Posted By joe.ami on 12/01/2009 9:03 AM
Posted By ANGELofDEBT on 12/01/2009 7:34 AM
I guess my concern was with the normal pipe layout and the fact that the out and return pipes were "close" to each other. Being that the pipes were 4' apart I wasn't sure if that was enough distance so as to cause efficiency loss.
If proximity (in your drawing) caused efficiency loss, both systems would be impacted equally.
Putting loops farther apart improves efficiency, but in geo all things are diminishing returns. If you were going to have an operator spend extra time seperating your loops, you may not appreciate a significant ROI for the expense.
J
By the pipes being close to each other my concern was on a convential loop you have 4' separation. So at the end part of the loop one pipe will be EWT and the other will be LWT.
This could be as much as 20 degrees difference. I see that as a possibility of loss of efficiency. The only issue I don't know is what sort of temperature gradient the ground has next to the pipe.