Posted By Dilettante on 09 Feb 2019 10:55 AM
Code minimum is most places I look is 7 ACH50 (Which must be like living in a screened porch).
"Moderate" is around 5 ACH50. And somewhere between 5 and 3 is where mechanical ventilation is code-mandated.
"Good" is 3 ACH50 or below
Passivehaus standard is 0.6 or below.
If you're pulling a 1.5 or less, you're doing GREAT.
ACH can be calculated by multiplying the CFM by 60, then dividing by the building volume in cubic feet.
Yes I used that formula and I included the basement air volume in that calculation. It's more like 2 ACH without the basement.
I honestly wonder if the guys equipment was not calibrated right or something. It's a log home with lots of cracks, the windows don't exactly shut right, and I feel drafts. Maybe it's my radiant floor not mixing the incoming air with the warmed air well enough??
So I might have another company do another test. But should I be looking for a heat recovery ventilator if it is that good?? Is there air quality test that can be done?