LoobyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:401
Avatar

--
04 Feb 2011 03:32 AM
WF sells a hydrometer kit (part# CAMT). Waterpirate might be
able to tell you the approx. volume of the measuring cylinder:

http://www.greenbuildingweb.com/Forums/tabid/53/aff/13/aft/66276/afv/topic/Default.aspx

One measurement is worth a thousand expert opinions.
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
04 Feb 2011 10:03 AM
Posted By docjenser on 04 Feb 2011 12:34 AM
Posted By geodean on 03 Feb 2011 08:24 PM
I have one of these.

The picture is lousy as it shows a case with about ten hydrometers.

It fits nicely in a piece of 3/4" PVC pipe


How well do they work?

Very well.
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
geomeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:987

--
04 Feb 2011 10:45 AM
Dewayne, Is the PVC opaque (I see some companies make clear pvc)? If so, do you fill it to the top so you can see the reading on the hydrometer? Did the pipe come with the hydrometer, or did you make it? This would be great, 3.18 fl oz (even less with the hydrometer displacement.)

Eric, when you get a chance, would you measure the diameter of the CAMT cylinder for me? I assume this is a 13" hydrometer?
Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
04 Feb 2011 07:09 PM
The PVC is white so you fill it to the top and then read the Hydrometer which is 12 inches long
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
geomeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:987

--
04 Feb 2011 08:12 PM
Thanks Dewayne. Just confirming, did the PVC come with the hydrometer, or did you make it yourself?
Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.
geomeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:987

--
04 Feb 2011 08:34 PM
Looby (or anyone) would a 0.950 to 1.000 scale be beneficial, or potentially too limiting (i.e. could the SG be less than 0.950 in the loop)?
Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.
LoobyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:401
Avatar

--
04 Feb 2011 10:01 PM
Posted By geome on 04 Feb 2011 08:34 PM
...) would a 0.950 to 1.000 scale be beneficial ...
Sounds about right. You really only need about 0.97 to 0.99
One measurement is worth a thousand expert opinions.
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
04 Feb 2011 10:09 PM
Really?

If alcohol has a specific gravity of 0.78, wouldn't a 20% mixture exhibit a hydro reading of .956? (Interpolating between 1.00 and 0.78)
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
LoobyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:401
Avatar

--
04 Feb 2011 10:13 PM
Really. See attachment (if it attaches).
One measurement is worth a thousand expert opinions.
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
04 Feb 2011 10:17 PM
Fair enough

Took a couple tries to get it open.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
LoobyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:401
Avatar

--
04 Feb 2011 10:24 PM
I still can't get it to work properly -- better yet, see page 21
of the WF Flow Center Installation Manual:

http://www.waterfurnace.ca/Engineer/Flow%20Centres/Flow%20Center%20Installation%20Manual%20-%20IM1961.pdf

One measurement is worth a thousand expert opinions.
geomeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:987

--
07 Feb 2011 02:51 PM
I decided to try the 0.94 to 1.010 model:
http://www.novatech-usa.com/6602-6

About $28.50 with USPS priority shipping. We'll see how many pieces it's in after the USPS drop kicks it over half the country to get it here. :-)

I'll post an update to let everyone know how it works. Thanks again for the advise from the experienced forum members.
Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon.