geotek
 Basic Member
 Posts:154
 |
| 05 Dec 2009 11:48 AM |
|
It does 1st stage -- just not for very long
First stage is 2.8 tons that's .3 ton different from your load. I would open all dampers and bypass Intellizone before I assumed unit was over sized. This summer was a cool one by most accounts.
|
|
|
|
|
MPH
 New Member
 Posts:13
 |
| 05 Dec 2009 12:01 PM |
|
Actually, the total load calculated for the system by the energy star rater was 2.5 and, (and if memory serves that was with a small round up). |
|
|
|
|
MPH
 New Member
 Posts:13
 |
| 05 Dec 2009 12:08 PM |
|
I'm not "assuming" anything. I've been told that the unit is oversized by a contractor who tested it along side the WaterFurnace territory manager. They spent two hours running tests on the equipment. The contractor chose his words very carefully in the letter I asked him to write. But he looked me in the eye and told me the unit was oversized. Two different energy star raters know this house and the equipment. They both say it is grossly oversized. I wish it wasn't the case. But it is. |
|
|
|
|
geome
 Advanced Member
 Posts:987
 |
| 05 Dec 2009 12:22 PM |
|
Is this correct? Let's assume the energy star rating was 2.3 tons for argument sake. If 1st stage is 2.8 tons then there is a .5 ton difference. .5/2.3=roughly 21.7% oversized for 1st stage. With fan speed, and other tweaks, shouldn't the system be ok (not great, but ok) for dehumidification in 1st stage?
Joe, do I recall you saying that zoning can be difficult to get right, or something to that effect?
At least, I assume, aux won't be needed for the coldest winters.
MPH, what temperature setting did you use in the summer for day/night? When we keep our house on the warm side (75-76 degrees) our unit doesn't run very much and indoor humidity is higher. |
|
| Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon. |
|
|
MPH
 New Member
 Posts:13
 |
| 05 Dec 2009 12:37 PM |
|
I really appreciate the effort here. My thermostat setting during the summer was at 72--sometimes lower just to get some of the humidity out of the air. :o) |
|
|
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 05 Dec 2009 12:52 PM |
|
4 zones will almost certainly demand a bypass or dump zone, especially since unit is oversized.
Are you absolutely positive that only low stage is coming on?
|
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
MPH
 New Member
 Posts:13
 |
| 05 Dec 2009 01:18 PM |
|
What do you mean by a dump zone? |
|
|
|
|
geo fan
 Basic Member
 Posts:408
 |
| 05 Dec 2009 03:55 PM |
|
a few points
4 zones is a significant contributer to the short cycling ( joining some zones together may be a start ) roughly 75% RH in the crawl space is an issue well worth adressing independent of the fact it is a MAJOR contributing factor to the homes humidity issue " It does 1st stage -- just not for very long " in your situation I would strongly consider disabling 2nd stage alltogether or setting it up to only run when specificly asked for . As well as not running continues fan as engineer pointed out limiting or eliminating the post purge fan time will also help "dump zone = an area(s) of the home where you dump the extra air , (there because your zoneing system is varying the overall duct size) so the air is not being pushed with as much speed and volume to the area calling , when having the system run longer is the name of the game it will help , but it sounds like the "adjusting zone damper setting " allready addressed that by setting the dampers to not close all the way , could be wrong there though just a guess. |
|
|
|
|
geotek
 Basic Member
 Posts:154
 |
| 05 Dec 2009 07:48 PM |
|
"dump zone = an area(s)
of the home where you dump the extra air , there because you zoneing
system is varying the overall duct size, so the air is not being with
as much speed and volume to the area calling , when having the system
run longer is the name of the game it will help , but it sounds like
the "adjusting zone damper setting " allready addressed that by setting
the dampers to not close all the way , could be wrong there though just
a guess.
geofan
You are on to something there but the Intellizone is demand driven so if 2 or 3 zones call it will go to second stage. Adjusting the damper setting will not help that.
I just remembered that it also central zone switch which will operate all zones from zone 1 thermostat, now that might be worth a try.
|
|
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 05 Dec 2009 08:21 PM |
|
Posted By MPH on 12/05/2009 8:36 AM The crawl space IS sealed. I mean all the tests have been performed and the data is being withheld from me. So you don't have a thread on your particular situation or answers to fundemental questions, you just want to squawk in the middle of someone else's thread. A lot of intelligent and well meaning people are here to help. Why don't you look up "help us help you", start a thread answer some questions and we might be able too. j |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 05 Dec 2009 08:24 PM |
|
It is a simple matter to mount a hand switch between Intellizone's Y2 output and the unit's y2 input. That'll stop the compressor from upstaging although the blower will still ramp up - hence my suggestion to use 5 lowest dip switch settings for CFM. |
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
MPH
 New Member
 Posts:13
 |
| 06 Dec 2009 08:58 AM |
|
Joe,
I posted on this particular thread because it was subject appropriate. I know a lot more about my hvac system than most people but I'm not an expert. I trusted the experts. I've had the experts out here and they've diagnosed the problem for me. I think I have answered most of the questions asked. There are other answers but those would be in the hands of the gentleman who ran the tests and he will not return them to me. I'm not inclined to perform the tests myself. I really wouldn't know where to begin. I'm a homeowner. I'm not supposed to be the expert. I am thankful that I had the good sense to start monitoring my humidity levels. Most homeowners don't do that -- which is probably why most don't realize they have some of the same problems I do. I will certainly gather up all of the thoughts and suggestions posted here and bounce them off of the people I work with to solve the problem. |
|
|
|
|
Alex_in_FL
 New Member
 Posts:96
 |
| 09 Jan 2010 08:45 PM |
|
A few points to keep in mind: 1. A load calculation is just an estimate - it is not a perfect number. And it depends upon the temperatures used (outside and set point). 2. A load of 2.5 tons means this is the peak requirement for about 98% of the time. Therefore if the load was 2.5 tons and they installed a 2.5 ton unit you still have an oversized unit except for the hottest part of the hottest days of the year (and yes, on two days of the year you probably have a slighly undersized unit). 3. Studies do not confirm the belief that perfectly sized units dehumidify better than oversized units. A study by FL solar actually found that after installing new units based upon manual J calculations (most new units were 0.5 to 1.0 tons smaller) that the interior humidity actually increased ever so slightly. 4. A larger unit has a larger latent heat removal ability (i.e. provides more dehumidification) per minute of run time. This is the overlooked factor. For example, a 4 ton unit removes about twice as much water as a 2 ton unit per minute of run time. The 4 ton unit runs 1/2 as long. Therefore, the humidity removal is practically the same.
If your house is running at a slightly negative pressure then you are probably pulling in more humidity than you realize. Quite possibly you are drawing air up through your floor which might even be more humid than outside air - especially if you are irrigating your yard.
If I were the dealer here are the questions I would ask. If I replace your 4 ton unit with a 2.5 ton unit and you still have humidity problems are you going to pay me for the costs or do you expect me to just eat them? And are you then going to be happy when in the middle of summer you get hot or are you going to call me again complaining that the unit is not working properly?
If you have spent as much as you say ($25K I think) then go talk to an attorney and ask him to draft a letter demanding satisfaction. Have him send the letter to both the installer and the manufacturer and the BBB. This should cost you between $50 and $75 at most.
It really sounds like you are going to need a dehumidification unit - no matter what size unit you have installed.
I don't have a dog in the hunt but thats my take. Best of luck what ever you decide to do (and my apologies to the thread owner for joining in this slightly off topic discussion).
Alex
|
|
|
|
|
rayder070
 New Member
 Posts:2
 |
| 03 Feb 2010 05:20 PM |
|
As far as comparing Geothermal manufacturers, my only experience is with WaterFurnace International and they have to have the worst customer service of any company I have ever dealt with. We built a new home in 2002 and installed a two Premier E series two speed units. We used an authorized WFI dealer recommended by the WFI Territorial Sales Manager who told us this was the only dealer in the area I should let install my system. For six (6) years we've had nothing but problems with the units and their installation. We would go anywhere from a few days to a couple of weeks without service. I called WFI on numerous occassions and begged them for help in correcting the problems. They basically told me I was on my own and refused to help. Almost two years ago the main unit shut down making a majority of the house unuseable. We are now in litigation with WFI and the company they recommended for us to use to install the units, so maybe after eight (8)years of never knowing if we will have heating or cooling when we get home we can get units installed and operating properly. Our court date is March 1, 2010.
As a builder, I feel I have bent over backwards to avoid the situation we are now in with WFI. In reading post on different blogs it appears our problems are just a small part of a bigger pattern to how WFI operates and in our case some of their actions I feel will be considered criminal. |
|
|
|
|
MPH
 New Member
 Posts:13
 |
| 15 Feb 2010 09:25 PM |
|
Just to clarify, I did some checking on the report that Alex mentioned. I had not heard about the study or anything that suggests that larger units dehumidify better than smaller ones--so this really concerned me. Alex noted: "3. Studies do not confirm the belief that perfectly sized units dehumidify better than oversized units. A study by FL solar actually found that after installing new units based upon manual J calculations (most new units were 0.5 to 1.0 tons smaller) that the interior humidity actually increased ever so slightly. " However, after looking into it, I don't think this really applies to my home which is brand new. For one thing, I believe this study was on much, much older homes in Florida with really leaky ducts and from my understanding, that was shown to be the real culprit. As part of my Energy Star package, my ducts were tested for leakage and performed extremely well so I don't think I would experience the same penalties for a properly sized system.
|
|
|
|
|