Posted By BrianPK on 04 Jun 2012 08:16 AM
There are 5 people and two indoor cats. In the house.
No, A blower door test has never been run. With the ICF and windows, and doors that were bought I would be very suprised if there were any big air leaks.
Thanks for your time.
While inherently tight wall systems plus better windows & doors make air-sealing easier, air tightness is by no means guaranteed.
Air-tightness starts with a defined primary air-barrier on all 6 sides of the cube at the design phase, and needs to be followed up on throughout construction. There are MANY ICF & SIP houses with higher than average air infiltration rates. Unless all trades & contractors involved with the project were both conscious of and dedicated to the notion of an air-tight house you can
bet there are air leaks, and even big leaks would not come as a surprise. The good news is that ICF houses are usually easier to retrofit air-seal than most timber-frame designs. But the assumption that it's air tight requires a lot more than ICF walls and pretty good windows.
The air tightness of ceilings are always suspect since most come with multiple plumbing stacks & electrical penetrations or even utility chases that may be open at both top & bottom, duct penetrations, etc. Air leaks at the top & bottom of the structure are the most critical, since the volume of air driven by stack effect forces is usually higher than wind-driven infiltration.
If the ventilation rate high, whether active ventilation or parasitic infiltration, it adds to latent load when outdoor dew points are high. A dehumidifier converts latent load to sensible load, but it doesn't reduce the total cooling load. Instead it adds more sensible load on top- the power it takes to run that compressor & blower. Running the ventilation at the minimum ASHRAE rate (or even turning it off for a day) might give clues about what's really going on. It takes about 2x the compressor energy to reduce the dew point by 10F than it takes to lower the sensible temp 10F, so a high ventilation rate when outdoor dew points are into the 65F+ range can even add up to a serious cooling load even when not very hot outside. And when it's 90F outside out the dew points can easily be in the 70s or even 80s. Healthy, comfortable indoor air has a dew point of ~55F or lower.
In a new ICF house the concrete itself can add quite a bit of latent load as the concrete cures. If there isn't a capillary break at the footings and bulk water is hitting the exterior walls and seeping down to the footing or if the footing isn't wall drained, concrete can even wick up substantial amounts groundwater 24/365, which can find it's way into indoor air.