06 Mar 2011 09:45 PM
If you use a heating system more often than air conditioning, you need an HRV. If the opposite is the case, an ERV is recommended.


<a href="http://www.londonccc.co.uk/">Carbon credits</a> | <a href="http://www.londonccc.co.uk/content/self-invested-personal-pension">Carbon investment</a> | <a href="http://www.londonccc.co.uk/content/what-are-carbon-credits">Carbon trader</a>
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
07 Mar 2011 01:59 PM
Posted By jumpingspidermedia on 06 Mar 2011 09:45 PM
If you use a heating system more often than air conditioning, you need an HRV. If the opposite is the case, an ERV is recommended.

It's not that simple.

If your summertime outdoor dew points are high enough to require active dehumidification to keep it under 60% RH @ 70-75F an ERV would save considerable even in a strongly heating-dominated climate.   If anyone in the home is allergic to dust mites and it needs to be kept under 50%, even more so.

That corresponds to dew points of 50-55F.  In most of the eastern US (any latitude or climate) the average summertime dew points are higher than than 60F, and an ERV may be the right choice. 

In the Rocky Mountain west or further, not so much, but the wintertime retention of moisture of an ERV would allow higher ventilation rates than an HRV without excessive drying.


guy_davisUser is Offline
New Member
New Member
Send Private Message
Posts:50

--
25 Mar 2011 03:34 PM
As a point of reference for the original poster's question, we built a tight (1.5 ACH @ 50) home in Calgary which is very dry in the winter.  House is heated via radiant in-floor so we have no active house-wide humidification. All the advice we received was to go with an HRV as we'd have more then enough humidity, but after moving in we found the humidity dropping below 20% when it got cold out (below 5 deg. F).

So, we paid more to get ERV cores installed into our HRV unit in hopes of retaining more moisture, with little impact.  As well, when it gets really cold we dial the runtime of the *RV unit down to running just 20 mins every 12 hours.  The VanEE unit we have is supposed to have a "Smart" mode that takes care of this automatically, but we found it would run faster/more whenever the humidity level got near 30%, ensuring the house was always dry.

Now we manually control the *RV runtime and run in-room humidifiers each night in all four bedrooms.  Even with this, we're lucky to hit 35% humidity in the house @ 32 deg. F outside.  It's much drier when it's really cold.  So, if you live in a really dry area and your family isn't taking showers multiple times a day, then be careful with dryness.

     

Our current status with ERV cores is found at: http://welserver.com/WEL0381/


Homeowner - Built in Calgary, Canada<br>Project Details: http://www.guydavis.ca/mphouse<br>
Live System Status: http://welserver.com/WEL0381/
FBBPUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1215

--
26 Mar 2011 12:15 AM
Posted By guy_davis on 25 Mar 2011 03:34 PM
As a point of reference for the original poster's question, we built a tight (1.5 ACH @ 50) home in Calgary which is very dry in the winter.  House is heated via radiant in-floor so we have no active house-wide humidification. All the advice we received was to go with an HRV as we'd have more then enough humidity, but after moving in we found the humidity dropping below 20% when it got cold out (below 5 deg. F).

So, we paid more to get ERV cores installed into our HRV unit in hopes of retaining more moisture, with little impact.  As well, when it gets really cold we dial the runtime of the *RV unit down to running just 20 mins every 12 hours.  The VanEE unit we have is supposed to have a "Smart" mode that takes care of this automatically, but we found it would run faster/more whenever the humidity level got near 30%, ensuring the house was always dry.

Now we manually control the *RV runtime and run in-room humidifiers each night in all four bedrooms.  Even with this, we're lucky to hit 35% humidity in the house @ 32 deg. F outside.  It's much drier when it's really cold.  So, if you live in a really dry area and your family isn't taking showers multiple times a day, then be careful with dryness.

     

Our current status with ERV cores is found at: http://welserver.com/WEL0381/


Isn't Calgary wonderful!! Reading between the lines I would assume there is at least four people in the house and the house while a nice size, is not huge. So still not having much humidity inside speaks volumes about our dry atmosphere. We have been a bit colder this year than the last five or ten so this wrings even more moisture out of the outside air. This is one reason you can't run hrvs of humidistats. They would never come on in the winter. Is it possible to slow the VanEE down at all or are you already running at the slowest speed? As its a new house, even though I'm sure you picked the best products available, I would still be concerned about out gassing. Normally I would say try for .25 air changes per hour of occuppied time but this would really dry you out. Sure would hate to see health issues due to contaminated air even if there is no humidity issues. You might try growing lots of indoor plants which will increase the moisture and some are very good at harvesting pollutants. I believe Olds College has some good data on this. Some people in the area also run small fountains that sound nice which help a bit. As with humidifiers watch for contaminates in the water. Great blog/website! Really like the logging data. I'm not sure what type of meter Enmax gave you but Is there any way to tie it in? Would love to know how often backup heat comes on in the heat pump. Also how much power it is using itself. On the waste water recovery unit data, I'm curious as to why there is small temperature spikes ( at night) when there is no water flow. I understand the drops, they would be heat loss due to venting in the stack but why heat gain? Is there times when Calgary's sewers have warmer air in them? Anyway thanks so much for sharing. Bob p.s. do you post from a Mac?


guy_davisUser is Offline
New Member
New Member
Send Private Message
Posts:50

--
26 Mar 2011 11:23 AM
Isn't Calgary wonderful!! Reading between the lines I would assume there is at least four people in the house and the house while a nice size, is not huge. So still not having much humidity inside speaks volumes about our dry atmosphere. We have been a bit colder this year than the last five or ten so this wrings even more moisture out of the outside air. This is one reason you can't run hrvs of humidistats. They would never come on in the winter. Is it possible to slow the VanEE down at all or are you already running at the slowest speed? As its a new house, even though I'm sure you picked the best products available, I would still be concerned about out gassing. Normally I would say try for .25 air changes per hour of occuppied time but this would really dry you out. Sure would hate to see health issues due to contaminated air even if there is no humidity issues. You might try growing lots of indoor plants which will increase the moisture and some are very good at harvesting pollutants. I believe Olds College has some good data on this. Some people in the area also run small fountains that sound nice which help a bit. As with humidifiers watch for contaminates in the water.
Yes, the VanEE has a programmed mode that will let you run it for as little as 20 mins every 12 hours. This helps a bit with the humidity but as you point out I try to avoid it as a new home will off-gas pollutants for a while. Normally, I leave the VanEE running 20min/hr at low speed. This does dry the air more, but gives us a nice fresh supply. Good idea on the plants. We'll definitely be adding more soon. As for humidifiers, we'll keep using our handful of small ones running in each bedroom for a few hours each night.

For your other good questions (outside the scope of this thread), I've answered them in another thread.

Cheers, Guy


Homeowner - Built in Calgary, Canada<br>Project Details: http://www.guydavis.ca/mphouse<br>
Live System Status: http://welserver.com/WEL0381/
UltimateAirUser is Offline
New Member
New Member
Send Private Message
Posts:8

--
12 Apr 2011 02:29 PM
First off – all ERV’s are HRV’s – meaning all ERV’s transfer heat, with the addition of transferring moisture. So – If an HRV will work for your application – then most of the time so will an ERV. At this juncture you would compare the heat transfer of the units you are looking to purchase, and our heat transfer is the highest performing unit on the market.

Next point – an ERV will transfer a percentage of the moisture from the higher moisture content air stream to the lower moisture content air stream. Ours say is – 40-60% given the conditions present. Do not confuse this with humidity ‘control’ or with relative humidity. Relative humidity is related by temperature, and when you discuss ERV’s and their transfer of moisture – it is absolute humidity, or specific humidity that needs to be looked at. SO- 40-60% of the humidity will stay where the humidity is highest, and the other 40-60% will be sent to the other air stream – be it inside or outside. More simply – an ERV is still dehumidifying when the outside air is more dry, and still humidifying when the outside air is more ‘wet’. Just not as fast as an HRV – and fast being defined as the latent (moisture transfer) of 40-60% in this case.

The moisture recovery from a bath exhaust – considering the amount of time during the whole day this would apply – is not significant to the overall picture. And it depends on your climate, and your house as to when the transfer of moisture would be beneficial or not beneficial. But- as stated, it is a minimal impact considering the fact that the bath exhaust time is very little compared to the time it is ventilating the house and the bath is not in use.

So – if you had a unit that you could say – turn moisture transfer on and off (which is not available in the market), this would be ideal. Else – you have to weigh the entire operational time – and conditions present as to how much moisture transfer (or none) would be ideal. And this is what we have done. From an energy saving performance standpoint – And ERV with 40-60% transfer will be about as good as you can get in a mixed climate location (most of the US)… and even so in a non mixed climate.

Contamination - ASHRAE deems up to 10% contamination is fine in residential applications – even for bath exhaust. This is not really an issue – ventilation is always diluting. The competition does things like “recirculation defrost” – more simply put – 100% cross contamination (we don’t)… but cross contamination is not a big deal. If this is still a worry – example – 3% cross contamination… then increase the ventilation flow by 3%... and now you have the same amount of fresh air as if it were 0% cross contamination.

Durability is directly related to the exchange media design/material, not necessarily that it is an HRV or ERV. We do moisture transfer with a polymer material that is washable and replaceable. There is no getting around service of a E/HRV core. Without yearly service of some kind – operation and performance will be negatively affected. Our design ensures the best operation and life – given the worst of service on the core, or neglect on the installation. But – even with that said – no service will result in failure within the first 3-4 years no matter what E/HRV you install.

So – you have a choice – Install an HRV or an ERV. There are only two technologies… and since we cannot ‘regulate’ the amount of moisture transfer on the fly… you have to decide which is going to work the best. Looking at just moisture transfer as related to energy savings in the home – some amount of moisture transfer will generally outweigh not having it. After this decision – you then compare heat transfer efficiency, watt per cfm (power to operate the unit), air filtration, and service/installation cost. When you weigh all of this in to the picture – our unit will shine.

Air Filtration Systems



UltimateAir® is the industry's leading manufacturer of <a href="http://www.ultimateair.com/air-filtration/">whole-house air filtration systems</a> and energy recovery ventilators that are energy conscious and environmentally friendly.
siddleUser is Offline
New Member
New Member
Send Private Message
Posts:28
Avatar

--
17 Apr 2011 12:50 PM
I presume the experts take Sundays off. I found this, and if you scroll down, you'll find a link to ERV’s under "HRV vs. ERV"...hopefully it will answer all your questions.

http://www.daviddarling.info/encyclopedia/H/AE_heat_recovery_ventilator.html
_________________________________

Absolute Steel— Steel building and carport kits with nationwide jobsite delivery. Easy DIY—America’s easiest to install building system. Watch the video & see for yourself.


ICFHybridUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:3039

--
17 Apr 2011 11:03 PM
ASHRAE deems up to 10% contamination is fine in residential applications-even for bath exhaust.
Even for bath exhaust?

That leads to all kinds of unpleasant thoughts about moving air from the bathroom out to the living areas.


bradleyoderUser is Offline
New Member
New Member
Send Private Message
Posts:4

--
31 May 2011 03:34 PM
We are getting ready to tighten-up a roughly 6000 sqft home here near Raleigh NC, sealing and insulating the crawl space and open-cell spray-foaming the roof deck and gable ends in the attic. Two things: 1) I don't see any conclusive recommendations of one over the other (HRV/ERV) for this mixed humid climate, though some of my colleagues have said we need to shy away from ERV because they are more expensive, more complex, and HRVs do enough of the preferred work of a recovery ventilator; 2) do you feel a blower door is a critical part of the process of determining the exact ventilation recommendations, or can we be reasonably comfortable, with communication with our HVAC pro, that an RV install will provide sufficient pre-conditioned fresh air?


Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
31 May 2011 04:39 PM
In NC ERVs cut the air conditioning latent load for the ventilation air by fully HALF compared to HRV. Summertime outdoor dew points in Raleigh average ~68F and often over 70F- it's a slam dunk winner there! Taking that air down to 75F without removing moisture would make it a mold-inducing stuffy 74% relative humidity.

Only in places where the summertime dew point average in the low-mid-50s or lower it's harder to make the argument for ERV, since cooling the air to 75F or even 70F room temps it would still be at healthy indoor RH levels even without removing moisture.

But if you run the AC via dehumidistat control it'll stay comfy & healthy, with an HRV, but at a boost in energy use. In a higher-R house with low sensible AC loads dehumidification control becomes critical, and an ERV helps.

Air sealing & blower door tests are a critical part of making the place energy efficient, but has little to no bearing on the sizing of the ventilator, which should be sized and run as if the house were hermetically sealed. An air-leaky house is just "ventilation by accident", with no guarantees that the room by room leakage is commensurate with the ventilation needs of those rooms. A blower door test can tell you when active ventilation is "absolutely required" vs. merely "strongly recommended", but it doesn't affect the sizing or duty cycle of the ventilation.


bradleyoderUser is Offline
New Member
New Member
Send Private Message
Posts:4

--
31 May 2011 04:57 PM
But if you run the AC via dehumidistat control it'll stay comfy & healthy, with an HRV, but at a boost in energy use. In a higher-R house with low sensible AC loads dehumidification control becomes critical, and an ERV helps.


Thanks, Dana. It seems that running dehumidistat is an option. I thought that it was understood. How do I ensure that that is the case without calling in the HVAC pro?

Also, we're operating under the pretty dependable assumption that much of the leakiness of a home (or at least the most liable portion of it) resides on the top and bottom ends. These things are fairly well confirmed by visual and IR inspection. We're addressing that pretty significantly with the crawl and attic scope, but without a blower door, we don't know by exactly how much. It seems like you are saying, according to the volume and occupancy of the house, we know what the ventilation needs are already, so if we employ an ERV (which it seems like you are recommending) we are ensured of the ventilation while reducing some of the moisture removal load on the HVAC system.

Does it seem like I've understood? Other thoughts in response?


bradleyoderUser is Offline
New Member
New Member
Send Private Message
Posts:4

--
31 May 2011 05:18 PM
Also, Dana, I went to your profile to learn a bit about your experience, company, expertise. Do you mind sharing a bit?


Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
31 May 2011 05:48 PM
I just make it up as I go along, isn't that obvious? :-)

You seem to have grasped pretty well what I was saying.

Most AC pros can set systems up to run in modes that are mostly-drying rather than highest efficiency sensible-cooling, switchable between modes depending on the type of load. In the simplest case this could be a dual- mode thermostat/dehumidistat on the wall of a standard on/off AC system, but those that change the speed of the air handler or compressor (or both) will work better. The slower the air, the cooler it is on the evaporator coils, and the more water is removed per unit of compressor energy. Of course this only works down to the frost point. Many variable speed mini-splits control both temp & humidity fairly seamlessly, but it's a design feature to get that with semi-custom ducted systems.

I'm an electrical engineer by profession, a math & physics nerd by education. The building science & HVAC stuff is primarily a hobby at this point, but I've consulted on construction & building-efficiency projects for decades. My family was in the construction biz from the late '50s through the '90s.


BrawlerUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:229

--
31 May 2011 10:47 PM
One hell of a hobbist! Ha! Thank you for all your help dana. God only knows how much time you have spent answering questions and reaserching answers. I always wanted to know what you did. Thanks.


Chloe TaylorUser is Offline
New Member
New Member
Send Private Message
Posts:89

--
01 Jun 2011 02:08 PM
Posted By Dana1 on 04 Feb 2011 04:01 PM
ERVs don't return humidity super-efficiently in cool weather, but they return some, allowing you to run a higher ventilation rate without excessive drying. There's little down-side to going with ERV, and since you can run higher winter ventilation rates there is a slight health-factor benefit.

Dew points are low enough in summers that you don't benefit a whole lot from ERV during the cooling season though- your sensible cooling loads far outstrip your latent cooling loads. The fact that your WaterFurnace condenses a bit of water in the summer isn't an indication of a NEED to dehumidify. No matter how dry the summer air is, the dew point above the temp of the cooling coils of a compressor system, and you'll get some condensation out of it. But the volume of water condensed is much much lower than in places where the dew points are well north of 70F (where the latent load is more than 80% of the cooling energy use for the incoming ventilation air.)

If can air-seal the house sufficiently to get your air changes per hour @ 50 Pascals (ACH/50) in a blower door test down below 2, you would almost certainly be able to maintain 30% RH indoors all winter without active humidification. The fact that it's dropping below 20% unless you actively humidify it's an indication that your natural ventilation rates are relatively high, and the argument for active ventilation may be moot. Houses that are PassiveHouse tight (<0.6 ACH/50) always need active ventilation to bring the humidity DOWN to 30% in winter. Canadian R-2000 standard (<1.5 ACH/50) homes can also be in the same situation. With cooking/bathing/breathing for six the amount of moisture introduced by your family SHOULD be able to keep it at 30% and then some.

With "natural" ventilation the infiltration/exfiltration points are somewhat random, and don't guarantee that the ventilation air is distributed where it's actually needed. Ventilate with an ERV, yes, but DO try to get the natural ventilation rate down- it'll save heating/cooling energy, and you'll end up with better indoor air quality overall. Tightening up the house to the point that you can decommission the humidifier and run the ERV in winter under dehumidistat control would be ideal.

Are you sure that ERV's dont return Humidity.... Well i have a doubt regarding this statement......  ?



<a href="http://www.capitalsteelbuildings.co.uk">Commercial Buildings for Sale</a>
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
01 Jun 2011 02:40 PM
ERVs exchange humidity in both directions. The direction of the humidity transfer is a function of which air mass (the conditioned air or the outdoor air) has the higher absolute humidity level (aka "dew point".) The humidity will only transfer from higher absolute humidity to lower.

In winter when the exterior air is drier than the conditioned space air, some of the humidity from the exhaust air is added to the incoming ventilation air, but when the outdoor air is more humid, the converse happens. "Relative humidity" is just that, relative to the TEMPERATURE of the air. Cool the air off, it's RH rises, warm it up, it falls. But the dew point of a body of air remains constant across temperature (untill it reaches the dew point, and moisture begins to be removed from the air via condensation.)

Which is the whole point: 90F, 65% RH air has a dew point of nearly 77F, so if you used that air with an HRV to ventilate a 75F home, it would be at saturation, condensing in the ducts. With an ERV half the humidity would have been transferred out, for a much lower moisture burden for the AC to remove.

The relationship between temp & humidity is mapped out in the psychrometric chart:

http://upload.wikimedia.org/wikipedia/commons/f/fc/PsychrometricChart-IP.PDF

If you find a temp & RH curve intersection, moving horizontally on the chart (cooling/heating the air), it will cross other RH curves. The dew point is the 100% saturation curve, the temp at which taking more energy out of the air causes a phase change of the water vapor into liquid water before the temperature can change. It takes dramatically more energy to lower 100% RH air 5 degrees compared to cooling 90% air by the same sensible (temperature) amount, since the "heat of vaporization" of the water has to be extracted first if it's at 100% humidity. By utilizing the dry air stream to extract moisture from the moist air stream an ERV saves a bit of compressor energy use by cutting the heat-of-vaporization burden in half.


bradleyoderUser is Offline
New Member
New Member
Send Private Message
Posts:4

--
01 Jun 2011 03:54 PM
Any problem with a Honeywell ERV (default for our HVAC pro), or should I be spec'ing another?


Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
01 Jun 2011 04:17 PM
Variable speed "ECM-drive" or very high efficiency single speed blower motors can make a significant difference in blower power use. I'm not sure what's in the Honewell lineup that's good/bad/other. The warranty period on the enthalpic core (the humidity exchanger) varies a bit from manufacturer to manufacturer too, but make sure it's at least 7 years.

Run the ERV at min rate during the humid summers, and use the AC/dehumidifier to keep the indoor RH under 60% (under 50% if anyone is allergic to dust mites.) In the coldest part of the winter it may be useful to run the ERV under dehumidistat control, turning the ventilation to minimum when the interior drops below 35% RH. Even an ERV can be too drying if the ventilation rates are high in winter.


Lee DodgeUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:714

--
01 Jun 2011 04:18 PM
Bradleyoder- In selecting an HRV, I was interested in minimum energy consumption, so part of my selection criteria was to choose a unit that had ECM (electronically commutated motors) as opposed to the higher energy consuming PSC motors. I found a chart that I have since lost track of that compared the energy consumption of many different models. Since the HRVs and ERVs have a high duty cycle, sometimes running full-time, it seemed worthwhile to me to choose a model with low energy consumption. Lee Dodge http://www.ResidentialEnergyLaboratory.com in a net-zero source energy modified production house


Lee Dodge,
<a href="http://www.ResidentialEnergyLaboratory.com">Residential Energy Laboratory,</a>
in a net-zero source energy modified production house
HHHUser is Offline
New Member
New Member
Send Private Message
Posts:81

--
13 Jun 2011 12:40 PM

I use this:  HEPA filtration and energy recovery ventilator, Broan GSEH3K.  True HEPA filter with a 99.97% efficiency on particles ≥ 0.3µm.  Pre-filter with a >90% efficiency on 3.0 - 10µm size particles which extends the life and performance of the HEPA filter.  HEPA filtration capability: 270 cfm; fresh air capability: 70 cfm – 110. The Broan GSEH3K tempers fresh air with outgoing stale air to minimize energy expenditures. 