GSHP Open Source GPM
Last Post 13 Nov 2014 08:25 AM by jonr. 158 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Page 7 of 8 << < 45678 > >>
Author Messages
jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
30 Apr 2013 12:50 PM
It would be interesting if one could create a system for geo HP water that only treats the water while the system is off. Ie, just before the HP turns off, some chlorine (or acid) gets injected at some upstream point. The chlorine then kills any existing bacteria and prevents new ones from growing. Treating all of the HP water (ie, while it is running) sounds expensive (but maybe not). A similar concept is a drainback system where all of the pipes drain back into the well (or out the drain) when the system is off. My guess is that iron bacteria wouldn't do well when getting dried out now and then.


danreed76User is Offline
New Member
New Member
Send Private Message
Posts:42

--
30 Apr 2013 01:34 PM
What about simply adding a UV light to the source water system with an active charcoal or carbon cartridge filter to remove the dead bacteria which would otherwise become slime or residue in the system? Minerals on the other hand, are a different story. This is probably best applied to closed loop systems to maintain them bacteria free.

For open loop where ferric iron is a problem, a peroxide dosing system could be installed, which would leave no harmful residual, and the only byproducts are water, oxygen, precipitated iron and dead bacteria. The water could then pass through a charcoal filter to remove precipitated iron and dead bacteria, and could set up to automatically backwash periodically.


noobooUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:136

--
30 Apr 2013 01:48 PM
Arkie, would you be willing to conduct an unscientific experiment on your filtered and unfiltered water?

Draw one gallon each of your filtered water and un-filtered into clean jugs, add 8 drops of 5% chlorinated, unscented bleach into each jug, wait an hour or so and see what color, if any, the water turns...


arkie6User is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1453

--
30 Apr 2013 02:22 PM
Last time I checked many years ago, I only had 1-2 ppm clear water iron coming from my well. I've never had any issues with the iron slime / iron bacteria. I don't have any evidence the iron is making it through my sand filter. But this would all depend on how much water your are trying to push through the system. You have to give the ferrous iron sufficient time to oxidize and form ferric iron allowing it to precipitate out of solution and get trapped in the sand bed. As far as the iron bacteria goes, you might be able get rid of it by shocking the well with bleach. The following link and imbedded links have some discussion on that.

http://www.health.state.mn.us/divs/eh/wells/waterquality/iron.html


noobooUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:136

--
01 May 2013 02:01 AM
The sand filter plan sounds effective. I could see an ICF version....add in a chlorine injection, or Hydrogen peroxide or ozonator to the spray water, or a chlorine tablet, although problematic getting a proper mix with tablets, all are possible.

A simple color chart for detecting iron could be a good thing to develop for an engineer out there. (8 drops of bleach in a gallon of water and compare the color to a chart)

How to waterproof icf?

Sand filters for swimming pools have a backflush cycle, but this seems like a bare simple method, KISS theory applied.

No backflushing needed in this system, but how is the maintenance chore? Do you just go over to HD or Lowes and get some clean play sand once a year? I guess that it couldn't be any harder than lugging firewood. How would you ensure the sand was not cat litter in a previous life. Or how would you know the mineral content of the sand??

This system seems appropriate for drinking water, but it doesn't seem right for the HP HX needs...Could work, but it seems the water just came through a filter of sorts, from the ground in my case, just anaerobic. Some systems may be using a open air system. The quality of sand Must be an issue. I might be inclined to just mine my own sand from my lot. But, if I have iron, ferric or ferrous, in my wet sand from my property, well I am just putting iron back into my drinking water system, rt? Maybe a zeolite type filter. At first I was thinking of a big cistern that had an injection system, filling up when the HP was on, then run the domestic through a commercial type filter with a shallow well jet, backflushing into the HX as needed...

Anytime the system is 'opened', it should be sanitized, rt??

Actually, cleaning the HX is not that big a deal and had planned for it. Mineralization would have been a different story.

Keeping water in the HX seems the way to go, which I do with a check valve at the well pump and with a solenoid valve at the HX.

To kill the bacteria on a regular basis, and or correct aggressive water, perhaps When the pump turns off, have a
power-off time delay relay
where a pressurized solution tank of bleach could inject something good for the HX to prevent corrosion and or bacterial growth?


jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
01 May 2013 08:36 AM
have a power-off time delay relay where a pressurized solution tank of bleach could inject something good for the HX to prevent corrosion and or bacterial growth?


Sounds like it would be worth exploring. Cleaning a HX twice a day isn't an issue - as long as it is completely automated. With titanium, frequent cleaning isn't likely to hurt it. And my guess is that a few valves, a timer, a circulation pump and a dosing pump (or venturi) are going to be far less $ than switching to closed loop.


arkie6User is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1453

--
01 May 2013 12:05 PM
Posted By nooboo on 01 May 2013 02:01 AM

...No backflushing needed in this system, but how is the maintenance chore? Do you just go over to HD or Lowes and get some clean play sand once a year? I guess that it couldn't be any harder than lugging firewood. How would you ensure the sand was not cat litter in a previous life. Or how would you know the mineral content of the sand??



For drinking water use, you shouldn't just use any old sand because you don't know what else might be in it.  I would be most concerned with heavy metals such as lead.  I purchase ANSI/NSF Standard 61 certified and labeled sand specifically intended for water filters.  The last time I replaced the sand in my filter, it cost ~$60 for enough sand to essentially replace all of the sand.  It comes in big brown paper sacks at ~100#/sack for ~$15 ea.  I get it from a local water well driller that also supplies water well and filtration equipment.  I believe this same sand is used by the local municipal water supply for filtration.  I'm sure they get it at a substantial discount from my price since they buy it by the truck load.

I've considered rigging up some type of backwash setup, but never really got around to it.  I give my old iron clogged sand to my mom.  She incorporates it into the soil around her rose bushes.




jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
01 May 2013 12:32 PM
It would be interesting to put some of that iron slime in a glass of water and see what effect different acids and bleach have on it. Thinking more radically, circulating water with some type of mild abrasive powder in it might remove it (aka water blasting).


noobooUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:136

--
13 Oct 2013 10:55 AM
Publishing the Utility Room updates, three pictures:
The homebrew utility Room as of 2013.


A domestic HX with 600' pipe stuffed into a 55 gallon drum.


Removed the exp tank from the production well.


Attachment: UtilityRoom.jpg
Attachment: HX600feetpipe.jpg
Attachment: RemovedGSHPItems.jpg

jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
13 Oct 2013 12:48 PM
What was the solution to your iron slime problem?


noobooUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:136

--
13 Oct 2013 05:10 PM


What was the solution to your iron slime problem?


The thinking was if iron bacteria require O2, removing the air bladder tank would help.

Water and air are supposed to be separate in the bladder tank, but the bladder tank was at a high point in the 'production well and injection well loop' and air may have been trapped there. The bladder tank was not needed to keep pressure in the loop when the pump on that loop was off.
The next cleaning will give me an idea if a chlorine injection system might be better.


noobooUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:136

--
25 Feb 2014 03:26 PM
Iron Slime is still a problem and the check valve failed in the closed position, perhaps due to the slime, but the electronics of the check valve were quite hot to the touch and I assumed it was bad and:
I had a water flow error. The Terminals to the pump were also not powering up.

Removed the check valve and now have straight pipes running to the production well HX.

Since the terminals powering the outside water pump continue to fail to power up, I supplied power to the outside pump w/o those terminals and now have good water flow.

But, now, I am getting a low pressure protection error.
I checked static R410 pressure at 155 psi, 55f; measured at the low side port.

The problem I have with this chinese unit is the support they provide is that we seem to talk past each other. They have told me three times that there is 'lack of gas'. Am I missing something? I have my EPA tech card, but new at this, I am.

A recent post here where Joe wrote: FP2 can be a thermistor, a pressure switch, inadequate GPM, low entering air temperature, low refrigerant charge........Is my error similar (ie low pressure protection)?


BergyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:277

--
25 Feb 2014 05:11 PM
Why are you attaching a gauge set to the unit? A Heat of Extraction/ Heat of Rejection should be performed, if the unit is found to be out of spec THEN further refrigerant circuit testing is required.

Bergy


noobooUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:136

--
25 Feb 2014 08:54 PM
Why did I connect a gauge? The guy in China said to (three times). And once it is on, well, I have left it on to review performance and I only connected the low side.

Please bear with me here with some numbers and see what looks 'out of whack':

GSHP R410a static low pressure port = 155psi
Start Compressor 1pm = 62 psi
2p 26 psi
3:30p 23 psi

Production Well Supply and return at previously measured 18gpm:
3:30p measure supply 41f, Return 34f
(18gpm seems wrong here)

Room Side 25/64 Grundfos circ pump
3:30p, Supply 62f, Return 58f

All temperature measurements taken with one analog Taylor 5989 thermometer.

System electric consumption total is 2820 watts.

Terminal for outside water pump is now operating. I had messed with the condenser.


joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
26 Feb 2014 08:39 AM
"A recent post here where Joe wrote: FP2 can be a thermistor, a pressure switch, inadequate GPM, low entering air temperature, low refrigerant charge........Is my error similar (ie low pressure protection)?"

Yes. And consistant with low water flow.
Just one side of the refrigerant pressures is not helpful.


Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
noobooUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:136

--
26 Feb 2014 12:03 PM
Posted By joe.ami on 26 Feb 2014 08:39 AM
...consistent with low water flow.


Thank you Bergy and Joe...I may have enough to go on, given the high delta T, about 7f, on the production well side and the delta T was at about 3f at commissioning. HX (well source) is all frosted up.


noobooUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:136

--
14 Mar 2014 11:18 PM
Please help with a good setup for measuring flow and temp:

: This 4 ton open loop system has not had an accurate flow and delta t measurement, but 20 gpm was observed at the fitting near the water table level at the pump first install. I throttled back to 18.6 gmm, which was the design number.

During the system running(s), there was low pressure at the HX; Jonr pointed out there might be fouling and there has been considerable iron bacteria build-up.

Flow has recently been measured at the top of the HX loop at 6 GPM. Discharge flow appears to continue unheeded, but I see that the injection well is not accepting all of the flow, but is surging out the top of the well and spilling on the ground.


System is now shutting off at low pressure protection.

So, before I pull the pump...on the discharge side of my open loop, I want to install pressure gauge(s) to measure psi and temo so then check pump flow.

Is there a link that I might refer to? All help appreciated.



joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
15 Mar 2014 09:46 AM
if you are fouling with iron, I can't think of a good flow monitor.


Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
noobooUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:136

--
15 Mar 2014 12:52 PM
if you are fouling with iron, I can't think of a good flow monitor.

How 'bout a bad flow monitor?


jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
15 Mar 2014 06:01 PM
You can use a paddle wheel flow meter. Add valves and unions so that you can easily remove it for cleaning.


You are not authorized to post a reply.