Posted By drlebel on 02 Jul 2014 10:27 AM
Okay so I had a new house built with a 4 ton geothermal unit for 4500 sq feet in memphis zone 4. My manual J states that it should be okay until it hits 17 degrees then i need supplemental heat. In reality I get in trouble after it gets under 35. My HVac guys says the unit is working normally. They might be able to boost eficiency a little on it. The house is fairly tight with blower door test coming in at .5 2x6 construction with cellulose, and 1 inch blueboard sheathing. The contractor forgot to put in foundation insulation(which really ticks me off) and only placed r-30 in attic(manual J called for R-50). I have a radiant barrier in roof but so far have done okay in cooling. My question is...is it worth it to beef up atic insulation to r-50 and to bury the ducts in insulation to try to get my heating better? I understand the ducts may sweat if I bury them but I need some drastic things to help the efficiency of this unit. SHould I try to tighten up the house some more or will I hit a wall of diminishing returns. Thanks
Placing ducts & air handlers above the insulation increases the heating & cooling loads the system needs to serve, and is a bad (if legal & common) practice.
R30 is below the
R49 specified minimum for climate zone 4 per IRC 2012 , so yes, it's worth adding to the attic insulation, independently of issues with the mechanical system's performance or sizing. That upgrade alone is unlikely to make a fully (35F-17F=) 18F difference in the crossover point to where auxilliary heating is necessary, but it's still going to make
some difference, and will be worth it on a long term energy cost savings basis.
If the ducts are poorly insulated you may indeed run into condensation issues when you bury them- pictures of the installation & specs for the existing ducts might be useful- it's pretty easy to screw up the duct flow volumes with a sub-par installation even if they get the duct sizes right. You say the house is "fairly tight", but has the duct tightness been
verified with a duct-blaster? (If yes, what was the cfm/25 leakage?)
When ducts cross through the pressure boundary of the house like that
duct leakage adds very substantially to the infiltration rates, and thus
the heating/cooling loads whenever the air handler is running (a
primary reason why installing ducts & air handlers in vented attics
above the insulation is bad practice.)
Insulating at the roof deck to bring the whole-shebang inside of conditioned space would probably have a more significant effect on the heat load & crossover point, but that solution comes with a hefty price tag compared to adding another R20-R30 as cellulose on top of the existing attic insulation.