Electrical cables in polystyrene
Last Post 02 Sep 2011 04:28 PM by arkie6. 2 Replies.
stevesakiwiUser is Offline
02 Sep 2011 03:44 PM
My understanding of conventional electrical cables that long term contact between the external cable sheath & the polystyrene causes plastisizer migration. This can become a potential fire hazard. How is this dealt with when using polystyrene SIPS
arkie6User is Offline
02 Sep 2011 04:25 PM
All NM-B cable that I have seen recently uses a nylon jacket over the PVC conductor insulation. The nylon prevents the PVC insulation plasticizer from migrating into the EPS. The overall cable jacket also is a PVC material and you may have some plasticizer migration out of the jacket, but the jacket serves essentially no purpose after the cable is pulled and installed. Cracks in the cable jacket (due to long term loss of plasticizer) will not increase the potential fire hazard as long as the underlying conductor insulation remains intact and it should be with the nylon jacket. Also note that some NM-B wire designed for easy pulling has nylon incorporated into the outer cable jacket as well, further reducing the concern of plasticizer migration.
People Online People Online: Visitors Visitors: 420 Members Members: 0 Total Total: 420