" stone. About a year after the projected was completed we had a call back to the site because the entire roof was flooded and was in danger of collapse. After reviewing the problem we dug up each basin in the parking lot and removed the filter fabric from around the basin which were all totally blocked with silt, as a result we never had a call back again. Ron
11 Mar 2012 11:00 AM
Posted By ICFHybrid on 10 Mar 2012 11:25 PM
 I didn't use any primer on the ICF foam based on recommendation from my supplier, but in hindsight, I would now.  I just thoroughly brushed and washed off the surface of the foam prior to application of the peel and stick sheet to the foam.  It stuck ok, but I felt that I could have had better adhesion with a primed surface.  We ended up using screws with 2" plastic washers every 8" to secure the top of the sheet.  Otherwise, the long sheets would tend to sag a bit.  This worked ok and we applied the mastic over the top edge and over the screws and washers.  Note that the mastic has solvent in it which tends to melt the foam it contacts a bit (~1/8" or so).  This seems to work really well around the edges of the sheet membrane as the mastic and foam are literally fused together as the solvent evaporates.
Also, prior to applying the sheet membrane, we applied the thick rubbery mastic to the top of the footing extending out from the wall.  This helped the membrane adhere to the somewhat irregular surface of the footing.  We extended the waterproofing membrane ~2" past the outside of the footing and folded it down over the edge.
Note that if I had used the primer, it would have been the TWP-2 water based primer which is intended for EPS foam.  The TWP-1 quick dry primer is solvent based and not intended for application to EPS foam.
11 Mar 2012 11:56 AM
I have read all of the above but now am wondering what each of you think about the following practice for waterproofing of walk-out cast-in-place basements:
Overcut the hole for the basement as much as required for worker access.  Slope the bottom of the hole towards the walk out end.  Spread and tamp clean gravel over the entire hole and slightly beyond the walk out area.  Form and cast in place the footers on top of the tamped gravel.  Cast the concrete walls on top of the footers.  Rough in the plumbing, etc. and then place the concrete slab for the basement.  Install the wall waterproofing.  Install footing drains to grade (daylight) beside the footer.  Install the main floor and then backfill the below-grade walls with clean tamped gravel to within one foot of the finished grade.  Lay down a filter cloth and then fill the one-foot area with impervious clay so that it slopes away from the house to meet the code requirements.
Although this practice would require the footers to be formed with something other than a trench, I think the clean, tamped gravel will allow any water that gets under the slab to flow freely to grade.  In a sense, the gravel should become one continuous footing drain to grade.
I mention all of this for your comments because basically this is what some precast wall companies do.  Some companies such as Superior Walls and Ideal Building System do not use a separate footer.  They just use a bond beam at the bottom and top of their precast walls.  Although I have used precast walls that resulted in water free basements, I wonder if the same technique would work well with a cast-in-place (CIP) footer for the CIP walls.  In other words, if this works for precast walls without footers, then will it also work with CIP footers?
11 Mar 2012 12:42 PM
More elegant. Because my footings were 3 feet wide on the outside, I opted to terminate the membrane (Miradri 860) at the bottom of the wall right on the footing. I then used the mastic (Carlisle CCW-704) to create a fillet at the corner. I took a 2" wide masonry trowel and ground the end down into a half circle for a filleting tool. That worked well. The mastic had lots of cautions about using it on plastics or foams, but it didn't appear to harm it in the few places they came into contact. Definitely a solvent-based mastic, though.
I really liked the latex "primer" (Carlisle CCW-702) as we had some retaining walls that needed waterproofing and the membrane would NOT stick to those without the aid of primer. Using the primer on the ICF created a strong bond with the peel-and-stick membrane.. If the two surfaces touched, they weren't coming apart, much like contact cement. According to the distributor, people like the quick-dry stuff for conventional construction, but I found the water-based primer to dry in as little as 30 min - 2 hrs on the ICF depending on temp and humidity. Faster on wood and concrete. The trick is to apply it sparingly with a roller.
eric monkmanUser is Offline
12 Mar 2012 08:03 PM
All Sask, you are correct to question the viability and performance of peel and stick membranes, congratulations
The main deficit of peel and stick is to trap water...... without providing an escape path, a total waste of money imho.
Once water gets behind the peel and stick membrane it can only escape to the interior of the foundation wall , which it invariably does
Air-gap is the ONLY product we use on ICF and Conventional Basement Walls, and as a concrete contracting company with 3 crews,
I can say we get ZERO call-backs or complaints about water penetration into our foundations.
We do all the sump, drainage system and clear stone work also to ensure that the water chanelled by the air-gap
has somewhere to go, either by gravity or sump pump.
The push to use peel and sticks by ICF trainers is a serious error.
Here is a link to a video on our weeper tile install.
This situation is allowing the 4 inch tile to be connected by gravity to municipal storm sewers,
 but in a rural condition we would be using plastic sump wells to handle the outflow.
This work is equally important as the air-gap.......... one doesn't work without the other :)
http://vimeo.com/35966139
12 Mar 2012 10:38 PM
There has been quite a large amount of peel-and-stick applied by now. Wouldn't we be hearing about widespread problems if that was the case? If you have done your job on the drainage, the waterproofing only has to resist the water pressure long enough to allow the water to get to footing drains.
During our frequent heavy rains this year, I have had standing water right up against the foundation, but the interior has been bone dry. I used peel and stick.
13 Mar 2012 04:16 PM
ICFHybrid..I stand by my comments discounting the effectiveness of "peel and stick"
Given good drainage, peel and stick will appear to be a success.
Given poor drainage, it will only be a matter of time before water infiltrates, then what ?
IMHO peel and stick is more difficult to apply, folds, creases and poor seams are easily to screw up.
Air gap is much more user friendly and 50% of the cost both labour and material wise of p&s.
The only failures i have been called on to repair have been by ICF installers who bought into the p&s mindset.
Trainers tend to embellish.
For me to make a living, I have to play it safe..and that is Air-Gap :-)
13 Mar 2012 05:45 PM
Doesn't air gap depend on good drainage, too?
People Online People Online: Visitors Visitors: 327 Members Members: 0 Total Total: 327