The
1% and 99% outside design temps in Wilmington NC are +27F and 91F, respectively. With a 70F heating indoor temp that's a 33F delta, and with a 72F cooling indoor temp that's an 19F delta, which is typical for a zone 3A kind of climate.
It's really the solar gain that makes all the difference in peak cooling load, not wall R, and in particular the solar gains that come late in the day when outdoor temps are near their peak. Since you have designed-out west facing glass that has fairly large effects on peak cooling loads for those rooms/zones. Typical code min builds will have an average load on the order of a ton per 1000 feet of conditioned space, but that's tweakable in the house design. So if it were just a code min house with average glazing distribution/orientation you'd be looking at something on the order of a 5000-6000 BTU/hr of cooling for that 450 square foot zone, plus the peak heat inputs from plug loads, cooking, etc. (Hopefully you're not roasting turkeys & boiling potatoes with the lid off when it's 91F outside :-) ) With solar gains limited and with a mass wall you should be able to knock that back 1000-1500 BTU/hr, call it 4000 BTU/hr + intermittent cooking spikes + the 24/365 plug loads.
All else being equal the 700' zone would be on the order of 7000 BTU/hr + plug loads, but can probably be reduced to 5000 BTU/hr + plug loads. The "...huge computer storage array..." needs to be specified in watts to know what it's contribution is to the cooling load (and subtraction from the heating load) really is. For every 1000 watts it adds another 3412 BTU/hr, so if it's 1500 watts (measure it with a Kill-a-Watt or similar) that would be another ~5000 BTU/hr, bringing it up to the 10,000 BTU/hr range. (If the power used by the storage array is really that high it would be covering 100% of the heat load for that zone, but it also means that hitting Net Zero could be tough with such a heavy background draw.)
At 90F when the FH09NA is modulating @ 9000 BTU/hr out it's hitting it's super-high 30+ SEER numbers. (That's the modulation level at which it's SEER was rated.) Running full-out can deliver 12,000 BTU/hr of cooling, but at a somewhat degraded efficiency at output higher than 9000 BTU/hr. If 12,000 BTU/hr covers the actual design load, the FH09 probably going to be the better choice for that zone than the FH12, due to it's lower minimum modulation.
ERVs help when the outdoor dew points are higher than the indoor dew points, but when it's drier outside than inside it impedes drying a bit. Either would be fine in your climate. During the heating season whenever the outdoor temps are 50F or lower an HRV can would usually handle 100% of the dehumidification, without need of mechanical dehumidifiers, unless you're the type to boil food on the stove top all day with the lid off.