I am mortified for myself and for the "professional" that installed your system and I feel like dirt...

It is good to research your options before jumping from frying pan to fire.Geo for your system is snake oil as my two asteemed colleagues have stated.

I think it is the first time a BadgerBoiler has been confused for a ModCon, but I think I like it?

My point is really, that a professional design should be done regardless of who installs the system, no matter where it located. A savvy designer is likely to know more about radiant applications than your local plumber, HVAC guy etc. Naturally they are needed for installation, service and warranty issues but design is a whole other animal.

Perhaps before you decide a new design should be done including especially heat load, near piping and control strategy?
MA<br>www.badgerboilerservice.com
eisensmsUser is Offline
New Member
New Member
Send Private Message
Posts:18

--
03 Feb 2011 12:37 PM
I really do appreciate all the guidance. Where do I send the check? I guess at this point we will go down the road of looking at a Solar-enhanced system like was mentioned above. The Geo sales guy said "a water-to-water Geo can crank out 125 degree water all day long!". As you say, "Who do you trust?" Maybe a used
car sales guy over a Geo guy, because the car sales guy "knows that he is lying to you", right? ;-)
NRT.RobUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1741

--
03 Feb 2011 12:38 PM
geo systems lose roughly a full cop per 10 degrees. at 125 your COP is typically pretty low, and lifespan of the compressor is greatly compromised.

I love Geo... love it... but I would never design a system for a geo heat pump at over 115 and I will do practically anything to keep it under 110.
Rockport Mechanical<br>RockportMechanical.com
BadgerBoilerMNUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2010

--
03 Feb 2011 01:09 PM
Radiant floors don't move air but naturally you will have an ERV to control air quality and the usual exhaust fans as necessary.
MA<br>www.badgerboilerservice.com
You are not authorized to post a reply.
Page 2 of 2 << < 12


Active Forums 4.1
Membership Membership: Latest New User Latest: croccohvacusa New Today New Today: 0 New Yesterday New Yesterday: 0 User Count Overall: 35027
People Online People Online: Visitors Visitors: 235 Members Members: 0 Total Total: 235
Copyright 2011 by BuildCentral, Inc.   Terms Of Use  Privacy Statement