Horizontal slinky on small lot
Last Post 10 May 2011 12:16 PM by esger. 38 Replies.
|
Sort:
|
|
Prev Next |
You are not authorized to post a reply. |
|
hausfxr
 New Member
 Posts:53
 |
| 04 May 2008 09:00 PM |
|
We are replacing our turn-of-the-century home’s foundation
and thought it would be a great opportunity to install radiant in our new
day-lit basement’s slab. The basement
walls will be ICFs. We will also be
installing staple-up radiant panels under our existing strip wood flooring (no
existing underlayment), as well as stripping our old plaster down to studs,
furring the studs with horizontal 2x2s, super-insulating the shell, and
installing new windows. Our
house is on
a 50’ x 100’ city lot located in Portland, Oregon. As soon as we
determine which heating source is best for us, we will be installing
the
hydronic tubing ourselves with a professional’s design and getting the
boiler
and manifold system designed and installed by a professional.
We originally thought we would have vertical geothermal
loops installed, but after getting a ball-park figure from contractors for both
DX and plastic, we decided the extra tens of thousands of dollars for those
systems would be better spent on energy conservation.
We then found out about air-to-water heat pumps, but every
homeowner and contractor we’ve talked to had their own bad experience of them
to relate, so we’ve decided that until some of the best residential European or
Japanese models are sold in the US, we’ll stay away from them.
What we now want to do is to install a water-to-water heat
pump with a DIY horizontal slinky system at about 4.5’ to 5’ below the
surface. Our lot has no trees and very
little shrubbery, and, since we are majorly disrupting the landscaping with our
foundation replacement anyway, we thought it would be easy and inexpensive to
install. The soil is a clay/silt
loam. Our heating load including
domestic hot water is 2.5 tons and we will not be cooling. Winters are extremely mild here. The ICF foundation will be a Quad-lock R-32
and the slab and edge of footing will be insulated.
Here’s our question:
Is our lot big enough to provide an adequate heat reservoir
for a slinky loop system? Every
professional we’ve talked to has no experience with small lot horizontal loops
and has expressed skepticism, and we can’t find an example on the internet, yet every description we’ve read
about indicates our yard has more than enough thermal mass to make this
work.
This diagram illustrates the best slinky configuration we’ve
come up with.
<!--[if !supportEmptyParas]--> <!--[endif]-->
Thanks,
Brint
|
Attachment: House_2008.05.04_HVslinky2.pdf
|
|
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 04 May 2008 10:47 PM |
|
I should have said that I my situation is similar to yours. My lot is about twice as big as yours, my house is bigger as well. I live in Salt Lake City where the winters are a lot colder. I have a 4.5 ton heat pump. I stood my slinkys in a vertical trench. I have 5 trenches 125' long with 1250' feet of 1" pipe per slinky. I used all of my back yard and most of my side yards for trenching.
My system has been in for three years now and it works like a champ. We just finished the heating season and my loop temp bottomed out at 41° . |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
hausfxr
 New Member
 Posts:53
 |
| 05 May 2008 12:00 AM |
|
Hi Dewayne,
Thanks for such an informative reply.
We are limited by some existing shrubbery, but we could
accommodate your suggestions. The one
contractor we talked to who seemed to know something about horizontal loops
told us the following rules of thumbs:
1. No pipe lengths
over 750' -- too much resistance.
2. Larger pipe
diameters also increase resistance -- don't go above 3/4"
3. Slinky loops
installed in the vertical position trap air and create resistance at the top of
each loop.
4. 1000' of pipe per
ton max.
5. Don’t return
loops in the same trench -- for obvious reasons.
<!--[if !supportEmptyParas]--><!--[endif]--> His advice in #2 does not make intuitive sense to me. I know that smaller diameter pipes increase
resistance and that there is an exponential relationship between diameter and
surface area, so a 1” pipe has potential advantages in heat absorption.
<!--[if !supportEmptyParas]--><!--[endif]--> His advice #3 also seems counter-intuitive assuming that the
system can purge air (I don’t know whether they can) as long as the dissolved
oxygen content was low, the bubbles that did form would be
readily reabsorbed.
<!--[if !supportEmptyParas]--><!--[endif]--> His general reasoning behind limiting resistance was that a
larger pump required to move more water or a faster water speed to purge air
bubbles takes more electricity and, thus, diminishes significantly the coefficient
of performance.
<!--[if !supportEmptyParas]--><!--[endif]--> Did you install a ClimateMaster heat pump at your house,
and, if so, do you prefer these over WaterFurnace?
<!--[if !supportEmptyParas]--><!--[endif]--> Have you done many vertical slinky loop installations and
have you had any problems?
<!--[if !supportEmptyParas]--><!--[endif]-->While I know you are in a different heating climate from
ours so direct comparisons are difficult, are you able to determine what %
of your electric use goes for heating, and can you determine the actual COP of
your system? Was it different from what
you calculated in the planning stage?
I will revise my diagram to reflect you suggestions and
repost it soon.
Brint
P.S., The
diagram was drawn in Autocad and the slinky is drawn using the measure tool
which places a block (a circle in this case) at a set equal distance along a
polyline.
. |
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 05 May 2008 12:36 AM |
|
Hey Brint,
Pipe size and length need to be determined by the gpm your system needs. Your 2.5 ton heat pump will need 7-8 gpm. If you split that between to two loops, then you are pushing 4gpm per loop. The maximum recommended flow for 1" pipe is 8 gpm.
I also do not agree with #1 and #2 . #2 is just plain wrong!
#3 is true but the issue can be solved by purging the air prior to using the system. I know this works because of my system .
Do not go with a self purging, non pressurized pump module!
"His general reasoning behind limiting resistance was that a
larger pump required to move more water or a faster water speed to purge air
bubbles takes more electricity and, thus, diminishes significantly the coefficient
of performance. "
This is a true statement. However, the best way to lower pumping resistance is to divide the flow with more circuits. If you have to use 3/4" pipe, then go with four 500' loops instead of two 1000' loops of 1"
If you have the room to lay the slinky horizontal it does make purging easier.
We have done two vertical systems and they both work. We always do horizontal when we can.
I actually have a Florida Heat Pump in my house. I would go with what ever brand you can get serviced by local contractors.
I have a submeter on my heat pump. I spent $190 on heating for the past heating season. My COP changes as my loop drops. It varies from 2.9 to 3.5.
This was the first system I installed and I didn't do any calculations prior to installation.
Keep in touch
|
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
TechGromit
 Advanced Member
 Posts:634
 |
| 05 May 2008 09:52 AM |
|
Posted By esger on 05/05/2008 12:00 AM
1. No pipe lengths over 750' -- too much resistance. 2. Larger pipe diameters also increase resistance -- don't go above 3/4"
I absolutely agree, the longer the runs, the more resistance... When you talking about electricity, Not water on a basically level surface. And number 2 baffles me, the larger the pipe, the completely oppose is true, the less the resistance. |
|
|
|
|
bartman99
 New Member
 Posts:57
 |
| 05 May 2008 11:07 AM |
|
Posted By geodean on 05/05/2008 12:36 AM
I have a submeter on my heat pump. I spent $190 on heating for the past heating season. My COP changes as my loop drops. It varies from 2.9 to 3.5.
Hi Geodean, Just wondering how you calculated COP's? Does the submeter give you kwh and you go from there? If so, how? Thanks, BM99
|
|
|
|
|
hausfxr
 New Member
 Posts:53
 |
| 05 May 2008 01:38 PM |
|
GeoDean,
<!--[if !supportEmptyParas]--><!--[endif]--> The attachments show two possible slinky layouts.
<!--[if !supportEmptyParas]--><!--[endif]--> Avoiding shrubbery accounts for its asymmetry.
<!--[if !supportEmptyParas]--><!--[endif]--> Questions:
<!--[if !supportEmptyParas]--><!--[endif]--> 1. So, if I follow your reasoning on pipe size and length:
pipe diameter (within reason) does not influence pump size for a horizontal loop,
but there is a relationship between smaller diameter pipe and how many
individual loop lengths optimally create the total.
If we went with ¾” pipe with four 500’ loops instead, we would be
pumping a similar volume of water at the same speed as a 1” pipe with two 1000’
pipes. However, the surface area of the pipe and, hence, the heat transfer would be greater for the 1” pipe. Would both pipe sizes with lengths as
described here require the same pump and use approximately the same amount of
electricity?
<!--[if !supportEmptyParas]--><!--[endif]--> 2. If the slinky trench is approximately level, can we run
the straight runs from the slinky trench to the header 2.5’ below the slinky
elevation? This would put both the
supply and return about 2’ below the slab drainage gravel. Does this influence the accumulation of air
if the center portion of the pipe is taller than the ends? It has the benefit of adding to the heat
sink the loop is drawing on.
<!--[if !supportEmptyParas]--><!--[endif]--> 3. A possible alternative is to run the supply and return pipe
level around perimeter. This is
attractive because it requires no additional excavation – we will already have
between 30” to 36” inches clear around our well insulated foundation. Is this a better placement?
Thanks,
Brint
<!--[if !supportEmptyParas]--> <!--[endif]-->
|
Attachment: House_2008.05.05_HVslinky3.pdf
Attachment: House_2008.05.05_HVslinky4.pdf
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 05 May 2008 03:46 PM |
|
Answer to #1:
with 8 gpm,
the pressure drop through two 1" loops by 1000' would be 14 ft of head.
the pressure drop through four 3/4" loops by 500" would be 6.1 ft of head.
so four 3/4" loops will only require 1/2 the pump capacity of two 1" loops.
Answer to #2:
As long as you have a big enough pump to properly purge the system before using, there is not a problem with elevation changes. Purging is an important step that often gets overlooked. Any air left in the system can block a loop so you might only have flow through 3 out 4 loops. Since you manifold is going to be inside, you can purge the loops one at a time. This is a big help.
If #3 is the easiest, I would probably go that way.
|
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 05 May 2008 03:52 PM |
|
Posted By bartman99 on 05/05/2008 11:07 AM Posted By geodean on 05/05/2008 12:36 AM
I have a submeter on my heat pump. I spent $190 on heating for the past heating season. My COP changes as my loop drops. It varies from 2.9 to 3.5.
[/quote] Hi Geodean,
Just wondering how you calculated COP's? Does the submeter give you kwh and you go from there? If so, how?
Thanks,
BM99
If you take the temp of the water going into the heat pump and subtract the temp of the water leaving the heat pump then multiply by the gpm through the heat then multiply by 500 this will give you the BTUs extracted from the water. The assumption is that heat is going into your house. Convert how many watts your heat pump uses to BTUs and divide the BTUs in by the BTUs consumed and you will have COP. Hope this make sense. |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 06 May 2008 05:34 PM |
|
Posted By bartman99 on 05/05/2008 11:07 AM Posted By geodean on 05/05/2008 12:36 AM
I have a submeter on my heat pump. I spent $190 on heating for the past heating season. My COP changes as my loop drops. It varies from 2.9 to 3.5.
[/quote] Hi Geodean,
Just wondering how you calculated COP's? Does the submeter give you kwh and you go from there? If so, how?
Thanks,
BM99
I found some better info on how to figure COP:
Calculations
Heat rejected or
absorbed to/from ground loop:
GPM x ΔT x 500 = Btuh (water only loop)
GPM x ΔT x 485 = Btuh (water/antifreeze loop)
Heat from electrical
energy (pump+compressor+blower):
- Determined
wattage load: Volts x Amps = Watts
- Convert
watts to heat: (Watts x 0.85) x 3.412 = Btuh
Net Cooling Capacity:
Heat rejected to loop - Heat from electrical energy measured
= Net Cooling Capacity
Total Cooling
Capacity to Ground Loop:
Heat rejected to loop + Heat from
electrical energy measured = Total Cooling Capacity to Ground Loop
Energy Efficient
Ratio (EER):
Net cooling capacity / watts = EER
Total Heating
Capacity:
Heat absorbed from loop + Heat from electrical energy
measured = Total Heating Capacity
Coefficient of
Performance (COP):
Total heating capacity / heat from electrical input = COP
|
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
TechGromit
 Advanced Member
 Posts:634
 |
| 07 May 2008 09:40 AM |
|
Posted By geodean on 05/06/2008 5:34 PM
Posted By bartman99 on 05/05/2008 11:07 AM
[/quote] I found some better info on how to figure COP:
[u]Calculations[/u][/b]
Heat rejected or absorbed to/from ground loop:[/b]
GPM x ΔT x 500 = Btuh (water only loop)
GPM x ΔT x 485 = Btuh (water/antifreeze loop)
Are these calculation based on a certain material and pipe diameter? I would think something like copper would have a better reject / absorb ratio and the diameter of the material in question as well. |
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 07 May 2008 09:51 AM |
|
The formula has nothing to do with pipe type or diameter. The purpose is to figure the COP of the heat pump. You measure the temp of the water going into the heat pump and coming out of the heat pump.
Pipe type and diameter would come into play when computing how much pipe you need in the ground. Certainly if your ground loop is not constructed properly, it will not be able to transfer the heat to and from the heat pump. This would have impact on the COP of the heat pump. |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
hausfxr
 New Member
 Posts:53
 |
| 18 May 2008 04:39 PM |
|
We were referred to a contractor who has done a lot of
horizontal closed loop installations and have gotten a new perspective on
slinky loops. Of the three local
contractors I’ve now talked with, this is the first who expressed willingness
to give us pointers on our DIY pipe trenching, sell us the best pipe at a reasonable
price, fuse our pipes to the collection heads, and pressure test before and
after backfill.
This contractor does not do slinky loops and advises against
them for four reasons.
- There
is an inherent conflict in sending a pipe that is slowly absorbing heat
backwards onto its previous path where it could lose heat to the colder
pipe/soil behind.
- Backfilling
and soil compaction is easier with less risk of one pipe crushing the one
below.
- Multiple
pipes can be placed in multiple lifts increasing the volume of soil
contacted.
- Straight
run pipe installation is all-around easier than loops.
They are not suggesting decreasing the total linear feet of
pipe, just running more single pipes per trench.
Again, not knowing the physics of how the number of pipes
affects head pressure and resulting pump size, I’m assuming it takes no more
energy to run twice as many same diameter pipes a shorter distance?
As to the concerns about freezing soil I posed in another
post (see my post “Best loop tubing?” and Cnygeo’s informative reply): The contractor has never designed a water based system
that had loop temperatures that dropped below freezing and thinks that such low
temperatures indicate poor design – the efficiency of the system depends on
water temperature, and in our mild climate, at the point of below freezing
loops, you’re better off with an air-source heat pump. They saw no real problem running a portion
of the piping around the foundation perimeter, especially with our well
insulated foundation.
Our modified design would have (8) 350’ loops – 340’ of individual
trenches away from the house, and an additional 175’ of trench around the
foundation perimeter. No one has done
any calculations of this layout, but our thinking is that it is the equivalent
of 280’ of slinky trenches, just with some of the pipes spread out over a
greater volume of the available soil.
Since we are replacing the existing house’s foundation, the loops near
the foundation are just a bonus taking very little extra effort. Soil placement during loop trench excavation is
our only real logistical challenge, and that is why some of the trenches are
only 32” wide.
If anyone has any advice on our latest scheme, we welcome
all opinions. In the attached PDF, I've included the slinky loop scheme GeoDean commented on previously. Also, is anyone aware of
documented cases of water based geoloops freezing the soil and damaging
foundations?
<!--[if !supportEmptyParas]--> Thanks for all the advice so far,
Brint
|
Attachment: House_2008.05.17_HVdetails5.pdf
Attachment: House_2008.05.17_HVtrench5.pdf
Attachment: House_2008.05.05_HVslinky4.pdf
|
|
|
|
cnygeo
 Basic Member
 Posts:170
 |
| 19 May 2008 12:44 AM |
|
Interesting - just goes to show the difference that region and climate can make. I assume if the contractor is confident that the loops never drop below freezing that he doesn't use antifreeze? That would be a small savings in itself and if a design was "on the edge" a good reason to add length to push the temps well above freezing. There's nothing magic about loop temps dropping below freezing that hurts efficiency. If you pull specs from any manufacturer you'll see that while loop temp certainly has an effect on COP, it is mostly linear with temperature and fairly gradual. I'm pulling numbers out of thin air here, but for example a heat pump might have a COP of 4.5 at 40F loop temp, 4.3 at 35F, and 4.1 at 30F, on down. Higher loop temps are always better for efficiency (heating) but at some point you are into diminishing returns with installation costs outweighing any reasonable payback in performance. Obviously the economics are very different in the Northwest than they are here due to a milder climate and presumably higher mean ground temps.
I don't quite understand the comment about an air-source heat pump being as good at below freezing temps - Even at 25F and lower loop temps, most GSHPs will beat the pants off an air source heat pump at below freezing air temps since the air-source pumps have to defrost the coil periodically. If he's talking about operating cost vs installation cost and payback he may have a point if you have cheap electricity, although the GSHP numbers won't change much between a loop temp of 30F and 35F. It's not like increasing the average loop temp by 5 degrees will suddenly make a geo system cost-effective.
Nothing necessarily wrong with more shorter loops vs fewer longer ones, actually it will decrease pumping work for the same flow. However, you need to make sure that your flow will be sufficient to maintain turbulence in the pipe for good heat transfer. using 8 loops on a smaller system may require you to increase the total flow, which could lead to high pumping work, especially if it is more flow than is speced for the heat pump - the pressure drop across the heat exchanger will get very high. Make sure you run the numbers so that with the flow your heat pump requires you have enough per loop to keep the Reynolds #s well into the turbulent region.
I guess I still cringe at the thought of running loops close to the foundation, but if it is common practice out there, go for it. I can't say that I've ever actually seen a documented case of a freezing loop damaging a foundation, so maybe the risk is blown out of proportion.
It's good you're thinking about where to put the soil ahead of time - my lot is larger than yours but we still dug ourselves into a corner a few times because of poor planning on my part. Not a big deal, but it wasted some time and money moving soil twice unnecessarily. By the time we were done we had a pretty good system down, but I bet an experienced loop digger could have knocked 30-40% off the time it took us. |
|
|
|
|
hausfxr
 New Member
 Posts:53
 |
| 16 Jun 2008 01:56 PM |
|
Thanks Cnygeo, Geodan, and others for your previous feedback.
Since my last posting, I visited a job site were the local
contractor who had looked at our plans and given us feedback was installing a
horizontal system in a 5’x5’ trench 500’ long with (6) ¾” pipes at the bottom. He
invited the public out to see an installation first hand and give advice and
answer questions. I had told him right
from our first interaction that we were looking to install the system DIY and
that we would not be a potential client (except for the heat pump which we
would only have a professional install), and this did not concern him. Seems like a great guy who has a keen
interest in promoting geothermal. He
advised us on how to make the system better, told us to base it on 3-tons of
heating (not 2.5), and said our system would never get below freezing as
designed. We revised our design and emailed the plans back to him but have not
heard from him either responding to email or phone messages for two weeks –
very busy guy, so I don’t begrudge him one bit, the advice was free after all. The system will now have (6) 375’ ¾” pipes
at 5’ deep. The 5’ wide trenches are
295’ in length, and the 3’ wide sections next to the foundation are 80’ – see
attached diagram.
We are scheduled to have the excavator come out on Wednesday
and will lay the pipe perimeter pipe in one day. The sections next to foundation and under the addition will be
done later when we replace the foundation.
We will bury the unsed portions of coils under some plywood to keep them safe until we are
get to the foundation excavation.
Does anyone out there see any problems with our system or
think we should change pipe size or number.
We where originally thinking we would place eight pipes in at least two lifts, but
after talking with the above mentioned contractor and our excavator (and seeing
an actual installation in the pouring rain!), we decided that placing all the
pipe just at the bottom of a wide trench was the best way to go. The excavator will start by digging a short
(30’ to 40’ to start with, shorter 20’ lengths after that) length of the trench
with a backhoe, we will lay that section of pipe, he will use a bobcat to take
the excavated soil all the way around the house and begin backfilling behind us. We’ll work our way gradually around the
house to keep temporary soil placement to minimum.
<!--[if !supportEmptyParas]--> Brint<!--[endif]-->
|
Attachment: Riggs_2008.05.30_Geo_loops.pdf
|
|
|
|
Palace Geothermal
 Veteran Member
 Posts:1609
 |
| 16 Jun 2008 11:48 PM |
|
Given the small lot that you have to work with, I would say that you have a pretty good plan in place.
Be very careful about the loop temp. The water leaving the heat pump can be as much as 10 degrees colder than the water coming in. So if the water coming from the ground gets down to 42 F you are in danger of freezing the coil inside your heat pump. This pretty much ruins your heat pump.
Methanol is not that expensive. There is no way I would install a system with out antifreeze. Since you don't have a lot ground area to work with, your loop temps might get colder than you think.
Please keep us informed as your project gets going.
Good Luck |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
cnygeo
 Basic Member
 Posts:170
 |
| 17 Jun 2008 12:21 AM |
|
Second what Geodean says about antifreeze - if you're going without make sure you have at least a few degrees safety factor and MONITOR the water temp going out to the loop. You could always start without antifreeze and if the outgoing temps start dropping too much for comfort you could add it. Of course the cost and difficulty of doing this in the middle of the winter could be great depending on your system! Open loop systems use various freeze-protection devices (refrigerant pressure and/or outgoing water temp switches) so you could look into adding these as well.
In terms of your loop design, my gut says that it is pretty dense - lots of pipe without a lot of surface area. But, you're on the other side of the country from me in a different climate and with different soil, so I'll defer to local experience here. It doesn't look like you have a lot of options to expand anyway!
Good luck with the project! |
|
|
|
|
hausfxr
 New Member
 Posts:53
 |
| 21 Jun 2008 01:24 PM |
|
We have finished installing the outer perimeter of piping of
our horizontal loops. Most of the job
went well though it took twice as long as the excavator first said it might take
– 20+ hours for the excavating.
<!--[if !supportEmptyParas]--> <!--[endif]-->Two pipe questions:
1. The pipe would get twisted when rolling it out, and that
twist would sort of curl up and poke out of the coil – I started calling these
hernias. The solution was simple, just
flip the entire coil until the twist unwound, and the problem would fix itself. One time during the job the excavator was moving the coils when he perceived things weren’t going fast enough, and I
had to insist that he leave the pipe laying to me. At the very end of the job, once again the excavator decided to
“help” with the coils again and one of the coils developed one of the hernias projecting
from the coil and the twist developed a crimp while he was pulling on it. The pipe now has a slight indent at
the crease line and is lighter in color.
All of the pipes are under 80-lbs of pressure, and that pipe appears to
have no leak when soaked at the crimp. This last section is not yet
buried.
The question is, does this compromise the pipe -- should it be
repaired or protected in any way?
I have told the excavator that if the pipe needs to be
repaired, he must pay for it. The contractor insist that kinks do not hurt the
pipe and that he is in no way responsible for damage to my piping under any
circumstances (he did not see that he had crimped the pipe until I saw it
later.)
2. The excavator was pulling dirt back along the bottom of the trench with
the track hoe after the pipe had been laid, and he was allowing the bucket blade to
ride along the tops of the pipes -- pulling dirt off the pipes. The bucked had a rounded blade edge and no
teeth. When I saw this, I insisted he
not do it any more. He says he does it
all the time with water piping, and all these pipes are so strong that he could
never hurt them with his bucket. The
pipe had obvious scratch marks running parallel with the pipe. None of them looked very deep. What I couldn’t see was any potential damage
at places that had already been buried where he might have been doing this. One of the pipes has lost about 3-lbs of pressure in 16hrs. Not sure wether it is coming from the
manifold or plug at the ends yet, but I’m now a little worried. My question is, would even a small leak make the pipe unusable?
Brint
|
Attachment: House_2008.06.20_geoloop.jpg
|
|
|
|
Alton
 Veteran Member
 Posts:2164
 |
| 21 Jun 2008 07:00 PM |
|
esger.
Ref question 1: What kind of pipe did you use? Was it HDPE (High Density Polyethylene) or cross-link polyethylene pex-a, pex-b, or pex-c? Whether permanent damage is done when the pipe is kinked oftentimes depends upon the type or material in the pipe. Sometimes damage will not show up for several years. It is best not to kink any type of pipe.
Ref question 2: In my humble opinion, the bucket blade should never touch any type of plastic pipe. Why take the chance of damaging pipe that will be covered that deep? I think you should monitor the pressure in the line that shows a loss of pressure. If the pressure keeps dropping then try to check the easiest things first. |
|
Residential Designer & Construction Technology Consultant -- E-mail: Alton at Auburn dot Edu Use email format with @ and period . 334 826-3979 |
|
|