Closed Cell Foam in Rafters
Last Post 03 May 2011 11:05 PM by Sporto. 24 Replies.
Sporto
| 21 Apr 2011 10:47 PM |
I'm building a new home and getting close to needing to decide on insulation. My contractor was planning on just doing FG batting in walls and roof rafters (no attic, just vaulted ceiling) however, I've been reading about the benefits of doing a hybrid (closed cell foam and FG batting or cellulose) insulation installation. We're building with 2x6 walls and 2x12 rafters. We're building in Seattle so pretty temperate. My understanding is that the spray-in closed cell foam will seal the walls so we won't need to do much sealing inside the bays (just along any other exposed seams not covered) and, if done correctly, won't require a a vapor barrier.
Question: in the rafter bays, do we need to create a 2" space under the roof sheeting for condensing or can will the combination of the spray in foam and batting replace the need to allow for a gap between the sheeting and insulation to allow for condensation? (i.e. can we just spray the foam onto the lower surface of the sheeting rather than allowing for a 2" gap per traditional building techniques?)
Any guidance and help is much appreciated
vipin
| 22 Apr 2011 03:22 AM |
Homeowners are increasingly looking for the best way to insulate across
rafters. For typical home, attics have the most extreme temperature of
any parts of the house. During the summer it is the hottest part of the
house. |
| 22 Apr 2011 09:20 AM |
I would take a good look at using taped/sealed rigid foam + cellulose. Less bridging and good price/performance.
Rosalinda
| 22 Apr 2011 02:26 PM |
Jonr - would you use that foam board on the outside of the roof deck? Sporto - are you doing 2X6 on 24 inch centers? Might be easier to go with a foam flash (or thorough caulking) and cellulose fill if you do, than to try and get the fiberglas batt insulation up to standard. Are you going to use 1.5 inches of foam board on the outside to prevent thermal bridging?
-Rosalinda |
| Sum total of my experience - Designed, GCed and built my own home, hybrid - stick built & modular on FPSF. 2798 ft2 2 story, propane fired condensing HWH DIY designed and installed radiant heat in GF. $71.20/ft2 completely furnished and finished, 5Star plus eStar rated and NAHB Gold certified |
| 22 Apr 2011 04:48 PM |
Posted By Sporto on 21 Apr 2011 10:47 PM
It won't meet code to do the roof deck unvented in Seattle (some inspectors are pickier than others), but it won't cause a problem either. The foam becomes the condensing surface, but A: doesn't wick moisture toward the roof deck, and B:Allows the roof deck to dry (if slowly) toward the interior and C:Has a very limited number of condensing hours per winter in Seattle's climate. See: http://www.buildingscience.com/docu...of-systemsBut it may not be the best value. On new construction, unless this is a built-out attic with kneewalls or you intend to finish it as living space some day, it's cheaper/better to air-seal with foam at the attic floor and blow cellulose until it's 3" above the tops of the joists (creating an ~R10 thermal break on the framing). If this method is used, even R50 is cost effective even in a 5000HDD climate, where as 2" of closed cell foam at the roof deck would already have costing you more than R50 in cellulose on the attic floor, before you bought the first bag of fiber to bring it up to code-min levels for R. If you ARE committed to going the conditioned attic approach, you can get more bang/buck out of putting 2-3" of rigid insulating panels above the roof deck, with the fiber inside, since that puts cheaper R on the exterior that thermally breaks the rafters for a big performance uptick. Nailer-deck panels bonded to iso or EPS are available from a number of vendors (Hunter, Atlas) and some variants come with a vent gap between the insulation and the exteiror nailer deck, which allows the nailer deck to dry into the gap. In Seattle's climate you'd only need 25-30% of the total R to be in exterior foam to make the structural roof deck resiliant to interior side air leaks or vapor diffusion, so even 2" of iso or XPS would allow you to do the interior at R30 and meet or exceed code for center-cavity R, but BEAT the whole-assembly R value of a batts-between rafters/joist solution by a huge margin. Similarly, even an inch of XPS (R5) on the exterior of the studs provides more whole-wall R value for less money than an inch of closed cell SPF (R6-6.5) in a flash & batt or flash & spray cavity fill, provided you detail the air-barriers correctly, again due to the thermal break it's providing over not just the studs, but the band joist and foundation sill as well. Taping the seams of the XPS with housewrap tape, and foam-sealing the edges can make it a primary air-barrier as well, but doing that and sealing the structural sheathing as well is worth the trouble. Spray foam is great for it's sealing properties, and for adjusting vapor
permeabilty in some situtations, but it's a very expensive way to add
center-cavity R. Acoustic sealant type caulk is a much cheaper way to
seal stud wall cavities to the sheathing/plates and between plates/subfloors etc. And with Seattle's modestly cool climate it doesn't take much exterior foam to keep the interior of the structural sheathing above the dew point of the interior air, making anything more vapor retardent than latex as an interior paint as a finish unnecessary. Displacing the bulk of the foam-budget to the exterior is the right thing to do. Adding furring to the exterior of the rigid XPS through-screwed to the studs as a means of mounting the siding further adds a "rainscreen" gap, enhancing the drying capacity of the assembly even further. (10mm minimum rainscreens are required by code for studwall construction in Canada, and should be in WA, IMHO) The fastener spacing required for the furring depends on the depth of the foam, the furring/stud spacing, and the type of siding used, but it's pretty straightforward to put as much as 3-4" of exterior foam with lightweight wood siding. Building studwalls with flash & batt but without exterior foam would be criminal-waste. If you're going to do one vs. the other, go with exterior foam. At 2x6 flash & batt/ or flash & spray with a 20-25% framing fraction comes in with a whole-wall R of ~R15, whereas the same studwall without flash-foam but with an inch of exterior foam it's ~R20, a 33% performance boost, for lower installed cost. (In colder climates than yours it's sometimes necessary to use both exterior and flash foam to avoid condensation issues in winter, or going to awkwardly thick exterior foam an a very thick wall.) |
| 22 Apr 2011 05:07 PM |
BTW: Even if it's a cost premium, spray cellulose (any density) or high-density (1.8lbs) superfine blown/sprayed fiberglass such as Optima or Spider will far outperform batts in any of these applications. If forced to use batts (and they'd have to really put a gun to my head, were it my house), it's worth buying only high-density "cathedral ceilng" batts. An R19 batt when installed per manufactures spec delivers only R18 center cavity, and then only at relatively modest temperature differences. Hyper-fluffed R22 batts in the same cavity only deilver R19(!), but R21 delivers, R21. See: http://www.owenscorning.com/around/insulation/CompressionChart.xls or http://numsum.com/spreadsheet/show/21111 Also note, in order to remotely perform to spec low and mid-density batts need air barriers (not necessarily vapor barriers) on both sides, or they lose R-value to convection currents when the temperature differences are high. This is often ignored in attic applications but even a sheet of housewrap over the top helps, but adding 3" of cellulose overblow does even better, since it also adds R. Blown cellulose is sufficiently air-retardent that it's convection losses don't make a dramatic difference. Low density batts and low-density blown fiberglass operate at something like half their rated R when it's 0F above the fiber, no air-barrier. High density new-school fiberglass doesn't have this issue, but it probably does if installed at only 1lbs density. |
jumpingspidermedia
| 22 Apr 2011 09:27 PM |
Posted By Dana1 on 22 Apr 2011 04:48 PM
Very well said. I'm sure what you need has been pointed out in this statement! |
| <a href="http://www.londonccc.co.uk/">Carbon credits</a> | <a href="http://www.londonccc.co.uk/content/self-invested-personal-pension">Carbon investment</a> | <a href="http://www.londonccc.co.uk/content/what-are-carbon-credits">Carbon trader</a> |
Sporto
| 23 Apr 2011 03:18 PM |
Thanks to all for the responses. Just a note of clarification. The house is structurally already built with steel roofing and windows installed. Wall structure is 2x6 studs with 1/2" sheeting over (16" centers). Roof is 2x12 rafters with 1/2" deck, ice barrier, and steel roof (24" centers). All ceilings are 'cathedral' style so there is no attic. At this point, with the roofing and windows installed I don't believe I can add any solid foam board on the exterior of the wall sheeting and, with the roofing on, certainly not the roof deck. If I had investigated this earlier on I could have accomodated for a 1.5" to 2" foam board on the exterior to mitigate thermal bridging but it seems too late for this (to my detriment).
Anyways, with this in mind what I'm hearing from the great input is that either solid foam and fill that is well sealed or a flash and batt or flash and fill for both would be the right way to go. In the ceiling rafters, while I don't need to allow for venting if I use the spray foam insulation I could have problems with inspectors so it might make sense to just put a vent space in under the roof deck and then do flash and fill type insulation. Did I get this correct?
Again, thanks so much for the input. Just trying to get as much performance out of the insulation as I can given where we are in the construction.
Sporto
| 23 Apr 2011 03:51 PM |
jonr, would you recommend to allow for a vented volume between the rigid foam and the roof deck? I am building in Seattle so climate is relatively mild. My contractor only has experience with creating a 2-3" space between the roof deck and the insulation. I know this is the traditional build technique to allow for a condensing surface but with enough spray foam/rigid foam it seems like you can move the dew point far enough inside the home volume to negate the need. At least, that is my understanding.
Sporto
| 23 Apr 2011 03:55 PM |
Rosalinda, Thanks for your reply. Please see previous post relative to construction type. I am strongly considering your recommendation of flash and fill rather than FG batt but just trying to decide whether to leave a void between the roof deck and the foam (whether rigid or spray) for venting or not.
Any thoughts are always appreciated.
Thanks again,
Alton
| 23 Apr 2011 08:41 PM |
If you have rafters instead of roof trusses, an air space can be left the depth of the rafters and still have a sealed and insulated attic but this system does not use any other insulation other than closed cell foam. E-mail me for more details, if interested. |
| 23 Apr 2011 09:35 PM |
would you recommend to allow for a vented volume between the rigid foam and the roof deck? It would be better but I just don't know if it is really necessary. |
Alton
| 23 Apr 2011 10:23 PM |
Sporto,
E-mailing someone through Green Building Talk forum does not leave a return e-mail address. So I can not reply to your e-mail without an e-mail address. My e-mail address is in my signature block. I write it strangely so bots will not recognize it as an e-mail address and send me a lot of SPAM. Anyone that wants to e-mail me should simply substitute the at symbol for the word "at" and substitute . for "dot".
I am not up on Seattle weather including humidity in the different seasons so I really can not go beyond what Dana1 has already replied. |
Sporto
| 23 Apr 2011 11:20 PM |
Thanks Alton.
Rosalinda
| 25 Apr 2011 12:18 AM |
Sporto, If the windows are in but not finished with returns etc, and you haven't sided the house yet, it still might be worthwhile to think about moving the windows to get that 1.5 inches of insulation board on the outside, since it greatly enhances the effectiveness of any insulation you have in the walls. Maybe in your climate this will be overkill, but I sure wish I had been able to add board insulation on the outside of my new house - and am still thinking about doing it at some future date, despite the major work that will have to be done to accomplish this. Since you have 16 inch centers in the wall, you could use windowpane caulking and R21 high density fiberglass batts IF you have someone who will do it to the highest standard. I did my own sealing and insulating using this relatively inexpensive method in my walls, and the results have tested extremely well, but I was meticulous to an extreme. There seem to be lots of good reasons to use flash and fill though, and given a sufficient density of the fill material, it sounds as if it will work better over the long term. I also have a cathedral ceiling, but it was 2X10 not 12, so there wasn't room to use anything but 2# closed cell foam to get the R50 I wanted. NY state allows unvented (hot) roofs though, and it does not sound as if your bldg code does, based on comments in this thread, so one of the several suggestions might suit. It probably would not hurt to run the ideas by your code person and see what he/she thinks. -Rosalinda |
Sporto
| 25 Apr 2011 12:33 AM |
Rosalinda, Thanks for the input. Question: If you do install 1.5" rigid foam over the outside of the wall sheeting how do you fasten the exterior siding boards to it? Do you drive a fastener all the way through the foam and into the plywood? Or do you install some sort of wooden firring strips to attach the siding to?
sporto |
| 25 Apr 2011 10:51 AM |
I've seen both - depending on foam thickness and siding weight.
| 25 Apr 2011 10:58 AM |
Posted By Sporto on 25 Apr 2011 12:33 AM
sporto
Long nailing through foam makes 10,000 air leaks as the nails bend/sag over time. Long-screw furring into the studs, mount the siding to the furring: http://www.greenbuildingadvisor...athed-wallIf you did a full-cover of Grace Ice & Water Shield on the roof deck under the metal roofing, you have a severe vapor barrier on the cold side of the assembly (in contradiction to best-practices.) Unless your ventilation gap under the roof deck is vented to the outdoors, the humidity at the roof deck won't be much different than if the insulation is at the roof deck. Adding at least an skim-shot of foam will protect it from wicking condensation into the roof deck though. It's possible to get a variance from the code (and in some states such as MA it's explicitly allowed) that if a requisite fraction of the total R is foam against the roof deck it need not be vented, and that WOULD be the best solution in this case. Print out that Building Science simulation, read it until you understand it, and present it to the relevant inspection agency before insulating. The most-relevant parts to present are Tables 3 & 4 on p.11, which indicate that independent of the albedo of the metal roof, with 2" of closed cell polyuretane the roof deck doesn't accumulate moisture from vapor diffusion even in a high-interior humidity situation with very low risk at normal humidity, and even at only 1" it would have but a modest risk at normal humidiy, and only if it was light colored metal roof. Rather than 2"/R12standard 2lb polyurethane, you might consider a higher-perm/lower K-value product such as Icynene MD-R-200 (and not MD-C-200) to give it a better capacity to dry toward the interior. A 3"/R15 shot of that stuff still gives 1.3 perms vapor permeability (about the same perm rating as 1" of standard closed cell polyurethane), and at R15 the mean January temp at the foam/fiber interface would be well above the interior air dew point. Finish out the cavity fill with either cellulose or 1.8lb Optima or Spider fiberglass blown-in-bag, and do NOT use interior vapor retarders (not even asphalted kraft goods.) That way the roof deck can dry seasonally toward the interior, and it NEEDs the extra drying capacity since it has zero capacity for drying toward the exterior. (Metal roofing mounted on purlins on a felt-clad roof is usually much more protective of the roof deck than with metal on extremely low-perm stuff like I & W Shield.) FWIW: The simulation in the BSC document was using 1.8lb JM Spider for the fiber, and 1.2 perms/inch closed cell foam. (see p.5) |
Sporto
| 26 Apr 2011 12:03 AM |
Dana1,
just for clarification... I do have the ability to vent the lower surface of the roof deck to the outside. Each rafter bay has 2 or 3 3" diameter vent holes in both ends of the bay. With that in mind, I take it from the first paragraph of your most recent response that it would be best to take advantage of this and ensure that each bay has a 3" air volume between the lower surface of the roof deck and the top of the insulation, correct?
The current build up of the roof is (from outside to inside)
1) Standing Seamed Steel roofing (dark charcoal grey in color) 2) ice barrier (sorry I don't know the brand - it was just described as an ice barrier material). The ice barrier material was some kind of flexible membrane which was adhered directly to the roof deck 3) 1/2" plywood roof decking
From what you've told me it sounds like the ice barrier and steel laid directly on the plywood roof decking means that I need to create an overall system that dries to the interior. It seems like this is the case with any steel roof in which the steel is laid directly onto the decking. If so, then I'm hoping that the vented space I'm proposing in the top paragraph above is sufficient adequite as its about all that is possible given that I've only got the depth of the 2x12 rafters to deal with.
Makes sense? |
| 26 Apr 2011 04:43 PM |
There are mesh-type underlayments for steel roofing still allow the roof deck to dry toward the exterior, but with vapor impermeable ice barrier goods already applied that's a moot point- what's done is done. The roof deck now has to dry downward, either into a vent gap or via a properly vapor-retardency adjusted wall stackup to the interior.
You don't need anything like 3" of vent gap between the roof deck and insulation for adequate drying- an inch will do, and would meet code. The other way it's done is to use pre-formed chutes stapled to the roof deck at the edges and insulating below that (typically with an overcompressed batt, but let's do better than that, eh?)
With a dark colored steel roof you can definitely get away with an unvented roof deck layup as outlined in the BSC document, which makes air-sealing issues a lot easier, and would get you a higher-R than code-min.
Using low-density R38 batts in a vented space with no top-side air barrier would be an energy-disaster, as they can only perform to spec with air-barriers on both sides. It would still meet code, but actual performance would be relatively low since warmer air in the batt would be constantly being displaced by the cooler air in the ventilation gap via convection. If it MUST be batts, use only highest-density "cathedral ceiling" batts which suffer much lower convection losses. (eg Owens Corning R38C rather than the standard R38 non-"C" version.) It may be possible to use housewrap to create an adequate vent-space side air-barrier, but I've not seen that done, and there are 1001 ways to screw that up, I'm sure.
An R38C batt in a 2x12 cavity would also give you a full inch of vent space without compressing the batt, whereas stock low density R38s would need supporting vent-chutes compressing them out an inch or so in the center, and delivering something like ~R33 (in your test-lab-only dreams, less in the real world.) Strangely, the latter still meets code in most places, but not the labeled performance spec. (Even without the venting chutes it would only hit R37 in a 2x12 rafter bay.) It's more expensive, but worth it, (yet still not as good a value as wet-spray cellulose.)
Still 3" of the higher-perm/lower-K 2lb foam plus wet-spray cellulose blown-in-blanket for an air-tight center-cavity R50 would be the best way to go from a true-performance and longevity point of view. A 3" shot of the low-K 2lb foam costs about as much as 2" of most closed cell foams ($2-2.25/square foot, installed) for a better R/$ ratio, and would give you a much better foam/fiber R-ratio than in the BSC simulation in that prior document. But it's definitely not cheap. (Doing the same R as 3-4" EPS above the roof deck would have been half the price, and higher performance, and would have put the structural roof & rafter edges at a warmer-drier place. Again, a moot point...)
307 |
307 |