Mojoe, HR cooling can be accomplished by circulating chilled water. Ronmar’s explanation and requirement to stay ABOVE the dew point is exactly right. You can find a discussion about HR cooling here:
GBT Radiant Cooling Discussion
If you live in a hot but dry climate, you can also use an evaporative cooler (AKA swamp cooler) in lieu of an air conditioner:
Borst Evaporative Cooler Performance Software
If you live in a hot and humid climate, you will likely need to use a dehumidifier or an air conditioner.
Ronmar, for a standard 2.5” EPS + 6” concrete + 2.5” EPS ICF build up using our 2013 Rogue River, Oregon outdoor temperature profiles, the ICF performance software forecast the effective R-value to be R21.38 in Spring, R66.15 in Summer, R63.42 in Fall, and R21.07 in Winter. This is an average annual ICF effective R-value performance of R43.07 or 1.86 higher performance than the conventional R23.10 R-value. These values agreed quite closely with the values determined from our actual building energy usage testing. We also had thermocouples in the concrete and the concrete temperature profiles also agreed quit well with the ICF performance software forecasts. Please also keep in mind that ICF can greatly reduce air infiltration which can also significantly improve performance. However, the software does not attempt to factor this into the effective R-value as this is better addressed separately by accurately forecasting the infiltration rate for a given building design and using this value and the ICF effective R-value in the ASHRAE or ACCA Manual J performance analysis.
After developing the ICF performance software, I exercised it extensively using some extreme ICF build up values. I don’t think there is anything earth shattering here, but the goal was to test and validate the software over a wide range of ICF build up values. Here is the excerpt from our ICF performance software instructions where I documented these observations at that time:
“Here are some ICF performance observations based on varying the various ICF design parameters from the calculator default values and using our Rogue River, Oregon indoor/outdoor temperature profiles:
When the interior EPS thickness is reduced to 0.1” and the exterior EPS thickness is increased to 4.9” (i.e., essentially putting all the insulation on the exterior side, but keeping the total conventional R-value the same), the summer effective R-value went from R66.15 to R44.05. In this case the concrete temperature stays very close to the indoor temp. The effective R-value remains the same (i.e., R44.05) when all the insulation is put on interior side. However, in this case the concrete temperature stays very close to the outdoor temp. This would imply that both these non-symmetrical ICF designs result in an equal, but lower performance than the standard, symmetrical ICF design for this summer outdoor temperature profile. When this is repeated for the winter outdoor temperature profile, the winter effective R-value went from R21.34 to R21.96, i.e., a slight performance improvement.
When both the interior/exterior insulation thickness is reduced to 0.01” (i.e., essentially removing the interior/exterior insulation), the effective R-value went to R0.77 (i.e., 1.12 times higher than the new R0.69 conventional R-value). This would imply that even an uninsulated, 6” thick concrete wall will exhibit some degree of increased effective R-value. When the insulation is retained, but the concrete thickness is reduced to 0, the effective R-value went to R22.50 (i.e., exactly the same value as the new conventional R-value). This would imply that as the concrete thickness is reduced, the effective R-value tends toward becoming equal to the conventional R-value. When the concrete thickness is then increased to 4”, the effective R-value went to R63.40 (i.e., 2.77 times higher than the new conventional R-value). When the concrete thickness is further increased to 8”, the effective R-value went to R67.79 (i.e., 2.91 times higher than the new conventional R-value). When the concrete thickness is further increased to12”, the effective R-value went to R69.99 (i.e., 2.95 times higher than the new conventional R-value). When the concrete thickness is further increased to 36”, the effective R-value went to R78.48 (i.e., 3.01 times higher than the new conventional R-value). When the concrete thickness is further increased to 360”, the effective R-value went to R177.12 (i.e., 3.03 times higher than the new conventional R-value). When the interior/exterior insulation is then removed from this 360” concrete thickness, the effective R-value went to R109.25 (i.e., still 3.03 times higher than the new conventional R-value). This would imply that as the concrete thickness is increased, the insulation thickness becomes increasingly less important in achieving the higher effective R-values. Furthermore, for this summer outdoor temperature profile, this would imply that the absolute maximum possible effective R-value is 3.03 times the conventional R-value and we are achieving 2.86 times the conventional R-value with a standard ICF design.
One might expect that higher effective R-values might be achieved by having some portion of the indoor temperature profile be the same as the outdoor temperature profile. For example, having that portion of the indoor temperature profile be the same as the outdoor temperature profile during the summer cooling season when the outdoor temperature is below 70 degrees Fahrenheit to simulate having open windows or using increased ventilation during these times. However, this is NOT the case. While doing this will reduce some of the Thermal Mass Temp output parameters, doing this will result in some of the Conventional Heat Flow Rate output parameters becoming 0 (where they were previously providing a building heat loss cooling effect), will reduce some of the Thermal Mass Heat Flow Rate output parameters (where they were previously providing more of a building heat loss cooling effect), will increase both the Total Conventional Heat Flow and Total Thermal Mass Heat Flow output parameters (i.e., provide increased building heat gain), but will increase the Total Thermal Mass Heat Flow output parameter more than the Total Conventional Heat Flow output parameter, and this will REDUCE the Thermal Mass Effective R-value output parameter. Doing this for the summer profile resulted in the effective R-value going from R66.15 to R39.06. One needs to keep in mind that this calculator only determines the effective R-value performance for just the ICF for the entered input/output temperature profiles and this calculator does NOT determine the HVAC system performance of the building. Or perhaps another way of thinking about this is that when you run the building AC system, the building cools down to a lower temperature than it would otherwise be, however, the heat transfer through the walls increases because of the increased inside/outside delta temperature. More thermal mass heat transfer is equivalent to having a lower thermal mass heat transfer resistance or a lower thermal mass effective R-value. Obviously, opening windows or increasing ventilation during the summer cooling season when the outdoor temp is below 70 degrees Fahrenheit is a good thing to do as this provides increased building cooling with minimum HVAC energy usage.”