The pipe is HDPE SDR11


cnygeoUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:170

--
22 Jun 2008 09:40 AM
Tough call. As your contractor said the pipe is pretty tough and will take a lot of abuse. On the other hand, you really don't want to be digging it up again. The kink shoudn't restrict flow to any significant degree, but it will be a weak spot that could compromise it over time as it expands and contracts. How did you decide to do your manifolds? If you're doing outdoor manifolds and having them fusion welded, I'd probably cut out the kink and weld it just for piece of mind if you've already got the equipment. As for the scratches from the bucket, impossible to tell without knowing how bad the buried sections are. Is only one pipe losing pressure? When you pressurize the pipe, it will stretch slightly and lose a bit of pressure. Are you pressurizing it with water or air?

If you're still hoping to do without antifreeze, I'd say a small leak might be tolerable, though certainly not desireable, depending on how you define small. I would be concerned about it getting worse with time. If you ever did need to add antifreeze, even a small leak would be unacceptable in my opinion.

Discalimer: I'm basing this on my vast personal experience of installing one system - one of the pros would undoubtedly have better advice.


hausfxrUser is Offline
New Member
New Member
Send Private Message
Posts:53

--
22 Jun 2008 01:32 PM

Cyngeo,

<!--[if !supportEmptyParas]--><!--[endif]--> We are doing indoor manifolds.  The pipe is being pressurized with air and each pipe has an individual valve connected to a common pressure gage.  Yesterday, we talked to the gas man who was testing the soil around our gas line the excavator had broken, and he said the crimp did not look too bad.  He suggested that we put a stainless pipe repair clamp around that section to stabilize expansion and contraction and reduce stress.  It would also help make sure the pipe does not re-crimp at that section as we lay the rest of the pipe.
<!--[endif]-->

I have bought some sheet plastic to create a water pond so I can drop the whole pressure testing manifold under water to see if I spot a slow leak that is not showing with soapy just water.  The excavator also ran over a section of pipe that was well out of his way when he was not paying attention (he also ran over a 7’ tall by 6’ diameter rhododendron which we were sad to lose and he ran into our the corner of our metal shed crushing a corner.)  I will test that section by submersing it too.  That section is not buried, but, while it had maybe quarter inch deep dents in it from the track hoe tracks, within an hour or so, it had returned to normal shape and you could only see scratches. 

As to the antifreeze issue, I never meant to imply that we would not use it, only that the system is expected not to go below freezing in the loops.  We will be using antifreeze.

An additional note about gas line safety:  I had the gas line clearly marked by the gas company at the excavator's request, but it turned out to be about 12” inches from where they thought it might be.  The excavator was trying to save a little time and effort by digging with his track hoe as close to the pipe as possible before hand digging, and he tore the pipe right out of the ground.  The supply side had sheared flush below the ground, so the excavator decided to bury the severed end to try stop the gas flow.  Apparently, that is the worst thing one can do – the ground can fill up with gas and create a giant underground bomb.  You should just clear away (the excavator continued to dig the trench), not try to stop the leak, and let the gas dissipate into the air. 

Also, while the excavator had several clauses in his contract about not being responsible for locating and damage to underground utilities, Oregon contractor's law says he is exclusively responsible for both locating and the cost of damages.  Apparently, he is also responsible for incidental property damage, despite any clauses in his contract to the contrary. 



AltonUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2164

--
22 Jun 2008 02:38 PM

esger,

Please tell us that the excavator is no longer on your property.  You have much more patience than I.



Residential Designer &
Construction Technology Consultant -- E-mail: Alton at Auburn dot Edu Use email format with @ and period .
334 826-3979
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
22 Jun 2008 02:49 PM
Brint.

Sorry to hear of your troubles.  It sounds like the excavator is really a loose cannon.    He should be reported for his dangerous gas line handling.  We had several homes in our area completely destroyed and people killed when a gas line was cut and the gas migrated underground into nearby homes.

We always test with water since this makes it really easy to know if there is a leak.  Since air can be compressed and water can not,  it will take a long time for the air pressure to drop very much where as with water you will know right away if there is a problem.  

I have attached a testing procedure that will guide you through the process.  Use a target pressure of 125 psi.

HDPE pipe while not indestructible,  it will take some abuse and still perform as needed.  It sounds like you will be OK.  Especially if it passes the test since system pressure doesn't need to higher than 40 psi and you will be testing at 125 psi.

Hope this helps


(the attachement is to large)

email me and I will send it to you

dean at palacegeothermal.com


Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
pachaiUser is Offline
New Member
New Member
Send Private Message
Posts:35

--
08 May 2011 10:38 PM
Did anyone hear how this project from 2008 worked out?
The straight pipes in lieu of slinkies intrigued me.
I tried to PM egser, but I am not sure my message was accepted.

Thanks
Seth


hausfxrUser is Offline
New Member
New Member
Send Private Message
Posts:53

--
09 May 2011 12:24 AM
Seth,

Due to an almost complete complete lack of work since the recession began, we have not installed the heat pump, but instead have been heating with the water heater.  We hope to have it installed next year.  We are also hoping that the price of heat pumps has been coming down as their popularity increases.  The lowest bid we got in 2008 for just installing the manifold, perging the pipes, heat echanger, and heat pump was $11k for a WaterFurnace 3 ton water to water unit. 

As I have mentioned elsewhere, the only thing we would have done differently so far was not to dig 5' foot wide trenches - the logistics of managing the soil on a small lot were extremely time consuming.  Stick to 2' wide trenches. 



pachaiUser is Offline
New Member
New Member
Send Private Message
Posts:35

--
09 May 2011 12:53 AM

As I have mentioned elsewhere, the only thing we would have done differently so far was not to dig 5' foot wide trenches - the logistics of managing the soil on a small lot were extremely time consuming. Stick to 2' wide trenches.


Do you mean, dig a 2' trench, put in 2 pipes, dig another 2' trench, 2 pipes - same amount of pipe/spacing,
but less dirt buffer space needed.


hausfxrUser is Offline
New Member
New Member
Send Private Message
Posts:53

--
09 May 2011 02:51 AM
What we did was to have six pipes in the 5' wide trench sections at 12" o.c., then three pipes in the 2' wide trenches at 12" o.c.  Same spacing, just less dirt to move at any given time.


joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
09 May 2011 08:30 AM
Posted By esger on 09 May 2011 12:24 AM
Seth,

 We are also hoping that the price of heat pumps has been coming down as their popularity increases.  The lowest bid we got in 2008 for just installing the manifold, perging the pipes, heat echanger, and heat pump was $11k for a WaterFurnace 3 ton water to water unit. 



I'm sorry, but you are likely to find the price has modestly increased, as longer warranties and efficiencies are required by energy star and R22 units are off the table.
j


Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
pachaiUser is Offline
New Member
New Member
Send Private Message
Posts:35

--
09 May 2011 09:08 AM
Posted By esger on 09 May 2011 02:51 AM
What we did was to have six pipes in the 5' wide trench sections at 12" o.c., then three pipes in the 2' wide trenches at 12" o.c.  Same spacing, just less dirt to move at any given time.
esger,
Thanks for the info... What I was wondering is if your system is up and running....
and if the straight pipes are giving the temperatures you need.

Thanks
Seth





hausfxrUser is Offline
New Member
New Member
Send Private Message
Posts:53

--
09 May 2011 12:10 PM
Seth,

We are curious to know how the system will perform too... someday.  All I can say is that the engineer/geothermal contractor that recommended we not use the slinky has been doing just geo here in the greater Portland area for over twenty years and everything he has said arguing for straight runs makes sense and he can back that up with calcs and installed functioning systems.  But it makes the most sense especially for a DIYer - why go through all that hassel of creating and placing the slinky when you can just roll out your pipes and be done with it.


docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
09 May 2011 01:11 PM
I could back the case for slinkies up with actual real time monitoring of performance.

http://www.buffalogeothermalheating.com/sample_diagram.html

All the horizontal loops are slinkies.

Both work the same if designed correctly, we need 30% more pipe versus straight pipes, but save 2/3 of the excavation.

I also scratch my head and wonder why someone would go through all the trouble of unwinding the coil when you can just spread it out fixate it with some wires, roll it up, and roll it out in the trench, and the excavator can start backfilling 10 seconds later? It would have avoided all the difficulties during your install.


www.buffalogeothermalheating.com
hausfxrUser is Offline
New Member
New Member
Send Private Message
Posts:53

--
09 May 2011 02:50 PM

DocJenser,

You are right about the ease of placement of the slinkies.  Before I started my project, I helped a DIYer create his slinkies and place them in the ground.  The problem he had was trying to make them all a uniform diameter of 32" with the coils often having a diameter of 36" as we stretched them.  It just meant al lot of pulling/pushing and definitely required two people.  His system was half again as big as mine and it took us several hours to make up all the coils with our handicap of inexperience.  I can imagine with you doing the slinkies all the time, they go together very rapidly.  I can also see from my experiences the simplicity of just unrolling the coil over having to stake the pipes at the corners as was required when turning corners, etc.. 

In my project with straight runs the coils tended to get the strange knot I've described earlier in this thread if you did not unwind them correctly.  Our pipe placement project was broken into two stages after I sent the excavator away after his third mishap.  I called the geo contractor to tell him about the hassle of the pipe knots in placement and he recommended we make an H shaped flat piece of plywood, cut it in two then reconnected to form a spool for our coils.  That worked perfectly and prevented the coils from kinking and made them overall very easy to handle.  He said his crew is experienced enough that they never have the knotting problem, but he's seen it many times with the inexperienced.   Still, even with the three times the coils got knotted, I remember thinking how much faster it was to just roll out the coils rather than create the slinkies too.  I'd estimate it probably took an hour’s worth of time total to unwind the coils, not including making and installing the plywood spools. 

The one thing the straight runs gave us over slinkies was flexibility in placement.  We ran individual sections of the pipe 30" below the bottom of gravel level of our basement slab at 4' o.c. in one place and there were a few places that we put all the pipes in one narrow trench (still spaced and in two layers) just for logistical reasons of existing shrubbery, etc. 

We were also trying to contact as much area of our limited lot as possible, and it was the engineer who showed us his logic of using less pipe with straight runs but contacting more soil overall. 

Seth,

My experience is anecdotal and very, very limited and DocJenser has installed and monitored both system types and would probably be willing to provide links to documentation to prove how slinkies make better long-term economic sense if you asked him.  I have not followed your postings on your trench layout that you posted in the fall, but they were initially very complicated and I wondered about the logistics of machinery access, etc.   I hope you've tapped some of the professional brainpower here and gotten some feedback on your plans.  Post you plans or paste a link to your latest discussion thread.



pachaiUser is Offline
New Member
New Member
Send Private Message
Posts:35

--
10 May 2011 12:15 AM
I'll try to attach a quick sketch I just did - somewhat based on discussions here.

The lot is 52' x 104'
The driveway is 104' x 9'

When they were installing the foundation wall, I had them
embed 2 "NDS Sewer pipes"  6" Diam x 2' long, below the frost line.
This way, I can do the geo later without harming the waterproofing.

The contractor is planning to replace the driveway soon.
I had in mind to ask him to bid out a trench 4' wide x 104' long x 8' deep,
and also a horizontal trench 50' x 4' x 8' deep.
(The NO DIG zone is the root system for a huge tree)

My thought based on the 6 pipes was to make 3 loops
up to the top of the lot, then down to the bottom,
then back to the house.   That's 6*100
and do it again on the horizontal.

But maybe I can do it with slinkies?

Is it possible to make a U turn (or a 4' Diam turn) with
a vertical slinky?   Could I put 2 vertical slinkies and 1 flat
in a single 4' wide trench?

BTW, my enhanced plan was to monitor loop temperatures
and have the computer choose the loops that can afford to
give the most heat.   I may also put solar themal collectors.

I live in NJ - 07055.
The living part of the house will be 2000 SF.
The attic will (by summer's end)  be sealed with closed cell insulation.
The walls will be R15 but I'll be spraying some foam there also.
I have a thermal imaging camera to observe leakage.

Thanks for any suggestions.
Seth



Attachment: Rothenberg_Ground_Loop_1.pdf

jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
10 May 2011 08:39 AM
There is software, such as "Ground Loop Design" that will compare all the different loop options. Maybe someday someone will do two supposedly equivalent loops in different ways (say slinky and straight) and post comparison results here.


Texas CoolerUser is Offline
New Member
New Member
Send Private Message
Posts:22

--
10 May 2011 11:16 AM
Posted By jonr on 10 May 2011 08:39 AM
Maybe someday someone will do two supposedly equivalent loops in different ways (say slinky and straight) and post comparison results here.


Hopefully later this summer I will have my demo system up and running. Currently in process of installing a 2-ton climatemaster package unit in my shop to heat/cool the office. Planning on 2 horizontal loops and 2 vertical loops with valving and manifolds to isolate each.


docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
10 May 2011 12:00 PM
Posted By pachai on 10 May 2011 12:15 AM
I'll try to attach a quick sketch I just did - somewhat based on discussions here.

The lot is 52' x 104'
The driveway is 104' x 9'

When they were installing the foundation wall, I had them
embed 2 "NDS Sewer pipes"  6" Diam x 2' long, below the frost line.
This way, I can do the geo later without harming the waterproofing.

The contractor is planning to replace the driveway soon.
I had in mind to ask him to bid out a trench 4' wide x 104' long x 8' deep,
and also a horizontal trench 50' x 4' x 8' deep.
(The NO DIG zone is the root system for a huge tree)

My thought based on the 6 pipes was to make 3 loops
up to the top of the lot, then down to the bottom,
then back to the house.   That's 6*100
and do it again on the horizontal.

But maybe I can do it with slinkies?

Is it possible to make a U turn (or a 4' Diam turn) with
a vertical slinky?   Could I put 2 vertical slinkies and 1 flat
in a single 4' wide trench?

BTW, my enhanced plan was to monitor loop temperatures
and have the computer choose the loops that can afford to
give the most heat.   I may also put solar themal collectors.

I live in NJ - 07055.
The living part of the house will be 2000 SF.
The attic will (by summer's end)  be sealed with closed cell insulation.
The walls will be R15 but I'll be spraying some foam there also.
I have a thermal imaging camera to observe leakage.

Thanks for any suggestions.
Seth




With slinkies you would get the most of heat out of it per linear foot of trench. Yes, the most squeeze would be 2 vertical ones and also some horizontal ones. Keep in mind that the loopfield must be balanced, same pipe and same length for each loop. Stay away from the house wall for at least 3'. Why can't you make the trench 6 feet wide? 2 loops on the bottom, 2 verticals on the side. You have 9' of driveway, you should be able to get 4 slinkies there, 800' each. Yes, no problem to turn a slinky within 4'. Just be careful during backfilling, that you do not knick it.


www.buffalogeothermalheating.com
hausfxrUser is Offline
New Member
New Member
Send Private Message
Posts:53

--
10 May 2011 12:16 PM

Seth,

You have some serious logistical challenges, not the least of which is you have very little yard area available.  Your driveway appears to be about 9.5' wide to the property line.  Only if you dug maybe an 18" wide trench 12" from the property line and 6' deep would you be able to place the soil next to the trench.  While there are some strategies to dig bigger trenches in this section if you move the soil elsewhere, your bigger problem is simply getting enough length of trenches.  It's advisable that you make all your loops approximately the same length so that you can get the same flow rate through each, so from what I can see you need to run one loop(s) toward the back of your house and another to the front and turn into your front yard, both starting from the basement access point.  At most, those two trenches would be 160 feet each, and I can't see you having enough of a heat sink to draw upon in any scenario, but you'll have to get the feedback of the professionals on this site.    

Does your driveway need replacement?  Why go through all the expense of demoing and hauling the concrete and pouring a new slab.  That alone would cost you at least $5k, so why not put that money towards a drilling vertical well? 