In US building material terms K-
value ="1/R value per inch of thickness". (I've been mis-stating it- mea-culpa! The K-value of the high-perm foam is
higher, not lower than the K-value of most other closed cell foams. Its the R-value per inch that's lower. The typing fingers are quicker than the mental-editing... )
Venting the roof deck from below will only keep the roof deck marginally drier than with a foam/fiber approach, but it limits the total R value to something that performs R33-R35-ish on it's best day, allows critter-access to the fiberglass, allows more convective loss of R-value when at the temperature extremes, leaks air from the exterior requiring more detailing to create a (more susceptible to damage) interior air-barrier, etc.
Batts degrade over time. I wish there was an easy way to rip out & replace the HD batts installed in a vented cathedralized ceiling in my house without tearing it apart. In less than 12 years it's had both mouse and bat infestations despite hard-screened soffit & ridge venting, and it's easy to spot the developing heat leaks from the compromized batting in the snow-melt patterns. This has not occurred on the un-vented foam insulated cathedralized ceiling sections. When I re-roof I'll blow cellulose into the vent gap from the exterior compressing the batts and add sufficient exterior rigid foam to mitigate the seasonal moisture issues, but until then it's not so great. (YMMV, but don't count on it.)
Closed cell foam at 3 " thickness adds structural strength to the assembly, creates a near-perfect & well protected air barrier at the exterior (that will be air-tight in a century), becoming the exterior air barrier necessary for the fiber perform to spec. It also allows you to use cellulose for the fiber layer, which protects the assembly further by buffering seasonal moisture and reduces convection within the fiber layer by an order of magnitude compared to high-density batts (almost 2-orders of magnitude compared to low density batts), has no gaps compressions or voids with a perfect fit, never attainable with batts, and adds as much thermal mass as increasing the thickness of the sheet rock by 1/4-3/8".
And, ~R50 is a 40% performance boost over ~R35, and it's a performance
level that will still be there in 50 years. (In whole-assembly terms
with the thermal bridging of the rafters factored in it's probably only a
30% boost, but that's still significant.) The big uptick in expense is
the foam, the wet-sprayed cellulose blown-in-blanket has a similar
installed cost per unit-R to high-density batts.
Between the air sealing to the exterior and extra rigidity of the closed cell foam, added to the mass and vibration absorption of the cellulose sound transmission through the assembly is also much reduced (which is a big plus under a metal roof in a hail storm, or even a rainstorm- but I know you never get those in Seattle.
In wall assemblies wet-spray cellulose is usually
cheaper than high density batts since at lower densities it's sprayed directly without neeting to install mesh as a prior step. If you're detailing the exterior sheathing as an air barrier, there's little value-added to dense-packing the cellulose in walls with 30-50% more material, which is sometimes done for limiting air infiltration instead of building a true exterior air-barrier. It'll have a slightly lower center-cavity R than high density batts, but the perfect fit of blown/sprayed fiber mostly makes up for that in real-world performance.