Frostwalls in Garage Under House
Last Post 28 Jul 2015 08:42 PM by jonr. 5 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
ShopGuyUser is Offline
New Member
New Member
Send Private Message
Posts:29

--
15 Jul 2015 04:30 PM
Planning an ICF addition.  House built into side of hill with front basement wall exposed.  The basement will actually be a garage that connects to the existing basement. See attachment.


The city inspector wants to treat the garage as unconditioned space.  As such he wants full 4' frost wall on all four sides of the garage.  My architect had planned to step the footings as they back into the hillside.  I see the inspectors point and agree that frost protection of those walls needs to be considered.  I'm wondering if there is a more elegant way to handle it.  Dirt side of the walls are protected once they get far enough below grade so it would just be a matter of protecting the garage side, right?  Would adding foam below the poured floor work?  Any suggestions?

Attachment: FrostwallDetails.jpg

ShopGuyUser is Offline
New Member
New Member
Send Private Message
Posts:29

--
15 Jul 2015 04:45 PM
That image was really degraded.  Let me try again.







Attachment: FrostwallDetails001.jpg
Attachment: FrostwallDetails002.jpg

ShopGuyUser is Offline
New Member
New Member
Send Private Message
Posts:29

--
28 Jul 2015 11:13 AM
After some more discussions we are going to frost protect the whole garage floor with 2" of foam. That way we can step the footings up and still maintain frost protection. It also minimizes how much we disturb the soil around the existing foundation wall. Seems to be good solution?

What sequence would you pour the walls and floors in? Footings first of course. Then pour the frost wall separate or do the frost wall and basement wall in one pour? The pour height would be like the first section view with a total height of 12'3" from top of footing to bottom of floor.


jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
28 Jul 2015 11:43 AM
You can extend foam horizontally beyond the walls, creating an unheated, frost protected shallow foundation. No need to go down to 4' anywhere, just a thickened edge slab.



billnaegeliUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:166

--
28 Jul 2015 06:28 PM
why isnt there any insulation on the exterior of the turn-down footer, on the vertical face, that is a huge thermal transfer, it is required under 2012IRC and IECC correct?


GNP Inc
ICF Construction & Concrete Services
1-800-713-7663
jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
28 Jul 2015 08:42 PM
In the picture, the space is unheated, so no need or purpose for such vertical insulation. But if the space were heated, yes, you would add vertical foam at the right side of the Dg arrow.