Posted By engineer on 11/23/2008 2:55 PM
Bill - 29 KBtu from 5 kWh translates to a COP of 1.7. I find that hard to believe given your Envisions and ground temp. Are you sure of those numbers?
Dewayne's rule of thumb works out to a COP of 3.5, perhaps a bit conservative for well-designed systems but useful for ballpark guesstimates.
I looked at the wrong line. I apologize. Total HVAC KWH for me today is 4.2 (all in heat mode, includes both units). Total KBTU transfered is 29 (again combined for both units). W/BTU is thus 0.14, which is the same as 1.7 KWH/ton (assuming 1 ton is 12,000 BTU).
I'll need some help seeing the relationship to COP. And perhaps this is best left to another thread, so as to not dilute from this one.
(COP is {(HE + P) / P), where HE is Heat Extracted in BTU/h and P is Power in Watts. My numbers are total BTU for the day and KWH for the day.)
Best regards,
Bill