Below are the design parameters supplied by my contractor after an on-site survey. Not sure what is meant by Winter/Summer Design or temp diff values:

Design Data: Comfort Conditions:
Heating Load: 51,000 Btuh Heating Setpoint: 68 °F
Heating Temp Diff: 68 °F Cooling Setpoint: 74 °F
Cooling Load: 30,000 Btuh Start Cooling Temp: 74 °F
Cooling Temp Diff: 17 °F HW Temp Setting: 130 °F
Constant Fan: No HW Users: 3 people
Design City: MINNEAPOLIS, MN Annual Loads:
Winter Design: -12 °F Heating: 109.9 million Btu
Summer Design: 92 °F Cooling: 14.6 million Btu
Bldg Bal Temp: 56.7 °F Hot Water: 17.3 million Btu
Internal Gains: 8,490 Btuh HW Use - Daily: 55.0 gallons

Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
19 Dec 2008 11:39 PM
Winter design is how cold it might get in your location in the winter
Summer design is how hot it might get in your location in the summer

The temp diff for summer seems right 92 - 17 = 75

The temp diff for winter seems off 68 - 68 not = -12

Temp diff for winter should be 80
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
Palace GeothermalUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1609

--
20 Dec 2008 09:25 AM
Are you going to be happy with an inside temp of 68° in the winter?
Dewayne Dean

<br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system
MasoudUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:180

--
20 Dec 2008 10:17 AM
It seems to me, Pipemajor's contractor defined Heating Temperature Differential as the difference between winter design temp (-12) and building balance point (rounded down to 56), thus: 56 - (-12) = 68 degrees. I think Heating Temp Diff, as Dewayne pointed out, is the difference between heating setpoint and winter design temps, therefore: 68 - (-12) = 80 degrees. Concern is that proper figures are put into load calc software, and building balance point, as well as internal gains are accounted for.

Regards, Masoud
gregjUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:326

--
22 Dec 2008 11:22 AM
What is a Building Balance Temperature???
engineerUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2749

--
22 Dec 2008 01:20 PM
Temp where internal building sources of heat (people, lights, appliances, cooking) and possibly also solar gain taken together equal the heat loss. Below the balance point the heating system must run to maintain setpoint.
Curt Kinder <br><br>

The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
You are not authorized to post a reply.

Active Forums 4.1
Membership Membership: Latest New User Latest: croccohvacusa New Today New Today: 0 New Yesterday New Yesterday: 0 User Count Overall: 35027
People Online People Online: Visitors Visitors: 309 Members Members: 0 Total Total: 309
Copyright 2011 by BuildCentral, Inc.   Terms Of Use  Privacy Statement