I have a Waterfurnace and live in a rural area where we sometimes have power outage.
I have a back up generator with more than capacity to operate the geo but not with even one of the aux heat banks on. The furnace is wired with compressor and control circuit to one of these aux banks so turning their breakers off will also turn the compressor/controller off.
I understand why Waterfurnace does it that way.
Can I put a switch in the E (or W) wire to the thermostat to keep the aux heat banks from turning on when using the generator?
Thank you!!
Mike
What model of WF do you have, and is the unit a split or a packaged (all-in-one) unit?
We typically don't use our heat strips, so I have the heat strips disabled via the thermostat installer setup options (Honeywell.)
We have one packaged Envision and one split Envision units and a 20kW generator:
The packaged unit will still run the heat strips due to the internal WF programming during some unit faults (ex. a compressor problem) even though the thermostat doesn't know that heat strips are installed. We have 15kW (10kW + 5kW) heat strips installed on the packaged unit I believe with a 60 amp breaker on the 10kW heat strip and a 30 amp breaker on the 5kW heat strip. I leave the 30 amp breaker turned off (for the 5kW heat strip.)
Our split unit heat strips (Carrier air handler) will not turn on the heat strips even if there is a WF fault.
I hope I remembered all of this correctly. Been a while.