I have used several "liquid applied" WRBs. However, only on vertical surfaces. The one I currently recommend is made by Sustant. It applies easily and creates a great barrier to moisture absorption. I helped the West Virginia University Solar Decathlon team with their SIP package and Sustant donated enough material to coat all the wall and roof panels.
The majority of SIP structures still rely on either a synthetic house-wrap or a asphalt impregnated felt. The key to a successful assembly is to understand permeability, airtightness, and (MOST IMPORTANTLY)drying. And all this is dictated by your climate zone.
A WRB is a must because ALL sidings leak! All SIP assemblies should be installed properly sealed and thus an individual air-barrier is not required. If an air-barrier is installed and it has little or no permeability, it is classified as a vapor barrier and must be installed on the correct side. All this applies to walls and roofs. Improper specification and installation of vapor barriers prevents drying.
If your climate or cladding require back-venting, (Or, as you called, a "rain screen")the introduction of air will promote drying and improve durability of the assembly regardless of the type of SIP or cladding.
Up on top, the term cold roof is used to describe the back-ventilating that is exactly the same as a rainscreen in vertical assemblies. I believe the term cold roof should be replaced with "Dry roof" I understand how it relates to ice dams, but the reason we back-ventilate a roof cladding has more to do with moisture than heat!
Agin, the roof's geographical location and type of cladding will dictate the need for back-venting. In short, if you're north of the Mason Dixon, I strongly recommend either a self-ventilating cladding and/or a back-ventilating (Dry-roof) detail.
Al |