dgbair
New Member
Posts:54
26 Feb 2011 06:39 PM
Rob, please start a new thread
senr
New Member
Posts:18
26 Feb 2011 09:25 PM
The unit shut down today. The CXM board said Fault Error 8. The installer changed the Capacitor again in 4 weeks.
Any clues why this could be happening?
Thanks again..
senr
New Member
Posts:18
01 Mar 2011 07:01 PM
New development -
My unit has a supply of 7 gallons per minute on the source side. Climate Master says this should be 15 gallons per minute.
The installer disagrees. It is a 5 tonn water to water unit.
Any thoughts??
docjenser
Veteran Member
Posts:1400
01 Mar 2011 08:46 PM
It gets confusing now. You posted a 7 psi pressure drop on the source side coil before (meaning about 16 gpm flow), now you are saying it is 7 gpm flow.
At the end of the day.....either your flow or your delta T is to low. I can only repeat myself, from the information you have given us, your refrigerant is not taking enough heat out of the source water. While I am the first to question the need for high gpm, the factory specs and the rating are done at 12.5-15 gallons for a 5 ton w-w, so your installer is incorrect.
www.buffalogeothermalheating.com
joe.ami
Veteran Member
Posts:4377
03 Mar 2011 08:50 AM
EWT is high enough to resemble open loop.
We need you to clear up whether you and your installer meant 7 gpms or psi.
j
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
You are not authorized to post a reply.
Page 3 of 3
<<
<
1
2
3
Green Building Forums
--General Forum - Residential
--General Forum - Commercial
--Green/Energy-Efficient Design and Planning
--Green/Energy-Efficient Building and Construction
Green Building Technologies
--Insulating Concrete Forms (ICFs)
--Structural Insulated Panels (SIPs)
--Radiant Heating
--Geothermal Heat Pumps
--Solar and Wind Power
--Windows/Doors and Interior/Exterior Finish
--Appliances, Lighting and Kitchen/Bath Fixtures
Feedback/Support
--Rules, Instructions and Announcements
--Suggestions/Feedback
--Testing Area
Forums
>
Green Building Technologies
>
Geothermal Heat Pumps
Active Forums 4.1
Membership:
Latest:
croccohvacusa
New Today:
0
New Yesterday:
0
Overall:
35027
People Online:
Visitors:
162
Members:
0
Total:
162