Forums > Green Building Technologies > Geothermal Heat Pumps > Subject: cooling water with geothermal heat transfer

You are not authorized to post a reply.   
Prev Next
Author Messages
chuckmUser is Offline
Registered Users

Posts:1




05/23/2007 2:15 PM  
I am trying to calulate the amount of buried tubing I will need to cool water in a stored 2500 gallon cistern. Soil clay/sandy average temp. 48" below grade I beieve to be 52 degrees the water temp will be appox. 74 degrees. I am trying to cool the water to the soil temperature overnight, 12 hours. The water will be circulated through a fan coil during the day to provide cooling.
WolfCandy3xUser is Offline
Registered Users

Posts:56




05/24/2007 8:19 AM  
Hi chuck,

Isn't this redundant in some way ?
You need to cool 2500 Gallon via Geothermal for day cooling: So you would be getting a water water GHP anyway for the process
so why not just feed the cooled water from the GHP to the fan coil directly and simply forget the 2500 Gallon of water ?

Francis
David hotUser is Offline
Registered Users

Posts:22




06/04/2007 10:21 AM  
Water at 52 degrees does not have a lot of cooling capacity. Also you would not get there without an infinite length of pipe as the earth does not cool down outsiide the pipe easily. You are totally off base from any energy transfer perspective. If you can pull water from the earth at a continuous 52 F you can get a little "free" cooling. But most places require a second well to return the water.
Don't waste your money. Better to cool your attic spaces with an attic fan so heat build up is reduced. Best bang for the buck in cooling and very often overlooked. Even better although noisy is pushing house air into attic from the house to displace hot attic air although you don't do this while running air conditioning
megatekUser is Offline
Registered Users

Posts:16




07/29/2007 11:20 AM  
David - the amound of cooling or energy removal you need is approximately=

Btuh = 500 x gallons x (temp drop).

the amount of tubing you need, you will have to pay someone to tell you that (liability)  ; )

John Herbert
Sales Engineer
www.hydroheat.com
You are not authorized to post a reply.
Forums > Green Building Technologies > Geothermal Heat Pumps > cooling water with geothermal heat transfer



ActiveForums 3.6

Professionals Serving
Your Location:

Creative Panels (Kingsburg, CA)
Amvic-Pacific (Nevada City, CA)
Sierra SIPs (San Andreas, CA)
Blue Lupin Developments (Incline Village, NV)
Greenblock Worldwide Corp (Cave Creek, AZ)
View More

GBT Project Albums:

Off-the-grid home (E of Eganville, ON)
Jay's House (Burlington, VT)
MN Geothermal Retrofit (Twin Cities, MN)
Kitchen/gathering room (Manchester, MI)
Out with the old (Fort Ashby, WV)
More Info |  Search
Copyright 2008 by BuildCentral, Inc.   Terms Of Use  Privacy Statement