Posted By DaveF on 09/25/2007 1:45 PM
in order to maintain structural integrity a minimum 2 inch deep 4 inch wide trough has to be driven into the foundation that is in filled by the concrete wall.
The house designer & TurboCAD guru who reviewed my plans in the early stages of drafting suggested this same thing. On the other hand, the
PRESCRIPTIVE METHOD FOR INSULATING CONCRETE FORMS IN RESIDENTIAL CONSTRUCTION,Second Edition, published by U.S. Department of Housing and Urban Development as part of the PATH project doesn't say anything about keyways, but instead calls for dowels, and even then only for serious side loading conditions. I can't find in the 2006 IRC what is required for the footing to ICF wall connection. Here's the requirement from the Prescriptive Method:
6.1 ICF Foundation Wall-to-Footing Connection
No vertical reinforcement (i.e., dowels) across the joint between the foundation wall and the
footing is required when one of the following exists:
• The unbalanced backfill height does not exceed 4 feet (1.2 m).
• The interior floor slab is installed in accordance with Figure 3.3 before backfilling.
• Temporary bracing at the bottom of the foundation wall is erected before backfilling and
remains in place during construction until an interior floor slab is installed in accordance
with Figure 3.3 or the wall is backfilled on both sides (i.e., stem wall).
For foundation walls that do not meet one of the above requirements, vertical reinforcement (i.e.,
dowel) shall be installed across the joint between the foundation wall and the footing at 48 inches
(1.2 m) on center in accordance with Figure 6.1. Vertical reinforcement (i.e., dowels) shall be
provided for all foundation walls for buildings located in regions with 3-second gust design wind
speeds greater than 130 mph (209 km/hr) or located in Seismic Design Categories D1 and D2 at
18 inches (457 mm) on center.
Exception: The foundation wall’s vertical wall reinforcement, at intervals of 4
feet (1.2 m) on center, shall extend 8 inches (203 mm) into the footing in lieu of using
a dowel as shown in Figure 6.1.