It's time to crunch some numbers!! (Operational Costs)
Last Post 01 Feb 2011 02:51 AM by pjc57. 96 Replies.
|
Sort:
|
|
Prev Next |
You are not authorized to post a reply. |
|
|
|
egouin
 Basic Member
 Posts:126
 |
| 01 Dec 2009 06:46 AM |
|
Posted By joe.ami on 11/30/2009 10:06 PM Once again, running a 4 COP heat pump 4 times as long as a 1 COP aux coil costs the same. Blanket statements where auxilliary coils are concerned really aggravate me as it has a lot ot do with system design. If 2 stages are good, why won't folks accept that 3 are better? joe This should be simple to understand... 1kWh of electric power to the resistance coils will supply ~3413 BTUs of heat to your house (this is at 100% efficiency). Use that same 1kWh to power a GSHP with a COP of 4.0 and you get ~13,652 BTus into your house. This IS why geo is what it is. I will make the blanket statement --- stage 3 is always BAD! It is simply electric resistance, and for most people it IS the MOST expensive way to heat a house. In a properly sized system, the 3rd stage (called "emergency heat") is only supposed to come on when the heat pump can't keep up with demand with stage 2 running 100% of the time. Setbacks create somewhat artificial situations. For example, the house drops to 65 at night. At 7AM the thermostat says it is suddenly supposed to be 70. The pump kicks on (1st and 2nd stages) but still the house isn't yet at 70. Stage 3 kicks on because this is "an emergency". Efficiency of the system drops drastically. If you want to use setbacks, rather than leaving it at the same set point all the time, do something to stop that electric coil from heating up. the house will take longer to heat up, but it will be done with the full - efficiency - of the heat pump. Regards, Ed Mr. Green Dreams See my house at: www.GouinGreen.com
|
|
| http://www.GouinGreen.com<br>Superinsulated SIP/Modular House (HERS = 30)<br>GSHP w/SCW, ERV, Passive Solar, Solar HW |
|
|
decafdrinker
 Basic Member
 Posts:420
 |
| 01 Dec 2009 07:18 AM |
|
Sensible setbacks and smart thermostats really should eliminate aux heat except in emergencies, which if I had an emergency, I'd take aux heat!
As of right now, aux is manually off at my house, and I'm trying to see just how GREAT this system is. So far, EXCELLENT! Even with 8 degree setbacks at night and during the day, the house warms right up within an hour or two (it comes on around 4:30 AM to get the house to temperature by 6:30 AM), with no aux heat.
That, in my mind, as a general consumer/homeowner, is what I hoped to see, and I am HIGHLY recommending these systems to everyone I know.
What I'd really like to find out is when EXACTLY the system is coming on early to heat up the house. I was thinking of putting ribbons on one of the floor vents, pointing the laptop camera at the vent, and taking pictures every couple minutes. Then I can look back and see when the system activated for its recovery period! I'll try to find out and post those results, too. |
|
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 01 Dec 2009 08:50 AM |
|
Posted By egouin on 12/01/2009 6:46 AM
Posted By joe.ami on 11/30/2009 10:06 PM Once again, running a 4 COP heat pump 4 times as long as a 1 COP aux coil costs the same. Blanket statements where auxilliary coils are concerned really aggravate me as it has a lot ot do with system design. If 2 stages are good, why won't folks accept that 3 are better? joe[/quote]This should be simple to understand... 1kWh of electric power to the resistance coils will supply ~3413 BTUs of heat to your house (this is at 100% efficiency). Use that same 1kWh to power a GSHP with a COP of 4.0 and you get ~13,652 BTus into your house. This IS why geo is what it is. Okay, you do not approve of my oversimplification. Since you have obviously thought through this, let's examine it more closely. 4.0 COP (this should be easy to understand) only occurs when a heat pump doesn't have to work very hard (small load requirements) and never occurs when the heat pump is running full out. Among things that affect it are EWT which falls when used. Furthermore a 10* swing (as we were talking about set backs) can easily cause a greater btu requirement than the capacity of the heat pump.
I will make the blanket statement --- stage 3 is always BAD! It is simply electric resistance, and for most people it IS the MOST expensive way to heat a house.
In my area, the price of electricity is such that once propane is over ~$2.25 gallon, electric heat becomes cheaper. The only thing that is worse than stage 3 is a heat pump sized so that it is not needed. A 5 ton compressor to cover a 48000 btu load in January will cost the consumer more to operate year round than a 3 ton compressor and auxilliary heater. That's a fact. You want to look at open loop? A 4 ton will cost about the same to operate as the 3 ton with auxiliary but will often pump a few extra thousand gallons of water off setting potential savings. That's a fact. Your blanket statement is true with oversized systems only. So perhaps you could say "stage 3 is bad with an improperly designed system." I speak of course of my experience in my area, but geography matters little with "blanket statements".
In a properly sized system, the 3rd stage (called "emergency heat") is only supposed to come on when the heat pump can't keep up with demand with stage 2 running 100% of the time. In a properly sized system 3rd stage is supposed to come on when temperature dips below balance point or demand is for sudden dramatic temperature swing.
Setbacks create somewhat artificial situations. For example, the house drops to 65 at night. At 7AM the thermostat says it is suddenly supposed to be 70. The pump kicks on (1st and 2nd stages) but still the house isn't yet at 70. Stage 3 kicks on because this is "an emergency". Efficiency of the system drops drastically. I can agree with the point that efficiency drops dramatically when recovering from setbacks. Was enough saved to justify it?
Regards, Ed Mr. Green Dreams
See my house at: www.GouinGreen.com
To sum this up, Interfering with system design seldom saves money. Design auxiliary out of a system seldom saves money. Over use of a loop field runs the risk of dropping efficiency all year to save a little on auxiliary in marginal situ's. ......in heating dominated climates. j |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
decafdrinker
 Basic Member
 Posts:420
 |
| 01 Dec 2009 09:02 AM |
|
Wow, exciting stuff this discussion. |
|
|
|
|
egouin
 Basic Member
 Posts:126
 |
| 01 Dec 2009 09:18 AM |
|
ok, so going on what you stated regarding lowering efficiencies... I have Climate Master Tranquility 27 units. I am using ground water (standing column well) so I will never get down below 32F without having freezing issues. That would call for emergency heat and/or emergency bleed from the well. In any case, the efficiency table for my units shows:
When running on 2nd stage - at 9.0 gallons per minute with 1250 CFM airflow: COP @ 50F EWT is: 4.68 / COP @ 20F EWT is: 3.51.
One could argue that even if the COP dropped to 2.0 it is still more efficient than electric resistance (which can never be more than 1 and is more likely 0.95-0.98).
One more general statement - From a physics point of view, temperature change is energy intensive. In all likelihood, a well sealed, well insulated house is going to use less energy to keep at a steady state (temperature) than allowing it to cool and then heat it back up.
Personally, I have disabled the setback feature on my thermostats. Our heating (and cooling) is set to 69F year round. However, my house is quite a bit more insulated than most houses.
Ed www.GouinGreen.com
|
|
| http://www.GouinGreen.com<br>Superinsulated SIP/Modular House (HERS = 30)<br>GSHP w/SCW, ERV, Passive Solar, Solar HW |
|
|
cnygeo
 Basic Member
 Posts:170
 |
| 01 Dec 2009 09:25 AM |
|
Posted By joe.ami on 12/01/2009 8:50 AM
A 5 ton compressor to cover a 48000 btu load in January will cost the consumer more to operate year round than a 3 ton compressor and auxilliary heater. That's a fact.
Wait, what? I don't agree with this at all, assuming that the loop field is properly sized to the 5-ton unit. There's no reason a 5-ton unit can't have the same COP as the 3-ton for a given loop temperature. I could see only 2 places where the system efficiency would be lower for the larger unit - a larger loop pump might be required (partially offset by the fact that the 5-ton will run for a shorter time) and more frequent cycling (not sure how to quantify this). I bet in most cases the aux heat and the slight drop in efficiency for the larger unit would be a wash at worst. Again, it comes down to individual system design and optimization. If you want to say that the 5-ton will never pay for itself because the additional savings is small I can see that, but I'll need some convincing that the operating cost would be higher. |
|
|
|
|
TechGromit
 Advanced Member
 Posts:634
 |
| 01 Dec 2009 09:28 AM |
|
Posted By stuart.wyss on 12/01/2009 7:18 AM Sensible setbacks and smart thermostats really should eliminate aux heat except in emergencies, which if I had an emergency, I'd take aux heat!
I agree, when the house is 5 degrees colder than the setpoint isn't an emergency in my opinion, an emergency is when the geo system isn't working period. Thermostats should be designed to allow you to set emergency conditions, when it's a greater range from the thermostat setpoint you select, or if the temperature drops below X, that you define (maybe 50 degrees). I too have my AUX heat disabled, but It's disabled via dip switches since the blower and Aux heater are on the same circuit. There is always the risk that the system will stop functioning on the coldest of winter days when I'm out of town and the house pipes will freeze cause the AUX is disabled. This is very remote possiblity, but could happen. They do make thermostats that "learn" how long it takes to heat a house back up from a setback and automatically adjusts the time it begins heating the house back up based on how long it took to heat the house up from the pervious day. Now weather or not these are compatiable with geo systems, I'm not so sure. |
|
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 01 Dec 2009 09:29 AM |
|
:) It's not the first it's been discussed. Remember this, I invite my customers to experiment but caution against certain things. One of which is the assumption that all aux. use is bad. It is after all designed in and among other things saved the H/O thousands on initial investment. On an estimate the other day the homeowner and I discussed the difference between a 3 and a 4 ton for his job. The 4 ton actually ran for about $70 less/yr but cost $2,000 more to install. With tax credits payback was only 20 years. You can make a case for either, but once it is made if the 3 ton is chosen you might not want to disable the aux. too much. Have a frank discussion with your installer, and you might spark some interest in him...... "look I was going to get a monitoring system and try different set-backs and such and compare the results, i'd be glad to share the outcome if you're interested." an affirmitive response would be enough to keep warranties intact. If you can communicate via E-mail you'll have a response to print. Regarding the results you are experiencing right now remember that this weather is mild and it is true you would not need aux. except for situations you are creating. Just remember when it gets cold, you can actually extract btu's from the field that you'd wish you had later. Colder EWT's caused by aux interuption drop COP for the long haul. In the case I mentioned above if he had were to disable aux in weather like last January's he might have spent half of Feb. on emergency heat. In our area electric rates are such that these "huge" costs of auxilliary heat are measured in nickels and dimes. So if someone's experiment went too far and they had to run emergency heat full out for a whole day, it would cost $18 for a 10K. Even at $540 for 30 days that is still less than a lot of propane bills around here. So again experiment, but not with the "aux is bad" bias, it is simply one of the possible ingredients to the best performance of your system. As far as results, run your tests during a winter with temps lower than those on the bin report and you'll have a good measurement of performance. J
|
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 01 Dec 2009 09:43 AM |
|
Wow more responses while i was typing. Ed, we've had this debate before and failed to convince one another, but again what I feel you are missing is that the lower EWT's impact far outlives the aux. requirement. So you are penalizing your efficiency for hours to come to save a few cents now. You also are skipping the point that you must pump more water (now and later) because of this, and if I recall your system is installed at 100% load which may not be true of the folks you are advising. Respectfully, I only object vehemently to the "blanket statement". We can argue the rest til the cows come home without me getting particularly excited.
CNY, Look at it like this when first stage is required on the 3 ton mentioned which is a large portion of the year, it is drawing very little amperage, while the 5 ton may still be at or near 20. If you have operating cost calc software plug this in. The 5 ton costs you more to run (in heating dominated climate) in bumper seasons and all summer it also has shorter run times and fails to contribute as much to the hot water production. Not loading for 100% is because we know it is for a small fraction of the year. A 5 ton compressor will draw more amps year round than anything but the aux. coil. So yes, you will find the 3 ton cheaper to operate when satisfying all your heating/cooling/hotwater requirements. j |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
egouin
 Basic Member
 Posts:126
 |
| 01 Dec 2009 10:12 AM |
|
J - Do you have Geo installed in your home? If so, please tell us about it. Utility Bills for my house - Total electric (entire house + geo) and propane (some HW and fireplace for ambiance) - total cost 12/2008 to Mid 11/2009 - $4,843.57
Neighbor’s house – total electric, oil, and cord wood cost since 12/2008 to Mid 11/2009 - $6,124.86 Houses are of similar size (~3,800 fqft) with similar finish materials. Theirs is conventional 2x6 with fiberglass, mine is SIP. I acted as the GC. They hired someone. My house cost $200k less to build (including land). I met and interviewed a lot of contractors / sub-contractors over the past 3-4 years. I have yet to meet even one who cares as much about my utility bills as I do. At this time I have no way to separate geo costs from the remainder of the house. I am working on a plan to sub-meter so we can get some hard numbers. BTW - Electricity in my area is ~$0.18 per kWh (ouch!). On average our area has 6990 HDD annually. We do not use setbacks of any kind. Aux heat is locked in the off position. The units have never shut down due to low temperature. Ed www.GouinGreen.com |
|
| http://www.GouinGreen.com<br>Superinsulated SIP/Modular House (HERS = 30)<br>GSHP w/SCW, ERV, Passive Solar, Solar HW |
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 01 Dec 2009 08:39 PM |
|
The proponents of 100% geo sizing are missing another significant issue - cycling losses. A unit does not produce anywhere near advertised COPs during the first several minutes of operation. It takes awhile for refrigerant pressures to build.
For example, a 3 ton unit might run continuously to meet a certain load. Alternatively, a six ton unit could meet the same load by running half the time, in theory. In fact, the six ton would run more like 60-65% of the time to compensate for cycling losses.
Morever, within a given manufacturers product line, the smaller units, 2-3 tons, tend to be the most efficient. The bold print claims of "up to 30 EER or 5 COP" tend only to apply to the smaller units. The 5-6 ton units are somewhat less efficient.
PS: When I use major east-west roadways of the Interstate system to delineate different design zones / criteria I am certainly guilty of making "blanket" statements - its just a handy easily-visualized demarcation between different ways to think about system performance |
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 01 Dec 2009 10:24 PM |
|
Posted By egouin on 12/01/2009 10:12 AM J - Do you have Geo installed in your home? If so, please tell us about it. Utility Bills for my house - Total electric (entire house + geo) and propane (some HW and fireplace for ambiance) - total cost 12/2008 to Mid 11/2009 - $4,843.57
Neighbor’s house – total electric, oil, and cord wood cost since 12/2008 to Mid 11/2009 - $6,124.86 Houses are of similar size (~3,800 fqft) with similar finish materials. Theirs is conventional 2x6 with fiberglass, mine is SIP. I acted as the GC. They hired someone. My house cost $200k less to build (including land). I met and interviewed a lot of contractors / sub-contractors over the past 3-4 years. I have yet to meet even one who cares as much about my utility bills as I do. At this time I have no way to separate geo costs from the remainder of the house. I am working on a plan to sub-meter so we can get some hard numbers. BTW - Electricity in my area is ~$0.18 per kWh (ouch!). On average our area has 6990 HDD annually. We do not use setbacks of any kind. Aux heat is locked in the off position. The units have never shut down due to low temperature. Ed www.GouinGreen.com No Ed, I do not have geo in my home, just several other folks homes- for reasons explained here (on this forum) and elsewhere. Your response neatly ignores all my previous points (and olive branch). Are you suggesting you are more of a geo expert because of your case study of 1 home than I with my 12 years in geo? joe |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
decafdrinker
 Basic Member
 Posts:420
 |
| 02 Jan 2010 07:01 PM |
|
Okay, bill just arrived for December's usage: $200. $100 (as previously explained) is what I'm considering normal usage sans heating of any kind (house/water). So, geothermal cost for December was $100. I'll do all the math in another post about heating degree days, etc. However, the house previously used $300/mo oil for heating, so geo saved $200 last month over the cost of oil (and oil certainly didn't go down much since November!) |
|
|
|
|
TechGromit
 Advanced Member
 Posts:634
 |
| 02 Jan 2010 07:15 PM |
|
Posted By egouin on 12/01/2009 10:12 AM J - Do you have Geo installed in your home? If so, please tell us about it. Utility Bills for my house - Total electric (entire house + geo) and propane (some HW and fireplace for ambiance) - total cost 12/2008 to Mid 11/2009 - $4,843.57
Neighbor’s house – total electric, oil, and cord wood cost since 12/2008 to Mid 11/2009 - $6,124.86 Houses are of similar size (~3,800 fqft) with similar finish materials. Theirs is conventional 2x6 with fiberglass, mine is SIP. I acted as the GC. They hired someone. My house cost $200k less to build (including land). I met and interviewed a lot of contractors / sub-contractors over the past 3-4 years. I have yet to meet even one who cares as much about my utility bills as I do. At this time I have no way to separate geo costs from the remainder of the house. I am working on a plan to sub-meter so we can get some hard numbers. BTW - Electricity in my area is ~$0.18 per kWh (ouch!). On average our area has 6990 HDD annually. We do not use setbacks of any kind. Aux heat is locked in the off position. The units have never shut down due to low temperature. Ed www.GouinGreen.com My house cost me $2,925 in utility bills (all electric 18,170 KWh) for the year (Nov. 08 to Oct 09), I'm currently running $95 less this year than last. My house is about 3,500 sq ft, located in Southern New Jersey, heated with Zone 1 Geothermal and Zone 2 ASHP.
|
|
|
|
|
TechGromit
 Advanced Member
 Posts:634
 |
| 02 Jan 2010 07:18 PM |
|
| Month |
Bill |
Meter Reading before |
Meter Reading After |
Power used |
Average Temp This month |
Average Temp Last Year |
KWH Daily Averages This Month |
KWH Daily Averages Last Year |
| Nov-08 |
$222.37 |
6287 |
7824 |
1537 |
51 |
47 |
38.3 |
54.9 |
| Dec-08 |
$340.61 |
7824 |
10189 |
2365 |
41 |
42 |
73.9 |
60 |
| Jan-09 |
$403.78 |
10189 |
12999 |
2810 |
37 |
40 |
90.6 |
85 |
| Feb-09 |
$362.06 |
12999 |
15512 |
2513 |
33 |
36 |
78.5 |
88.7 |
| Mar-09 |
$360.27 |
15512 |
18016 |
2504 |
39 |
40 |
86.3 |
75 |
| Apr-09 |
$244.69 |
18016 |
19704 |
1688 |
47 |
48 |
56.3 |
61.2 |
| May-09 |
$138.23 |
19704 |
20640 |
936 |
61 |
58 |
30.2 |
43.7 |
| Jun-09 |
$124.80 |
20640 |
21365 |
725 |
66 |
68 |
24.2 |
45.3 |
| Jul-09 |
$173.57 |
21365 |
22272 |
907 |
72 |
76 |
30.2 |
65.7 |
| Aug-09 |
$214.55 |
22272 |
23385 |
1113 |
76 |
78 |
35.9 |
5.5 |
| Sep-09 |
$206.61 |
23385 |
24457 |
1072 |
73 |
73 |
35.7 |
29.3 |
| Oct-09 |
$133.02 |
24457 |
25224 |
767 |
63 |
61 |
23.8 |
25.6 |
| Nov-09 |
$192.30 |
25244 |
26452 |
1228 |
53 |
51 |
39.6 |
54.9 |
| Dec-09 |
$274.74 |
26452 |
28223 |
1771 |
46 |
41 |
59 |
73.9 |
|
|
|
|
|
TechGromit
 Advanced Member
 Posts:634
 |
| 02 Jan 2010 07:22 PM |
|
If you interested to know why i bother to track the meter reading, it's because sometime before i started tracking the meter readings the electric company replaced the meter, it was a digital meter and now it's an analog one. I don't know why or exactly when it was replaced, I just know it's not the same meter as the one before.
|
|
|
|
|
decafdrinker
 Basic Member
 Posts:420
 |
| 02 Jan 2010 07:39 PM |
|
Here are the updated numbers: Heating degree days covered by the electric bill: 985 Gallons of oil needed (if I still had oil) : 166 Current cost of oil x gallons needed/used = 2.80 x 166 = $465 worth of oil to heat the home last month Electric bill was $200 last month, minus $105 (base cost of house usage with no heating/cooling) = $95 to heat using geothermal Comparison vs. oil = $370 saved vs oil heat.
November 09 savings : $150 December 09 savings : $370
|
|
|
|
|
TechGromit
 Advanced Member
 Posts:634
 |
| 02 Jan 2010 10:50 PM |
|
Having never had anything other than Geo in this house, I have nothing to compare my numbers against. I guess I could compare my figures to a similar sized house in the area that uses Gas or oil, but that's not an exact science. I do have my figures from the year before, and I'm trying to take steps to decrease my energy usage each Month / Year, my goal is to get the energy bills low enough so the electric company is paying me.  Woo Hoo, My 500th post, an Advanced member now. I must know what I'm talking about now. |
|
|
|
|
decafdrinker
 Basic Member
 Posts:420
 |
| 29 Jan 2010 06:23 AM |
|
NOTE: during January I had some thermostat wiring issues, and for about a week, I ran the house entirely on emergency heat. Here are the updated numbers for January: Heating degree days covered by the electric bill: 1044 (according to degreedays.net) Gallons of oil needed (if I still had oil) : 176 (degree days x home oil coefficient) Current cost of oil x gallons needed/used = 2.98 x 176 = $527 worth of oil to heat the home last month Electric bill was $231 this month, minus $105 (base cost of house usage with no heating/cooling) = $126 to heat using geothermal Comparison vs. oil = $401 saved vs oil heat.
November 09 savings : $150 December 09 savings : $370 January 10 savings : $401 - running total: $920 |
|
|
|
|
Ozark01
 New Member
 Posts:26
 |
| 30 Jan 2010 10:21 AM |
|
Can someone tell me if this is correct.
I now heat with propane at a cost of $2.60 a gallon. I used 100 gallons last month to heat with at a cost of $260. At 90,000 BTU per gallon that is 9 million BTU's. I am not taking the efficiency of the gas furnace into consideration.
I am looking at putting in a geo unit with an average COP of 3. To generate 9 million BTU's with this system I would use 659 kw worth of electricity at cost of .105/KW for a total of $69.
Is this pretty close or am a leaving something big out of the calculation? |
|
|
|
|