During the compilation of the shoppers checklist we discussed a trouble shooter's checklist. I am inspired to kick one off now in no small part due to simultaneous posts that complain about electric bills without any supporting data to confirm or exclude trouble with their systems. I'll throw in some thoughts and as before encourage anyone's input:
If you are having trouble with your heat pump (or think you are) and wish to ask for advice here, you will be asked some or all of the following. In a brief desription of your problems, your ability to provide this information greatly increases your odds of success;
1) Where you live 2) Heat loss/gain calculations for your home 3) Brand, size (model), age and type of heat pump 4) Type of loop field (open/closed/vertical/horizontal) size and design parameters 5) Average cost/Kwh of electricity and consumption 6) Entering and leaving air temperatures (EAT, LAT) measured immediately upstream and downstream of the heatpump 7) Entering and leaving water temperatures (EWT, LWT) measured at the geo system 8) Percent of load to be covered by geo and balance point 9) Installer's assessment of your systems operation. 10) Projected operating costs, actual operating cost and previous heating and cooling costs
Items 2, 3, 4, 5, 8 and 10 are all easily found operating cost projection reports such as Climatemaster's Geodesign. Most signs of trouble are when actual experience varies greatly from these projections.
Air temperatures may be taken with an inexpensive probe type thermometer. Water temperatures may be taken with the same instrument if ports are available where water lines go into heat pump or by taping the thermometer to the entering and leaving water lines and insulating it from surrounding air.
It is also helpful to state your question briefly and in short paragraphs. Lengthy blogs make useful information difficult to ferret out.
Finally, YOU MUST read responses and answer questions.
Good Luck, Joe |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
|
geome
Advanced Member
Posts:987
|
25 Feb 2010 10:58 AM |
|
Joe, not sure how detailed you want to get, but here are a few ideas: Day/night thermostat settings. Slinky, pipe layout (4 pipe) and spacing, length and type of loop pipe. Is Aux heat enabled, disabled, or otherwise controlled. Aux type (electric, gas). Thermostat make and model number. For 5), I would clarify - total electric bill divided by kWh used, if this is what you want. Some people may see the price to compare on their bill and provide that figure. How they quantify colder, milder, etc., temperature comparison between seasons (degree days, average temperature, etc.) Alternative energy types and prices (fuel oil, natural gas, propane).
P.S. It would be nice to receive timely responses from the OP. Having to go back and re-read pages of replies after several days, or weeks, of waiting for a response is an unnecessary waste of time for people that are trying to help (I know, we don't have to reply if we don't want to). Some questions may take some time to answer, but other questions can be answered quickly if the OP is motivated. It's a "help us help you" situation.
|
|
Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon. |
|
|
engineer
Veteran Member
Posts:2749
|
25 Feb 2010 09:28 PM |
|
I like it as is - make it a sticky. I've wasted way too much time playing 20 questions with folks unwilling or unable to provide the basics |
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
joe.ami
Veteran Member
Posts:4377
|
26 Feb 2010 08:42 AM |
|
Geome, I think I asked most of your questions except thermostat and other fuels. See #4 type of loop field and #5 if answered gives me different factors to reach the total. Curt, appreciate your thoughts. I haven't had a lot of time lately to visit the other forum, if you have a moment and wish to drag the list over there, perhaps the others will have thoughts. To all we have a recent poster who wiithout knowledge of previous energy use by the building's heat plant or clear representation of electric consumption has decided geo doesn't work. Sometimes emotions can ran very high because the dollars are great and geo is still "new" to many. Further many buyers are the "first kids on the block" to have one and are being quizzed by their family and neighbors. Good and intelligent people can get excited and slightly irrational when they think they have squandered tens of thousands of dollars. For those reasons I think the previous heating/cooling bills that Geome was hinting at may be a good addition to the list. I will add them to item ten via edit. J
|
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
joe.ami
Veteran Member
Posts:4377
|
05 Mar 2010 09:13 AM |
|
I felt obliged to add a final item and mention it here due to its importance.... "Finally, YOU MUST read responses and answer questions." j
|
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
whiskey
New Member
Posts:4
|
23 Mar 2010 10:26 PM |
|
I have a Tranquility 27 two stage 4 ton Climate Master.The black light on the thermostat is red.The screen indicates service needed,phone contractor and E4-Low Water Temp.Can't get ahold of contractor.I shut off breaker, switched on breaker, furnis ran two days then shut down again.Cleaned filter then it ran for three days and shut down in to auxiliary heat. cotinuse to shut down every other day or so.System was just instald a month a go.E4 Low water Temp on thermostat means what?Is my duct work sound like it's to small.Maby not enufe air flow. |
|
|
|
|
joe.ami
Veteran Member
Posts:4377
|
24 Mar 2010 10:36 PM |
|
Shoulda mentioned.... Start here means try to answer these questions, but start your own thread..... Meant for mod to close this to replies. j |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
jhoffman327
New Member
Posts:8
|
05 Mar 2011 02:06 PM |
|
1. Clare, Michigan 2. lost all heat to home 3. Geomax 2 Model #HTV060A1C01JRK 3yrs old 4. pump and dump
All I am really looking for is a code for the error. It looks like a "lockout" code but I don't know how to disconnect power to the control as the manual tells me to do. All I know is it is not working and either is the aux heat.
I need to know where to start. Can you help me?
|
|
|
|
|
engineer
Veteran Member
Posts:2749
|
05 Mar 2011 09:39 PM |
|
Please start a separate thread |
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
jhoffman327
New Member
Posts:8
|
06 Mar 2011 08:34 AM |
|
I did. Thanks |
|
|
|
|
Bradley S
New Member
Posts:2
|
22 Jul 2011 05:12 PM |
|
I have had a geothermal heat pump since 2002 with a water heater dsh. My water heater started to leak so am going to replace it myself. The dsh is hooked up to the bottom of the water heater with two hoses connected to the drain with no shutoffs on the hoses. How do I disconnect the hoses from the drain on the water heater? Is there small hoses going in the drain that I will have to pull out and reconnect? thanks for your help |
|
|
|
|
twistor
New Member
Posts:3
|
02 Nov 2011 03:43 AM |
|
Hello, My name is Robert. We are having a problem with a Carrier "Tranquility 27" system involving 3 units on the water loop. Every summer (hottest months) the heat pumps go out on high head PSI.installed three years ago and every summer this happens. Has anyone had intermitant problems like this before?
• GPU-1 Model No. -TTH026AGS40ELPS Serial No. - L13781181
• GPU-2 Model No. -TSHO18BGS40ELWS Serial No. - L13781140
• GPU-3 Model No. -TTH026AGS40ELPS Serial No. - L13781180
Service info.
• Water flow to the units has been confirmed. (It might be too much).
• Water temperature to the loop has at 90 degrees. GPU1 – Water Temp In – 85 Water Temp out – 95 Temp diff = 10 degrees.
• GPU 1 – Source water pressure In – 40 Source water pressure out – 33 Press drop = 7
Report 9-16-11 PM that GPU 1 – shut off - flash code 2. (High pressure lock out code2) according to page 61, Safety Feature – CXM/DXM Control. |
|
|
|
|
twistor
New Member
Posts:3
|
02 Nov 2011 03:45 AM |
|
Hello, My name is Robert. We are having a problem with a Carrier "Tranquility 27" system involving 3 units on the water loop. Every summer (hottest months) the heat pumps go out on high head PSI.installed three years ago and every summer this happens. Has anyone had intermitant problems like this before? • GPU-1 Model No. -TTH026AGS40ELPS Serial No. - L13781181 • GPU-2 Model No. -TSHO18BGS40ELWS Serial No. - L13781140 • GPU-3 Model No. -TTH026AGS40ELPS Serial No. - L13781180 Service info. • Water flow to the units has been confirmed. (It might be too much). • Water temperature to the loop has at 90 degrees. GPU1 – Water Temp In – 85 Water Temp out – 95 Temp diff = 10 degrees. • GPU 1 – Source water pressure In – 40 Source water pressure out – 33 Press drop = 7 Report 9-16-11 PM that GPU 1 – shut off - flash code 2. (High pressure lock out code2) according to page 61, Safety Feature – CXM/DXM Control. |
|
|
|
|
joe.ami
Veteran Member
Posts:4377
|
02 Nov 2011 09:19 AM |
|
"start here with problems" meant read the list of questions we might ask and answer as many as you can........then start your own thread with your questions. Climatemaster (who made your heat pump) and many others have had switches fail, indicating trouble when there was none. 90* EWT may also have spikes from time to time (after long runs) that take unit out of tolerence. Follow up tests wouldn't be patient enough to last an hour. A WEL or other logger might help. Please start your own thread for follow up. Joe |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
geo pup
New Member
Posts:14
|
14 Nov 2011 10:37 PM |
|
Hey has any body here ever flushed a geo ground loop before? This is my first , but I'm have a hard time getting air out of the loop, the loop is installed in series , the loop goes up hill about 30 feet above my flush cart . I've been flushing for about 9 hours , but I can't seem to get the air out ,.. I have been shocking the loop from the return side |
|
|
|
|
KvdM
New Member
Posts:2
|
09 Feb 2012 01:59 PM |
|
Asweetwood, I'm going be very blunt here: Either do your calculations, or get out of the industry! If you calculated the amount of GPM required @ xxft of hd to obtain 2ft/sec velocity in ALL parts of the field, you should know whether or not your flush pump has enough capacity. From the fact that you did an install in Series and not parallel, I'm thinking not...
|
|
|
|
|
smitty50
New Member
Posts:1
|
08 Nov 2013 05:46 PM |
|
I have a TT 064 with a fault code 4 EAT 67, LAT 73, EWT 56.6, LWT 54.3, psi out 14, psi in 19 I have methanol at 30 percent in my closed loop wells (4 at 300") vertical. The system is 4 years old and has been running perfectly until now. Any ideas? |
|
|
|
|
joe.ami
Veteran Member
Posts:4377
|
10 Nov 2013 09:57 AM |
|
Smitty it appears your compressor is locked-out, please start a seperate thread and we will offer thoughts there..... |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
Carl Odle
New Member
Posts:12
|
23 Feb 2014 09:47 PM |
|
OOOOOOps Shouldn't have "Started" at "Start". So I "Started" a NEW thread. |
|
|
|
|
Bergy
Basic Member
Posts:277
|
23 Feb 2014 10:26 PM |
|
Could you please post a drawing of how it is piped? Bergy |
|
|
|
|